Which Connection to Motor 5HP or Above, Star or Delta in DOL

02/10/2012 10:20 PM

i have 10 hp and 15 hp motor ,iwant to know if conect it directly to doL starter how should i conect whethere it is star or delta

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: which conection to motor 5hp or above, star or delta in dol

02/10/2012 11:18 PM

"A Direct-On-Line (DOL) starter is an electronic 3-phase motor-control system which offers soft starts in DELTA configuration. DOL starters are now replacing the use of manual or semi-automatic "star-delta" starters.

Read more: http://wiki.answers.com/Q/What_is_a_DOL_or_direct_on_line_starter_and_how_does_it_work#ixzz1m2iWbKKX

"To start a motor direct on line (DOL) in delta requires approximately 6 to 8 times the full load current of the motor and delivers full torque. Delta places 415v across each of the windings on the motor. A Star-Delta starter starts the motor in Star which places 240v across each winding on the motor. This results in a lower starting current and also a lower starting torque.

Read more: http://wiki.answers.com/Q/What_is_the_advantage_of_a_Star_Delta_Motor_Starter#ixzz1m2lRly8l

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 2 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11
In reply to #1

Re: which conection to motor 5hp or above, star or delta in dol

02/13/2012 3:28 AM

That ↑ cannot be a star-delta starter, as the motor needs 6 leads. The diagram only shows three.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster #1
#2

Re: which conection to motor 5hp or above, star or delta in dol

02/11/2012 12:05 AM

You can connect up to 45 Hp with DOL starter,even though star delta is recommented.

Register to Reply Score 1 for Off Topic
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#3

Re: which conection to motor 5hp or above, star or delta in dol

02/11/2012 12:24 AM

If starting current in DOL/across the line starter is high you may use a shunt capacitor or auto transformer starter to avoid switching surge during changeover from star to delta.

__________________
pnaban
Register to Reply Score 1 for Off Topic
Commentator

Join Date: Oct 2011
Posts: 95
#4

Re: which conection to motor 5hp or above, star or delta in dol

02/11/2012 12:41 AM

The DOL starter which is commonly available in the market are not the one shown in the drawing of Mr. SolarEagle. The one in the drawing is an advanced version of DOL, which is better than star-delta starter.

It is advised to use Star-Delta starting for motors above 5HP. This is to limit the high staring current of motor, which in turn cause a voltage fluctuation in the whole system.

Motor connection is always DELTA , to get maximum output from motor.

Register to Reply Score 1 for Off Topic
2
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5

Re: which conection to motor 5hp or above, star or delta in dol

02/11/2012 2:04 AM

DOL can be used on large motors so long as the supply is substantial enough. The biggest I've installed was 800HP. As to the connection being star or delta depends on the supply voltage.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#6
In reply to #5

Re: which conection to motor 5hp or above, star or delta in dol

02/11/2012 6:31 AM

Correct answer.

The size of your supply will determine the method you use to start your motor.

In the first few seconds the motor can easily draw 8 times its normal running current. This temporary overcurrent will cause your supply voltage to dip - could cause brown outs - might in turn cause other equipment to trip out.

In your capacity as engineer you should know the magnitude of your supply.

another thing to be aware of is the voltage rating of the motor. It might be wound such that in star its good for 690V and 400V in delta. This should be on the name plate.

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#8
In reply to #6

Re: which conection to motor 5hp or above, star or delta in dol

02/11/2012 8:58 AM

Why do you want 690V rating for star connection,if phase to phase voltage is 400 in delta connection?.

__________________
pnaban
Register to Reply Score 1 for Off Topic
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#7

Re: which conection to motor 5hp or above, star or delta in dol

02/11/2012 8:36 AM

It depends on your motor and where you live. In the USA and Canada the majority of electric motors under 100 HP are factory built as double wye 9 lead connection types for 230/460 VAC input which does not give you a choice on how you set them up.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#9

Re: which conection to motor 5hp or above, star or delta in dol

02/11/2012 3:34 PM

Everyone except tcmtech has, I believe, misinterpreted your question. As I see it, you have a motor, which you intend to start via a DOL stater, but it has two connections available INSIDE of the motor; Star or Delta. This would be because it is a dual voltage motor. Being that you used the term DOL, I can assume you have an IEC motor, in which case it will be 230/400V (or 220/380 or 240/415, it's all the same really).

If your supply voltage is the lower one, i.e. 230V nominal, you connect the motor in the Delta configuration.

If your supply voltage is the higher, i.e. 400V nominal, then you use the Star configuration.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User

Join Date: Mar 2011
Location: oz
Posts: 252
Good Answers: 10
#10

Re: which conection to motor 5hp or above, star or delta in dol

02/11/2012 3:45 PM

G.A No.9, I have seen many motors burn because they were connected star or Delta because of size , but it is very clear on the motor nameplate the method of connection depending on supply voltage.

Register to Reply
Register to Reply 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); arifkunnath (1); eltech (1); JRaef (1); pnaban (2); PWSlack (1); silverfox (1); SolarEagle (1); tcmtech (1); TonyS (1)

Previous in Forum: Vector Group of a Transformer?   Next in Forum: Induction Motor

Advertisement