DYN 11 Tx. Neutral and Ground

03/20/2012 3:41 PM

we have a 10KVA 3phase 50HZ Transformer with:- A1-B1-C1=477V

A2-B2-C2=415V

A3-B3-C3=353V and

a-b-c=230vac which is used to supply various UPS, RTU'S and CPU'S. People using the office computers sometimes experience electric shock when in contact with the metal body of the computers.There is voltage of about 113vac between neutral and ground on the secondary side. What do you say about this?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: DYN 11 Tx. Neutral and Ground

03/20/2012 8:49 PM

Irrespective of any N-G voltage, either the computers should be double-insulated (so there is no possibility of any mains voltage coming into contact with any exposed metalwork), or all exposed metalwork should be grounded.

If people using the computers are getting shocks when touching them, either it's static (that they've accumulated while walking over carpets etc.) or there's something seriously wrong with your wiring.

Find a qualified electrician, and get it checked.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Score 1 for Good Answer
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#2

Re: DYN 11 Tx. Neutral and Ground

03/20/2012 10:32 PM

poor grounding, or neutral not bonded to ground on the secondary of the transformer. last possibility is instability between the step up and step down transformers, possibly because they lack good grounds or a common ground between them.

__________________
BSEE but always learning
Register to Reply Score 1 for Good Answer
Participant

Join Date: Mar 2012
Posts: 2
#4
In reply to #2

Re: DYN 11 Tx. Neutral and Ground

03/21/2012 3:25 AM

Is it true that this type of a transformer i.e DYN 11 Type SKTC9 does not have its neutral bonded to the ground on the secondary side? please note that the secondary voltages are as follows:- Live-Neutral=240V

Live-Ground=127V

Neutral-Ground=113V.

Register to Reply
2
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#5
In reply to #4

Re: DYN 11 Tx. Neutral and Ground

03/21/2012 4:13 AM

Neutral point must be efficiently and effectively grounded to avoid this dangerous situation where fatal accident can occur. All metallic enclosures of all electrical equpments must be grounded effectively. It is better to hire qualified electrical engineer for correct electrical installation complying local electrical codes. Also pl. check amount of third harmonic current passing thro' the grounded neutral since there are lots of non-linear loads like computers etc.

Thanks,

Manindra

__________________
Manindra
Register to Reply Good Answer (Score 2)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#8
In reply to #5

Re: DYN 11 Tx. Neutral and Ground

03/21/2012 8:08 AM

GA

First good answer reading down from the top.....the situation could be dangerous as it is at this time, it looks as though the original installer did not do a good job.....he should use another company.....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Active Contributor

Join Date: Mar 2010
Location: Maine
Posts: 14
Good Answers: 2
#3

Re: DYN 11 Tx. Neutral and Ground

03/20/2012 10:32 PM

113 volts from neutral to ground?? Say what?? Starting to sound like you have an early retirement plan for some of your workers....

Lets try a simple test. Hook a small 110volt light bulb from the chassis of one of the computers to some external ground. A water pipe will do. Does it light up? Even a little? If so, there's probably enough voltage/current to kill someone.

If that is the case, then you really need to do something about this quick. Find a competent Electrician/Engineer or whatever you call them in your neck of the woods and get this problem taken care of.

So far, I do not see enough info to offer any guesses as to what is wrong, or has gone wrong with your system - But get it FIXED!!

Register to Reply Score 1 for Good Answer
Commentator

Join Date: Oct 2011
Posts: 95
#6

Re: DYN 11 Tx. Neutral and Ground

03/21/2012 5:02 AM

I observed the electric shock on body of some equipment when phase and neutral connections are reversed. That is , in a socket out let if connect phase and neutral reverse and plug an iron box , there is a chance to get electric shock from iron box. In this case it is not related to the transformer.

Register to Reply
Active Contributor

Join Date: Nov 2011
Posts: 19
#7

Re: DYN 11 Tx. Neutral and Ground

03/21/2012 5:43 AM

I will request you to check the voltage between phase and earth as well, if it is approximately 110 -120 volt, it indicates that neutral is floating with respect to phase.

In such cases you have earth the neutral of the isolation transformer if installed in between or the neutral coming out from the UPS is to be grounded.

This is based on the similar problem faced by me in the past.

Subhash

Register to Reply
Active Contributor

Join Date: Mar 2012
Posts: 22
Good Answers: 1
#9

Re: DYN 11 Tx. Neutral and Ground

03/21/2012 8:37 AM

hmmm... i completely understood the problem you are facing.

Firstly... there is failure in the grounding system. This means that the ground wire is floating and not been connected to any earth pit.

Secondly... As u said that the electric shocks are found in the computers. Please check whether the power to computers is fed from electronic spike busters. Many times Electronic spike busters malfunction.

What you have to do is;

1) Keep the tester on the ground line continously (which will glow for 100V also) and remove the plugs of spike busters or any other equipments having ground pin.

2) During this checking whenever the glowing tester goes OFF, check which plug was removed.

3) Rectify that particular spike buster or equipment.

hope this will help u in tracing the problem.

__________________
"Learning new things everyday keeps u healthy"
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#10

Re: DYN 11 Tx. Neutral and Ground

03/21/2012 9:12 PM

so, to sum up, probably either

1. neutral not bonded to ground

2. floating ground, as Yooogs said

3. bad spike buster [or UPS powering computers]

__________________
BSEE but always learning
Register to Reply
Register to Reply 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

1capybara (2); Andy Germany (1); arifkunnath (1); DAVID MATU (1); JohnDG (1); manindra (1); oldfefan (1); SUBH_ASHD (1); yooogs (1)