Energy Saving for Constant Torque Loads

02/08/2012 4:00 AM

Dear all,

Greetings!

I recently conducted an energy saving exercise on one of our plant motors.

The motor is a Mixer Motor - 45 kw. I installed a load manager on it and observed the variation in the Killo Watts drawn by the motor wrt time.

It was observed that the Peak Load - 35 kw, for 30 % duration and average laod - 15 kw, for 70 % duration. The process requirement is to maintain a CONSTANT TORQUE all through the cycle.

My question is - IS ENERGY SAVING POSSIBLE considering huge maount of load variation, but the torque should remain constant by a VFD or any other device??

Also what could be the quantum of energy sacing / thumb rule / percentage ??

Looking forward to your reply.

Thanks and regards,

Rooney

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Energy Saving for Constant Torque loads

02/08/2012 4:07 AM

What is the nature of the electrical tariff:

  • per kWh?
  • Maximum demand?
  • other?

Is there a power factor penalty imposed by the utility supply company?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Feb 2012
Posts: 3
#2

Re: Energy Saving for Constant Torque Loads

02/08/2012 10:31 AM

what is ur application? if it is hoist then i will suggest don't go for saving.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Energy Saving for Constant Torque Loads

02/08/2012 10:41 AM

The original poster has already stated that it is a mixer. What type, and what it is mixing, how much of it and at what temperature and pressure have not yet been stated.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#4

Re: Energy Saving for Constant Torque Loads

02/08/2012 12:10 PM

You have to answer Pw's question. If you are billed kwh's and/or kw demand then it does not matter. You are billed for what you use.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#5

Re: Energy Saving for Constant Torque Loads

02/08/2012 10:15 PM

I know that this is not what we were asked to answer but I cannot help myself from pointing out that there is no such thing as a constant torque motor. If there was a constant torque motor then there could be a motor with an infinite angular velocity.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Score 1 for Good Answer
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#10
In reply to #5

Re: Energy Saving for Constant Torque Loads

02/09/2012 8:06 AM

At redfred : Perhaps it is a DC motor with a constant current flowing in the armature ;-)

I still have a problem, at the moment there seems to be no speed regulation in your application. And you want a constant torque, how is it possible that the load is going from 35 to 15 kW? Mechanical speed regulation ?

Power still equals torque times angular velocity

Register to Reply
Guru

Join Date: May 2007
Location: Geelong, Australia
Posts: 1084
Good Answers: 54
#6

Re: Energy Saving for Constant Torque Loads

02/09/2012 1:01 AM

Based on your figures, your average power is 21kW, compared to a minimum of 15kW. So you could save 6kW , assuming 24hrs/day, 365 days/year, 0.12$/kWh that costs about ~$6,000.

So the answer is yes, you could save money.

Most modern VSD's have a function that lets you run at (approximately) constant power and depending on your circumstances that would seem worth looking at.

Also check if you actually need to mix as fast as you do, a gearbox change might also lower the required power (cost).

__________________
If there's something you don't understand...Then a wizard did it. As heard on "The Simpsons".
Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11
In reply to #6

Re: Energy Saving for Constant Torque Loads

02/09/2012 10:01 AM

It still depends upon the electrical tariff charged. Oh, well. Try another thread. <unsubscribes>

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#14
In reply to #6

Re: Energy Saving for Constant Torque Loads

02/09/2012 3:44 PM

You need to re-read the question. He did not say that he reduced the load from 21kw to 15 kw. He said it varies between those figures. So there is no apparent savings.

Register to Reply
Associate

Join Date: Aug 2011
Posts: 45
#7

Re: Energy Saving for Constant Torque Loads

02/09/2012 5:50 AM

Just a thought (need to be studied in details): Let there be two motors ,one 15 kw for 70% of duration and other 20 kw for peak load.This 20kw motor to get coupled and synchronize to take care of peak load of 35kw (15+20=35).Friends,this is no solution ,just a point for discussion.

Register to Reply
Anonymous Poster #1
#8

Re: Energy Saving for Constant Torque Loads

02/09/2012 6:20 AM

First you need to find out the power factor. If the power factor is very low such as .7 below than there is slight saving. Having variable power is directly to do with the load and quality of power.

Register to Reply
2
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#9

Re: Energy Saving for Constant Torque Loads

02/09/2012 7:19 AM

If I recall correctly, motor torque is proportional to current and motor speed is proportional to voltage. If the motor is supplying constant torque, then the current should be constant. When a lot of material is being mixed, the motor would turn slowly and when the amount of the product being mixed is less it would turn faster, with a higher voltage needed to be supplied to maintain the higher speed (ironically consuming more power, since power = volts X amps or torque x rpm).

So, it seems to me that if the voltage is varied to maintain constant current, then the constant torque requirement should be met.

Since Energy = power x time, to save energy, I would think you might want to look at how the mixer is used. Is it mixing a small amount of material (at higher power) for too long a time?

Another thought is: Does the constant torque requirement make sense? I would think that if you were mixing material, it would be more logical to consider speed x time (or number of revolutions) as an indication of how well the product is mixed.

Register to Reply Good Answer (Score 2)
Power-User
Canada - Member - New Member

Join Date: Feb 2010
Location: The Great White North
Posts: 185
Good Answers: 13
#12

Re: Energy Saving for Constant Torque Loads

02/09/2012 10:44 AM

My guess is that your motor is constant speed and that the Kilowatts vary depending on the load in the mixer. The motor will only use the amount of energy it needs to maintain the speed. If this is the case, using a variable speed drive will not save any money except for starting, and only if you exceed your demand factor. You will actually have a slight loss dependant upon how efficient the drive is.

__________________
Knowledge makes what was impossible, seem easy.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#13

Re: Energy Saving for Constant Torque Loads

02/09/2012 10:54 AM

Other than a POSSIBLE small savings from a VERY small improvement in power factor- assuming that the site is paying a PF penalty, there is virtually NO value in adding anything to this drive.

In the future- if the motor needs replacement- and if the "tracked" loads are typical and not lighter than what might be expected, there is an argument for installing a replacement motor closer to the 35 kW peak power load observed.

Other than that- look elsewhere for savings- you are paying for what you are using, whether that is demand or kWh.

ONE possible option- depending on operations and the electric rate charged- would be to schedule the mixing operation so that the "high" loads occur at night and the lighter loads occur during peak electrical demand hours. That MIGHT generate a small savings due to the electric rates charged- if they are "time of day" based.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#15

Re: Energy Saving for Constant Torque Loads

02/10/2012 10:33 AM

Elroy hit the nail on the head. A motor uses what it has to use. You cannot dictate to a motor how many kW it will consume for a load task, it is what it is.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Register to Reply 15 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: