Customized Adapter with Ex Brass Gland

02/06/2012 6:42 AM

Hi,

We have an Ex Brass gland of size M25 and the hole size is smaller and non standard. Can we use a customized adapter, made in workshop (obviously with proper thread depth >8mm and Brass material) but with no Ex stamp, along with Ex gland without infringing classification requirements?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Customized Adapter with Ex Brass Gland

02/06/2012 6:53 AM

If the equipment it is to screwed into is Ex d, Ex e or Ex p, then no, it may not be done within the hazardous area. Nor is it permitted to open-out the hole in the equipment to fit the gland that is currently to hand without doing approval testing on the modified equipment if that equipment is in the hazardous area.

Choose instead the correctly-sized, rated, gland for the enclosure into which it is to be screwed.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#2

Re: Customized Adapter with Ex Brass Gland

02/07/2012 12:46 AM

Not permitted as an adhoc modification but technically possible if accepted practices and proper materials are used.

Find out if the enclosure manufacturer has a tech memo on this and follow the instructions.

I doubt you are the first to encounter this.

Depending on the application environment, both technical and litigious, you can proceed with informed confidence or err on the side of caution.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: Jun 2011
Location: Mossel Bay, SA
Posts: 777
Good Answers: 21
#3

Re: Customized Adapter with Ex Brass Gland

02/07/2012 2:30 AM

PWSlack is correct.

I wish to add that when tan item is certified, it means 'manufactured to specification for use in a described Ex area/s.

Either your cable spec is incorrect, or the gland is faulty in manufacture. Suggest you compare with another fitting, or measure accurately and refer to your supplier to confirm dimensions against the manufacturing data sheet.

Ensure you are not confusing the certification eg Ex(d) with Ex(e). There may be a difference in orifice size...

Register to Reply