23 MVA Power transformer IR value

03/22/2012 11:16 AM

What is the reference IR values for 18/23 MVA power transformer

core to tank, tank to frame, Frame to core at 25 degree.c

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: 23 MVA Power transformer IR value

03/22/2012 11:27 AM

Sure you are not looking for I2R losses?

Register to Reply
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#2
In reply to #1

Re: 23 MVA Power transformer IR value

03/22/2012 1:11 PM

I think he refers to Insulation Resistance, (a megger test); in which case, I'd know the answer if I was an engineer in charge of such a costly project, OR I had read the manufacturers specs.

Regards

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3

Re: 23 MVA Power transformer IR value

03/22/2012 11:42 PM

1. Doesn't it depend on the voltage?

2. Core, tank, frame...should they all not be earthed ? If so, no IR between them?

Not my field, so, sorry if this is stupid.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#4

Re: 23 MVA Power transformer IR value

03/23/2012 2:08 PM

I'm not sure what you mean by "frame," but the core of the transformer in operation will be bonded to the (grounded) tank. The core must be bonded to the tank in only one place. A core grounding strap, often using a relatively easy to access low-voltage bushing, is provided so that during acceptance testing you can disconnect the strap and do an insulation resistance (IR or "Megger") test.

Per IEEE C57.12.00, the core to ground insulation resistance should be measured at 500VDC for 1 minute. It does not give a value for acceptable IR. Industry rule of thumb is 1 megohm + 1 megohm per kV equipment rating. Since the core is normally grounded, I would use 1 megohm as minimum IR, but typically you will read more.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply