Can anyone give clear picture about the difference between D/A Trim, Scaled D/A Trim option in Hart Calibrator (rosemount 275 model)
1) I know D/A TRIM means calibrating transmitter output section(digital to analog) ie 4-20mA. Is it correct?
2) Then what actually SCALED D/A TRIM option in HART calibrator?
Re: Difference Between D/A Trim, Scaled D/A Trim Option in Hart Calibrator
02/24/2012 5:14 PM
"Scaled D/A Trim:
Scaled D/A Trim is a feature that allows HART® communications users to trim a smart transmitter's 4-20 mA
output using a different analog scale to measure the loop current. For example, an I/O resistor is commonly
placed in series with the two wire 4-20 mA loop to convert the current signal into a voltage signal for use by
the DCS. By measuring the voltage across the I/O resistor, the loop current value can be obtained by
dividing the voltage by the resistor value. Scaled D/A Trim allows the user to enter this voltage directly
instead of having to convert it into the actual current value. During the trim function, the transmitter output is
set to a fixed output (first 4 mA and then 20 mA). The user is prompted to enter the meter reading using the
analog scale selected by the user. The transmitter D/A calibration trim is then adjusted to obtain the correct
meter reading. The resulting calibrated loop delivers a precision voltage signal to the DCS."
http://www.meriam.com/pdf/Manuals/MFT%204000%20400%206.pdf
Good Answers: 176
02/24/2012 7:50 PM
GA for that excellent explanation, one that is not documented in any of the 275/375/475 communicator documentation.
02/24/2012 5:16 PM
One is a gain adjustment, the other is an offset adjustment. With g and o being gain and offset the equation will be y=gx+o or y=g(x+o). Read your documentation to find out which method was used.