Furnace Oil Piping

03/03/2012 12:14 AM

hello,

We are installing oil (HFO) fired boiler of 10 TPH , 12 kg/cm2 working pressure .

We have tank farm area where we are storing furnace oil and also have a day tank near boiler. Main storage is 500 meter far from day tank.

Now Furnce oil piping is to be laid down with electric tracing line.Fuel supply will be pumped from main storage tank to day tank at a pressure of 7 kg/cm2 & temperature 90 DEg C approx.

My question is that which pipe should we use for laying between main storage & day tank , Should it be SEAMLESS OR ERW (Gr B Is 1239).

I have read the ASME B 31.1 but it is not mentioned specifically about pipeline for furnace oil.

Also i want to know which standard should I follow for above pipeline.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#1

Re: Furnace oil piping

03/03/2012 3:01 AM

What is the diameter of the line, Uncle?

__________________
Good moaning!
Register to Reply
Power-User

Join Date: Dec 2010
Posts: 377
Good Answers: 20
#2

Re: Furnace Oil Piping

03/03/2012 11:51 AM

Here is a link for your help.

Register to Reply
Guru
Engineering Fields - Piping Design Engineering - New Member Egypt - Member - Member since 02/18/2007

Join Date: Feb 2007
Location: Cairo, Egypt
Posts: 1733
Good Answers: 248
#3

Re: Furnace Oil Piping

03/04/2012 10:33 PM

This pipe line may be sized within the range of NPS 2 up to 6, therefore it is better to use a seamless piping system.

__________________
It is better to be defeated on principles, than to win on lies!
Register to Reply
Commentator

Join Date: Jun 2011
Posts: 77
Good Answers: 8
#4
In reply to #3

Re: Furnace Oil Piping

03/04/2012 11:26 PM

I agree with Abdel, go with seamless as you do not want joints underground (they will eventually leak). Do not use polyethylene or its cousins, as the material will leak out the walls over time. I would also avoid using any Fe-based metal as it will corrode over time and the piping will need to be replaced. Although a bit spendy, copper should do fine as long as you have the copper isolated against galvanic reaction.

Register to Reply
Power-User

Join Date: Nov 2008
Location: Port Glasgow, Free Republic of Scotland
Posts: 360
Good Answers: 30
#9
In reply to #4

Re: Furnace Oil Piping

03/07/2012 5:00 AM

I am surprised at this comment. In over 20 yrs I have never seen a copper line in this service. Steel pipes do corrode (you only need carbon steel for this service) but properly designed you make allowance for the loss of wall thickness due to corrosion over the life of teh user. ie if you need a wall thickness of 5mm based on pressure calculations and the corrosion estimate is 0.1mm/yr you need a minimum of 7mm wall thickness.

Copper is very rarely used on oil and gas facilities for utility or process systems. Off the top of my head you use it in instrument air fittings but only the last few cm's at the user. A simple Carbon steel line will be far more robust and although you will need to make allowance for the corrosion this is standard practice and acrbon steel pipe is widely available and cheap

__________________
Free advice guaranteed or your money back
Register to Reply
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#5

Re: Furnace Oil Piping

03/05/2012 2:03 AM

500 m length, India - No problem except end January-end February winter nights will become nightmares.The Cost pipelines + electrical heat tracing + power to pumps will all add up to the cost of HFO to generate steam. Already HFO Vs Gas is 60% + higher/T steam. This will increase your cost production.

I will suggest that you make a pit 6ft x 6 ft x 6 ft near the Boiler House, fit a Ms De-canting Tank with electrical heater . Install a small 1 Hp gear-pump x 2 sets to transfer HFO from this De-canting tank to your Day-oil tank with transper pipes electrical/steam heat traced & insulated . Have a small Tanker on wheels (or the type selling kerosene to slump areas and donkey-driven, common in India/Pakistan) to transfer HFO from Tank farm to the De-canting tank. Simple system-no nightmares!

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply
Anonymous Poster #1
#6

Re: Furnace Oil Piping

03/05/2012 10:57 AM

ERW Pipe - IS - 1239 CLASS C is the most economical, safe and approved for this application.

The temperatures are not very high, may be around 50-60 degree C.

For all types of Fuel lines, IS - 1239 Class C pipe is fine.

Register to Reply
Power-User

Join Date: Aug 2009
Posts: 100
Good Answers: 8
#7

Re: Furnace Oil Piping

03/06/2012 1:28 AM

I would agree w/the others that seamless would be best if possible. I would also advocate using a double wall system like enviro-flex or something similar. I would be curious to know if you have to pump or can siphon. Controlling the flow can be a delicate problem. Simple is usually better. If you have to pump from the lower end you might consider a mechanical stop as well as a telemetry/level system for safety.

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#8

Re: Furnace Oil Piping

03/06/2012 1:50 AM

I have read the ASME B 31.1 but it is not mentioned specifically about pipeline for furnace oil.

Furnace oil is reticulated andmanaged the same as fuel oil for any other purpose. Don't expect to find specific reference to furnaces. Follow the directives for fuel oil.

Customise it in accordance with the relevant industry standards to suit your application/environment.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Register to Reply 9 comments
Copy to Clipboard

Users who posted comments:

Abdel Halim Galala (1); Anonymous Poster (1); Crabtree (1); ducon (1); JonathanG (1); Mukesh0861 (1); simonsd (1); Sourdough (1); Wal (1)

Previous in Forum: Looking for Coefficient of Friction for Base Rail   Next in Forum: HDPE Long Term Hydrostatic Strength

Advertisement