Tap Changer on Transformer

03/02/2012 12:34 AM

Suppose I have 6 units of generators that feed a busbar. From the busbar the voltage will be stepped up via 4 units of transformers.

Can I take out all of the tap changers from the transformers? As the voltage regulation will be done by the generators?

Register to Reply
Pathfinder Tags: Tap Changer of Transformer
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Tap changer on transformer

03/02/2012 1:59 AM

Yes & NO

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Commentator

Join Date: May 2011
Posts: 80
#2

Re: Tap changer on transformer

03/02/2012 2:31 AM

And what does it mean?

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#3
In reply to #2

Re: Tap changer on transformer

03/02/2012 3:15 AM

It means that from the dribble of information provided, a torrent of questions will be needed to ascertain a viable answer.

Are you frightened of using words or something?

__________________
Good moaning!
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: Tap changer on transformer

03/02/2012 3:22 AM

If they already exist, why would you bother to take the tap changers out? Even if unneeded, they won't hurt anything.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Commentator

Join Date: May 2011
Posts: 80
#5
In reply to #4

Re: Tap changer on transformer

03/02/2012 4:03 AM

@ Tornado

Actually, I'm going to install 18 units of 2500 kVA transformer. If I order them without tap changer, the price will go down more than USD 14.000. That's the reason I want to take it out.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6

Re: Tap Changer on Transformer

03/02/2012 12:16 PM

Get an engineer (or doctor) to look at your problem. Before you make a very expensive mistake.

I think the doctor is the better option because it will be cheaper to fix your imagination.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Commentator

Join Date: May 2011
Posts: 80
#9
In reply to #6

Re: Tap Changer on Transformer

03/04/2012 9:15 AM

Stop giving worthless comments!

Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#10
In reply to #9

Re: Tap Changer on Transformer

03/04/2012 12:58 PM

You're OP

Suppose I have 6 units of generators that feed a busbar. From the busbar the voltage will be stepped up via 4 units of transformers.

Can I take out all of the tap changers from the transformers? As the voltage regulation will be done by the generators?

Post #5

Actually, I'm going to install 18 units of 2500 kVA transformer. If I order them without tap changer, the price will go down more than USD 14.000. That's the reason I want to take it out.

If you can't make your mind up how do you expect any one to take you seriously?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Commentator

Join Date: May 2011
Posts: 80
#12
In reply to #10

Re: Tap Changer on Transformer

03/04/2012 8:48 PM

Would it make any difference between 4 and 18 transformers?

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#7

Re: Tap Changer on Transformer

03/02/2012 3:58 PM

Quote "Actually, I'm going to install 18 units of 2500 kVA transformer. If I order them without tap changer, the price will go down more than USD 14.000. That's the reason I want to take it out."

Are you referring to a tap changer or transformers with taps? Big difference.

Register to Reply
Commentator

Join Date: May 2011
Posts: 80
#8
In reply to #7

Re: Tap Changer on Transformer

03/03/2012 12:36 AM

@ wareagle
It's transformer with the usual +/- 2 x 2.5% tap

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#11
In reply to #8

Re: Tap Changer on Transformer

03/04/2012 1:21 PM

There are just too many unknowns in the stated system to be able to say it is safe to take out the transformer tap changers and rely on the generator regulation.

A proper study and assessment of the customer's system and requirements is necessary (and worthwhile) before the order is placed with the transformer supplier.

Don't forget to get approval from the client (especially if the client originally specified or expects tap changers), after all you cannot put them in later after the transformers are built.

__________________
jack of all trades
Register to Reply
Commentator

Join Date: May 2011
Posts: 80
#13
In reply to #11

Re: Tap Changer on Transformer

03/05/2012 12:36 AM

The SLD looks like this:

The distance between all of the generators and 11 kV bus is around 30 m.

I'm sure the generator can maintain the 415 V at the output, and therefore 11 kV at the main busbar. That's the reason I want to take out the off load tap on all of the 2500 kVA transformer.

Register to Reply
Anonymous Poster #1
#14
In reply to #13

Re: Tap Changer on Transformer

03/05/2012 7:37 AM

I will supply you all 18 transformers with tap changing without the additional cost of USD 14,000.

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#15
In reply to #13

Re: Tap Changer on Transformer

03/05/2012 5:37 PM

Given the information provided I am a little concerned that tap changers may be only one of your problems. What you are describing resembles powering an 11kV power grid of a small town, city or large industrial park using generators in an island mode (complete isolation from the power grid) in the event of loss of (or rarer - lack of) grid supply.

I have only done one of these before and that was only 1-4 generators at 2500kVA total for a small town, and even then it was complex enough with all the CT's, VT's, circuit breaker, protection relay, load sharing and synchronization, etc required. Your project is much, much more complicated.

And yes my 2500KVA transformer was ordered with a tap changer and it was used for fine-tuning the output voltage.

I am only aware of a few sites in the world that currently use a system this large. Are you able to provide more information on this rather large application?

Is this an Australian mining site application where the generators are being used for black-start island-mode emergency supply?

__________________
jack of all trades
Register to Reply
Commentator

Join Date: May 2011
Posts: 80
#16
In reply to #15

Re: Tap Changer on Transformer

03/06/2012 2:00 AM

Yes! It's an island mode of the main supply for Australian mining. The generators aren't used for black-start only, because they didn't connect it to other power supply.

When you say 'fine-tuning', it means for all of the transformers? Then you have to shut down the supply for "small town"? Why can't the generator do the voltage regulation?

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#17
In reply to #16

Re: Tap Changer on Transformer

03/06/2012 1:07 PM

I think the reasoning behind it was that the voltage regulation was still handled by the generators but the fine tuning (up to +/-5% output voltage step changes) was handled by the transformer tap changer. I think the main reasons for having it were to increase the output voltage to compensate for voltage drop. I think we did need to change the tap to increase the voltage during commissioning.

I don't know much about the generator output voltage regulation, it may be that the generator output voltage cannot be adjusted that much. The generator literature may offer some insight.

Yes! It's an island mode of the main supply for Australian mining. The generators aren't used for black-start only, because they didn't connect it to other power supply.

I thought so <cringe>. The fuel storage facilities and monthly bill must be enormous. Did the customer not look at other (cheaper and greener) alternatives such as a small natural gas power station?

__________________
jack of all trades
Register to Reply
Participant

Join Date: Mar 2012
Posts: 2
#18

Re: Tap Changer on Transformer

03/10/2012 2:58 PM

It mainly depends upon the grid to which you are connecting. If the nearest recieving station has frequent load (reactive) changes due to more distribution lines feeding end level customers and the load flows are not controlled ,the voltage get more fluctuations. Indirectly it can be determined by voltage used for transmision. Generator transformer used at 400kv level wont use OLTC due to cost reduction and stability of grid voltage.

Register to Reply
Participant

Join Date: Mar 2012
Posts: 2
#19

Re: Tap Changer on Transformer

03/10/2012 3:20 PM

It mainly depends upon the grid to which you are connecting. If the nearest recieving station has frequent load (reactive) changes due to more distribution lines feeding end level customers and the load flows are not controlled ,the voltage get more fluctuations. Indirectly it can be determined by voltage used for transmision. Generator transformer used at 400kv level wont use OLTC due to cost reduction and stability of grid voltage.

Voltage controll by AVR of generator is possible upto certain limits only. After connecting it with a grid. The grid voltage cannot be controlled by your generator avr, it depends on VAR demand in the grid because voltage & VAR is related. Since you actually controlls the VAR output of your generator which cannot meet the system demand, so there is possibility of Under voltage trip. this can be controlled upto some level by using Tap changers.