Why some control valves have been designed for the process inlet from the top side of the valve body with a balance plug, as usually it is from the bottom.
Re: Control Valve
02/18/2012 9:36 AM
You have a valve designed for the southern hemisphere.
Probably because a customer wanted it that way, or the process dictates it.
Re: Control Valve
02/18/2012 11:47 PM
Dear,
Thank you for the comments.
There must be some technical reason's, other than these known ones and I am searching for that.
Rgds.
Re: Control Valve
02/19/2012 6:40 AM
These valves open while moving downwards and close during upwards movement. These are called reverse acting valves. They are normally spring to close and air to open type. The system pressure works against the closing of the valve. Here valve opening time should be short and is more important than closing time and should be used in such requirements.
Re: Control Valve
02/19/2012 6:51 AM
Dear,
Thankyou for the comments.
My question is with regards to the valve body not the actuator.
Rgds.
Re: Control Valve
02/19/2012 11:42 AM
On any normal application, the fluid enters from the bottom of the valve disk against the closing force (force exerted by air). But if reversed, say fluid enters from the top of the disk, the fluid pressure (force) adds to closing force exerted by air. If an application calls for positive closing (besides controlling), may the later is preferred.
Re: Control Valve
02/19/2012 4:25 PM
Arif,
this is often done to get a better "flow" of the medium. (noise reduction)
The medium expands from one side of the plug to the other side.
In reverse flow there is more space for the mediun to expand, only you need more power to open the valve (bigger actuator), to compensate this you can use a balanced plug.
Only if it's impossible, it will never happen
India - Member - Naveen Menon Engineering Fields - Instrumentation Engineering - Naveen Menon
Re: Control Valve
02/19/2012 11:47 PM
Hello Arif
Flow over the plug or under the plug in case of Globe valves and Shaft upstream abd downstream incase of Butterfly valves
Over the plug is used to ensure flow assists in valve shutoff. Shaft Upstream must be selected if the actuator is sized for a shutoff pressure lower than maximum upstream pressure,
Re: Control Valve
02/21/2012 6:26 PM
In addition to the answers already given, you may find good information in the Fisher Control Valve Handbook.
All the best.
Re: Control Valve
02/21/2012 11:46 PM
Dear,
Thank you for your guidance.
Rgds.