Fans, Chamber Size & Static Pressure--Co-relationship/How to Control?

03/06/2012 11:31 PM

Once I had a peculiar problem erecting a blast freezer but could find no satisfactory explanation to the problem other than that it was due to built up of static pressure so much so that I had to redesign it to work.

It was a masonry-built insulated chamber with single entrance, approx size 8 ft by 14 ft long by 6 ft high fitted with an forced-air finned evaporator (for ammonia as refrigerant) 10 feet long open in the front and two axial fans fitted at the back to blow air through to cool fish stacked for freezing in the front. The blast freezer was doing well before I thought of reducing its height from 12 feet to 6 feet with the mind that that will save me on electricity as well as reduce the freezing time. All being done when i ran the blast freezer I was shocked to find that there was no air movement there!! Absolutely no air even though two heavy 5 HP motored fans pushed the air through!!

Could someone tell me what and where I went wrong?? I rested with the idea that some static pressure had stalled the air movement and failed my experiment. What other measures could I have taken to run the blast freezer with the lowered height?? What should be the critical/optimum height of a blast freezer or a hot-air dryer for forcing out air through fans in a closed chamber??

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Associate

Join Date: Nov 2011
Posts: 34
Good Answers: 2
#1

Re: Fans, Chamber Size & Static Pressure--Co-relationship/How to Control?

03/07/2012 11:24 PM

It seems that you have either Blocked the Return Air Flow to the Fans or the Exhaust stream from the Chamber, when you reduced the height of chamber.

In any comfort air conditioning system, we use approx. 90% return air and 10 % fresh air which may vary depending on the application. Hence approx. 10% air is exhausted out to atmosphere.

I suggest to provide a return air ducting or passage in the chamber and also an outlet for exhaust. Some fresh air is always needed for any airconditioning system to maintain proper ventilation. The use of return air will save energy.

Hope it HELPS.....

Register to Reply
Power-User

Join Date: Nov 2011
Posts: 287
#3
In reply to #1

Re: Fans, Chamber Size & Static Pressure--Co-relationship/How to Control?

03/07/2012 11:43 PM

Thanks but the present case relates to a blast freezer operating at minus 25/30C and there is no provision or need to exhaust some air.

I also place a sheet above the evaporator grid to act as a overhead duct for aligning the air flow from suction to discharge and back but even this didn't work. To my astonishment, with heavy fans operating I could not see them stir even a leaf!! That was amazing and the thought still haunts my mind.

For your information the evaporator coil/grid discharge was fully open (as you find in a home window Air conditioner) while the suction air was let pass through the fans only. Failing to get this work I even reduced the discharge by placing a metal sheet against it but to no avail. It seemed as if some black magic was holding down air movement!

Science surely is magic in itself...I love it!!

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member India - Member - New Member

Join Date: Aug 2008
Location: City of destiny, INDIA
Posts: 775
Good Answers: 67
#2

Re: Fans, Chamber Size & Static Pressure--Co-relationship/How to Control?

03/07/2012 11:41 PM

Lot of information missing. What was the static and total pressure before and after? First you stated chamber hight was 6 feet but later you say "I thought of reducing its height from 12 feet to 6 feet". What is volume flow rate, temp, TR etc? A simple line diagram would help more.

Register to Reply
Power-User

Join Date: Nov 2011
Posts: 287
#4
In reply to #2

Re: Fans, Chamber Size & Static Pressure--Co-relationship/How to Control?

03/07/2012 11:49 PM

The blast freezer was working efficiently at 12 feet height but was taking a bit too long time. So I thought of reducing the chamber size to make it keep more cooling and to give the target temperature sooner. I did that and that was kinda my fruitcake moment. I badly failed.

As for other factors you pointed out to we can assume them to be constant before and after except ofcourse the reduction of size of the blast freezer chamber which really matters.

Register to Reply
Power-User

Join Date: Apr 2007
Posts: 414
Good Answers: 19
#5
In reply to #4

Re: Fans, Chamber Size & Static Pressure--Co-relationship/How to Control?

03/08/2012 2:14 AM

Axial fans respond to the increased load imposed by constrictions on either their inlet or outlet side by requiring increased power and reducing their rotational speed. If you had cut off the air on either side of the fans, you would be alerted by a change in the sound as they run, or by tripped circuit breakers or blown fuses if the additional load is sufficiently great.

It's possible that air passage through the evaporator is blocked by ice. That would certainly restrict circulation. An accurate sketch or diagram would reveal other possibilities. A written plan accompanied by drawings is a good beginning for any project of this kind. If you skipped that step, it's still not too late.

Register to Reply
Power-User

Join Date: Nov 2011
Posts: 287
#11
In reply to #5

Re: Fans, Chamber Size & Static Pressure--Co-relationship/How to Control?

03/08/2012 2:35 PM

I take your point on usefulness of drawings and i will see if can post any.

Here's an excerpt from a reply I posted here to an other member...and hope it will help clarify the setting..

'''The air is thrown into a finned evaporator from axial fans attached to it at the back and discharged air comes out from the opposite open side of the evaporator (ie from the front). Product to be blast frozen such as fish is placed right in front of the evaporator grid. The strong air thrust coming through the evaporator hits the fish and freezes it down to about minus 30 degrees in 10 hours or so, depending upon the thickness of the fish , its initial temperature and the way it is stacked. There is only one door located right in front of the evaporator grid which serves both as entrance or exit .''

