DP MCB or 1P+1N MCB for 1 Phase Supply

02/08/2012 10:53 PM

For utility company 240V, 1 Phase power supply to your premises, what will you prefer for Main switch 1P+1N MCB or 2P MCB and why?

__________________
BNDas
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: DP MCB or 1P+1N MCB for 1 Phase supply.

02/08/2012 11:23 PM

Neither.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#2
In reply to #1

Re: DP MCB or 1P+1N MCB for 1 Phase supply.

02/09/2012 7:40 AM

why?

__________________
BNDas
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #2

Re: DP MCB or 1P+1N MCB for 1 Phase supply.

02/09/2012 4:46 PM

In the U.S., in single-phase loads with an ungrounded "hot" line and a grounded neutral line, the neutral is not interrupted, and single-pole breakers/switches are used. There are some exceptions, but they are rather unusual. Your local Code may vary.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: DP MCB or 1P+1N MCB for 1 Phase Supply

02/16/2012 10:09 AM

Why do you bother? There is no big cost difference between an SPN MCB and a DP MCB. Technically, it is better to opt for a DP MCB.

Register to Reply