Load Calculation for Transformer

02/04/2012 2:04 AM

Can some one help me about load calculating i.e i have 24 volt step down transformer for lighting purpose (2.5 kva input 415v output 26v ) the bulb I am using is 60watts 24v now what is formula for load calculating i.e how much bulb i can use on that transformer?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: load calculation for transformer

02/04/2012 3:10 AM

How many phases?

I(A) = 1000 × S(kVA) / V(V)

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Load Calculation for Transformer

02/04/2012 9:45 AM

If PF = 1.0 (as would be the case for incandescent lights), 2500 ÷ 60 ≈ 41 lamps. If the PF is less, the number of lamps will be correspondingly fewer.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Apr 2007
Posts: 414
Good Answers: 19
#3
In reply to #2

Re: Load Calculation for Transformer

02/05/2012 12:06 AM

True, but...

"To achieve maximum transformer efficiency, maintain average transformer loading between 60% and 80%."

See this item:

http://www.grainger.com/tps/electrical_general_purpose_transformer_selection_guide.pdf

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5
In reply to #3

Re: Load Calculation for Transformer

02/05/2012 3:54 AM

That differs from what I have seen elsewhere.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1271
Good Answers: 27
#9
In reply to #5

Re: Load Calculation for Transformer

02/05/2012 9:26 AM

Since I did worked for a manufacturer, I remember the allowable maximum load is actually dependent upon on the designer / manufacturer. In my old company the auto-transformer types were designed to safely provide up to a 25% of its rated capacity. The added safety margin are computed for resistive loads, and applicable on transformers having kva ratings of 1 kva and above.

The Isolation type transformers were designed a bit differently due to physical (core and copper) limitations. They were hot tested them to provide 80% of its rated capacity, with 2 degrees C., maximum allowable temperature rise for 24 continuous hours.

In short, real performance mostly will be brand and/or manufacturer dependent plus the country of origin!

__________________
vsar
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#4

Re: Load Calculation for Transformer

02/05/2012 3:26 AM

What will you be illuminating?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Associate

Join Date: Jul 2007
Posts: 26
Good Answers: 1
#6
In reply to #4

Re: Load Calculation for Transformer

02/05/2012 4:37 AM

Assuming the pf is 1 ( lighting load ):

· 2500 VA can means 2500 watts power . So you can use - 2500 / 60w = 41 lamps as mentioned earlier .

· In another way , the transformer of 2500 VA , can deliver current of : 2500 / 25 ( approx 26 v ) ie., 104.16 amps

· A 60 watts lamp on 24 v , will take - 2.5 amps . So the number of lamps that can be connected to secondary is 104.16 / 2.5 = 41.66 .

Approximately the number of lamps that can be connected is 41 ( Bulbs of 60 w / 24 v each )

Register to Reply
Associate

Join Date: Jan 2012
Posts: 25
#7
In reply to #6

Re: Load Calculation for Transformer

02/05/2012 8:09 AM

hey everyone i know all formulas which you are giving

the formulas which the members are suggesting is only applicable if the transformer efficency is 100% then you can say that 41 lamp..... i want to know the average load calculatiion i.e if transformer eff is 80% and pf is 1 then which formula is applicable..

note that transformer connection is Y-Y and line volt is

i/p volts = 415_____420v

o/p volts = 26.5____24v

Register to Reply
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#8

Re: Load Calculation for Transformer

02/05/2012 9:00 AM

I presume that if you have a 60 watt bulb that you have all ready decided what you are going to put on your transformer, or was the question you were given worded differently?

__________________
Dont get on to the roundabout if you dont know how to get off
Register to Reply