HV AC Cable

02/06/2012 9:25 PM

What is the function of wire armour in a 132 kV / 230 kV cable? Why this is not earthed at the cable end termination? Since the function of fault current carrying and mechanical strength is offered by the metallic (aluminium or lead) sheath.

Register to Reply
Pathfinder Tags: Electric cables
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: HV AC Cable

02/06/2012 10:36 PM

You will find one end will be earthed. To earth both ends causes circulating currents. Use the search button at the top right of you screen and you will find lots of threads on this subject.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: HV AC Cable

02/06/2012 10:49 PM

Well first your using the British spelling but a review of the definition of the word "armor" will help you understand what it does and why its called armor. Now one reason why the armor is not connected to earth involves the concept of ground loops. Another reason involves the mathematics of transmission line theory which is even more complicated than ground loops.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Active Contributor

Join Date: Sep 2009
Posts: 12
#3
In reply to #2

Re: HV AC Cable

02/07/2012 12:17 AM

Thank a lot for the reply! However what could be the function of this armor in such case? Also there is stress reliever is installed to reduce the stress on the insulation due to over voltages induced in the armor.

I understood the Lead / Aluminium sheathing is performing the function of fault current carrying, switching voltage dissipation, mechanical protection and also water sealent. Kindly comment!

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: HV AC Cable

02/07/2012 3:27 AM

Earthed armour (or grounded armor, depending on the side of the pond) is there to operate the circuit protective device in the event of a fault.

A typical example of a fault is some silly sod individual putting a spade through the buried cable. Instead of blowing the individual to smithereens, the circuit protective device operates, minimising the damage, and requiring only a fresh set of underwear for the individual concerned for full service to be resumed.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#5
In reply to #3

Re: HV AC Cable

02/07/2012 11:44 PM

According to codes/regulations the minimum cross section of metal conduit or armour/sheath should be satisfied to effectively carry the fault current to trip the protective device.

__________________
pnaban
Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#7
In reply to #3

Re: HV AC Cable

02/08/2012 1:30 PM

Armour of Single core cables is earthed at one end directly and the other end through a surge arrester. The surge arrester helps control the over voltage induced in the armour when there is a through fault etc.

The earthing of armour only at one end is basically due to economic reasons as earthing at both ends will mean reduction in the cable ampacity to accommodate the additional heat due to the circulating currents in the armour.

Trust the above is helpful.

__________________
Raghunath
Register to Reply
Active Contributor

Join Date: Feb 2012
Location: Norfolk, England
Posts: 11
#6

Re: HV AC Cable

02/08/2012 2:08 AM

There are two threads of thought on this topic. Generally in the UK, the cable armour is earthed at both ends even if only as a supplementary bond rather than straight to earth. Again this is to protect As PW Slack mentions. However on a military installation a separate earth cable is also run to reduce the risk of loose connections in the cable termination glands. However, the armour itself is there to protect the cable and to provide added strength when the cable is laid in ducting, trenching or externally to provide an added protection to prevent personnel from damaging the cable in day to day use. It will not stop the big yellow cable finder (JCB) from damaging the cable should it do so, but if earthed, may trip the protection circuit or prevent the cores from being struck.