Register to Reply
Associate

Join Date: Nov 2011
Posts: 34
Good Answers: 2
#6
In reply to #4

Re: Fans, Chamber Size & Static Pressure--Co-relationship/How to Control?

03/08/2012 3:06 AM

You are having a situation similar to the one in which the discharge damper of the Fan is fully closed. Fan is running, is drawing current and is also developing static pressure, but NO FLOW..

For a trial just let some air exhaust in the atmosphere and see the flow..

Hope it helps

Register to Reply
Power-User

Join Date: Dec 2007
Posts: 177
Good Answers: 6
#7

Re: Fans, Chamber Size & Static Pressure--Co-relationship/How to Control?

03/08/2012 7:49 AM

Two thoughts- evaporator iced up in fins and not readily apparent blocking airflow or blower motors running backwards(if 3 phase and wiring was disconnected/reconnected during work)

Register to Reply
Participant

Join Date: Feb 2012
Posts: 3
#8

Re: Fans, Chamber Size & Static Pressure--Co-relationship/How to Control?

03/08/2012 10:43 AM

maybe your 2 fans make to and from airflow if u tampered with electricity

Register to Reply
Power-User

Join Date: Nov 2011
Posts: 287
#12
In reply to #8

Re: Fans, Chamber Size & Static Pressure--Co-relationship/How to Control?

03/08/2012 2:46 PM

the fans were not even touched!

they operated perfectly well before the rood height was lowered. After I raised the room height they again became functional as ever!

Register to Reply
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#9

Re: Fans, Chamber Size & Static Pressure--Co-relationship/How to Control?

03/08/2012 11:58 AM

Don't look for "Exotic" solutions, look for basics first. Was the evap moved when height was lowered. If so, check operation and rotation of both fans. Don't just look. One fan operating will make the other spin, or one runnig backward will circulate air round and round in the fan area and never discharge it to the box. -- JHF

__________________
If it's too good to be true, it probably isn't
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 287
#10
In reply to #9

Re: Fans, Chamber Size & Static Pressure--Co-relationship/How to Control?

03/08/2012 1:24 PM

thanks.....but

Allow me to inform all here that

1. No, the evaporator was not moved.

2. Fans were not touched.

3. Evaporator was not choked. In fact it was clean and dry before operation.

4. Fan rotation was correct.

5. No electric changes were made.

6. Suction and discharge openings were clear.

7.The blast freezer was also operated with a 4 ft wide door open.

In short, nothing was changed except the height of the blast freezer chamber roof which was lowered. The ''Exotic' or the 'Occult'' side to this that the air stopped to move and even two heavy fans couldn't even move a straw!!

Register to Reply
Associate

Join Date: Nov 2011
Posts: 34
Good Answers: 2
#13
In reply to #10

Re: Fans, Chamber Size & Static Pressure--Co-relationship/How to Control?

03/08/2012 11:50 PM

Hi,

I am of the opinion now that the 2 Fans are working against each other with the Reduced Volume of Air available for Suction.

You must take a trial with ONLY 1 FAN RUNNING AT A TIME and see IF FLOW OF AIR IS RESUMED.

Low Buffer Volume for the Suction side may be a possible cause when you reduce the height of chamber.

Hope it solves yr problem,.....

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2011
Posts: 287
#14
In reply to #13

Re: Fans, Chamber Size & Static Pressure--Co-relationship/How to Control?

03/09/2012 12:16 AM

Thanks, I think that's a good idea.

Yes, it appears that the fans are too big for the reduced space and starved of suction air, hence no discharge. However, only a test will tell.

Register to Reply
Power-User

Join Date: Feb 2010
Posts: 103
Good Answers: 2
#15

Re: Fans, Chamber Size & Static Pressure--Co-relationship/How to Control?

03/20/2012 5:34 PM

I would start by requesting the the vendor of the evaporator to get an engineer from the evaporator manufacturer to inspect the installation. If the product being frozen is stackerd tightly to the lowered ceiling it could be the fans, propeller type I presume, are at their "cut off" point. Propeller fans are very sensitive to back pressure.

Get the help you paid for when you bought the evapoprator. I cut my teeth in the HVACR industry with a manufacturer and it seemed that was where the buck always stopped when one our products didn't perform, regarless of whose fault it was.

Good luck...Lou Bindner

Register to Reply
Power-User

Join Date: Nov 2011
Posts: 287
#16
In reply to #15

Re: Fans, Chamber Size & Static Pressure--Co-relationship/How to Control?

03/21/2012 4:32 AM

There is no after-sales-service available for the equipment, no warranty either. But the fact is that the evaporator was performing well before the ceiling was lowered.

Stacking was not the problem nor the back pressure on the fans...because I ran the blast freezer both in vacant and stacked positions but got the same odd result. The two heavy fans wouldn't even move a feather!! But when i pulled off the lowered ceiling and got back to the initial height all went well.

Register to Reply
Register to Reply 16 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

alex pol (1); bubbapebi (1); Circuit Breaker (1); kkgupta (3); Lou Bindner (1); lrsheldon (1); mazhur (7); pritam (1)