Control Valve Sizing

02/25/2012 4:44 AM

Dear All,

Please explain me about how control valve sizing to be done , what are all the parameters needed , what is the formula for doing that.

Regards

Khwaja

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Aug 2010
Location: Wales, UK
Posts: 391
Good Answers: 18
#1

Re: Control Valve Sizing

02/25/2012 6:52 AM

Hi,

A good starting point is to know, what is going through the valve (water, air, oil,...) , how much (litres per minute ...), at what pressure (psi, bar,...) and the environment the valve is in(indoors, outside, explosive or corrosive, ...)

Best regards

John

__________________
Best advice I can give as you get older "Never miss an opportunity to relieve yourself"
Register to Reply
2
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Control Valve Sizing

02/25/2012 11:28 AM

Many control valve manufacturers have good catalog or online information about Cv (or Kv), which is used to determine flow rate and pressure drop.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Dec 2008
Location: Australia
Posts: 143
Good Answers: 24
#4

Re: Control Valve Sizing

02/25/2012 9:32 PM

Hi Khwaja,

This is a very complex task.

The easiest way - without going through all the thoery and understanding, is to firstly determine your limits of duty (ie the control valve needs to control between a maximum and minimum points). So you need to define the maximum flow/pressure duty points, and the minimum flow/pressure duty point.

Then simply use the manufacturer to determine suitable valve for accurate control between your system max/min duty points. They are the experts, and they also know the Cv of thier valves accurately.

Hope this helps,

Kind Regards,

Anthony

Register to Reply Score 1 for Good Answer
Member

Join Date: Jan 2012
Posts: 6
#5

Re: Control Valve Sizing

02/26/2012 12:09 AM

Dear All,

Thanks for your infos.

khwaja

Register to Reply
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard