Commentator

Join Date: Dec 2006
Posts: 88

Breakers for Motors

05/07/2007 5:43 AM

Dear Sir,

What is the criteria has to be used in selecting breaker size of a motor? If the motor capacity is 75 kVA (3 ph 400V) can I use 120 A MCCB with an 3 X In, softstater (30 Sec starting time)?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Breakers for Motors

05/08/2007 12:09 AM

That answer is going to be dependent upon your local installation codes.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Anonymous Poster
#2

Re: Breakers for Motors

05/08/2007 2:29 AM

The breaker should be sized as close to the load as possible without causing nuisance tripping. The motor capacity is only peripherally associated with the breaker size, soft start notwhithstanding. The characteristic of the driven load is the critical issue; the current pulled through the starter and breaker and the time to full speed. A simple formula would necessarily oversize the equipment.

Register to Reply
Power-User

Join Date: Nov 2006
Location: SE MI USA
Posts: 105
#3

Re: Breakers for Motors

05/08/2007 5:37 AM

Breaker with a soft start? The smarter soft starts don't necessarily require a protection between it and the motor. With NFPA 70e, we've moved back to fuses and generally we protect the soft start inline with class J fuses at 150%.

Register to Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#4

Re: Breakers for Motors

05/08/2007 8:15 AM

The National Electrical Code governs circuit breaker size in the US. For instantaneous-trip breakers, the breaker may be rated up to 800% of motor full-load current; for inverse-time breakers, the breaker may be rated up to 250% of full-load current.

Rather than decoding your cryptic question, I will defer to you to make the decision as to whether or not the breaker you ask about will fit the criteria.

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Anonymous Poster
#5

Re: Breakers for Motors

05/08/2007 9:02 AM

The CEC states that you can go as high as 1300% providing that you have followed the rules for motor cabling.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6
In reply to #5

Re: Breakers for Motors

05/09/2007 12:04 AM

That has only to do with the instantaneous magnetic trips. Please refrain from making erroneous statements if you have no idea what you are referring to, it could lead to someone misusing their equipment and starting a fire!

That is why I posted the answer that it really depends on YOUR local code requirements. What I tell you for the US or someone else posts for Canada may mean absolutely nothing for someone in China or India or Lesotho. There are general guidelines that depend totally on the type of "breaker" being used, the available fault current, the design of the entire system etc. etc. etc., but the FIRST place to start is with the local jurisdiction that regulates electrical installations. What is acceptable in one area may be illegal in another.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Active Contributor

Join Date: May 2007
Location: Vermont and Alaska
Posts: 24
Good Answers: 3
#7
In reply to #6

Re: Breakers for Motors

05/09/2007 10:03 AM

I had exactly the same thoughts. I post only to endorse your statement.

Register to Reply
Power-User
Popular Science - Weaponology - New Member Popular Science - Cosmology - New Member

Join Date: Apr 2006
Posts: 261
#8
In reply to #6

Re: Breakers for Motors

05/11/2007 2:20 PM

I just thought that someone should mention that the Manufacturers do
publish the delay curves for their products and in the size and voltage
required some of these products are adjustible.

Register to Reply
Register to Reply 8 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); Bill (1); JRaef (2); jstolaruk (1); Pragmatist (1); Wireman (1)

Previous in Forum: protection   Next in Forum: How would I go about figuring out how to vmod a motherboard?
You might be interested in: Circuit Breakers, pH Electrodes, pH Transmitters

Advertisement