Problem Encountered During Measurement of Energy by a Energy Meter

03/28/2012 4:50 AM

Presently I am a doing a research work and trying to measure amount of energy required to drill a hole on steel with a drill bit size of 10mm. I am using Nanovip energy-meter for this. The experimentation is being done on a 3 phase milling machine with a drilling attachment. I am clapming the current and potential jaws to the respective 3 wires of the power circuit. I am selecting CT ratio of 100 and PT ratio of 10. But after the drilling is done , when I look the software for the amount of current and voltage it has taken for drilling , I find that the voltage column is all zero and hence the energy column is also zero. But in the current column I get the values.

Please anyone pls let me know how to rectify this error ?

Thanking you.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#1

Re: Problem encountered during measurement of energy by a energy meter

03/28/2012 5:12 AM

As a quick fix you could stick a fixed value in the voltage column... dunno if a mill is going to really pull the voltage down much unless you have a dodgy supply...
Del
(Not my field so I reserve the right to be wrong... any how I jus a cat)

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Active Contributor

Join Date: Mar 2012
Posts: 22
Good Answers: 1
#2

Re: Problem encountered during measurement of energy by a energy meter

03/28/2012 5:44 AM

If the energy meter is not faulty, then there will always be a good chance in wrong connection and also in settings.

look into it...

__________________
"Learning new things everyday keeps u healthy"
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3

Re: Problem Encountered During Measurement of Energy by a Energy Meter

03/28/2012 11:01 AM

As others have already mentioned, you most likely have a bad voltage connection somewhere. You're Current Transformer and Phase Transform (CT and PT) ratios are not a capricious value that one can select to fudge a measurement. They are determined by the transformer and attenuation network you are using in this setup. I highly recommend that you use an oscilloscope to measure the voltages entering the energy meter to verify that things are wired correctly and that Phase A gets Current A to measure the correct phase angle.

There is a possibility that you exceeded the input voltage capability of your instrument and damaged circuitry in the energy meter. If the voltage range for the instrument without an attenuator is ±48V and you fed it directly 480 VAC RMS then you have a dead energy meter. This type of mistake can produce exactly the symptoms you've presented.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Problem Encountered During Measurement of Energy by a Energy Meter

03/28/2012 1:40 PM

It's likely simpler than all that.

If you have ONE clamp meter and you are clampping it around ALL THREE conductors at the same time, the values will sum to zero!

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Belgium - Member - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: Aug 2006
Location: Glabbeek, Belgium
Posts: 1480
Good Answers: 28
#8
In reply to #4

Re: Problem Encountered During Measurement of Energy by a Energy Meter

03/29/2012 2:16 AM

This is already answerd by the original poster: The current is measured. it is the voltage which is not measured.

__________________
"Here we are now, entertain us"
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#5

Re: Problem Encountered During Measurement of Energy by a Energy Meter

03/28/2012 3:36 PM

What is the actual current reading and voltage? Get you volt meter and see if the recorder is seeing a voltage reading. Do you actually clamp the voltage jaws around the conductor? Why not make a direct connection?

Register to Reply
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#6

Re: Problem Encountered During Measurement of Energy by a Energy Meter

03/28/2012 4:46 PM

Don't know the specific meter, but is there a DC/AC option?

If it's set on DC, then the average observed voltage in line should be zero. As someone else has suggested, probably a meter setting.

__________________
Just an Engineer from the land down under.
Register to Reply
Guru
Panama - Member - New Member Hobbies - CNC - New Member Engineering Fields - Marine Engineering - New Member Engineering Fields - Retired Engineers / Mentors - New Member

Join Date: Dec 2006
Location: Panama
Posts: 4273
Good Answers: 213
#7

Re: Problem Encountered During Measurement of Energy by a Energy Meter

03/29/2012 12:08 AM

A quick look at the manual for the Nanovip meter tells me that for a balanced 3 phase measurement, one clamps the current meter to one of the conductors (let us designate that as L1), and measure voltage across the other two conductors (let us call these L2 and L3). This confuses me, but I don't know what sort of algorithm the meter is using internally to calculate watts. Anyway, there is also a switch on the front of the meter that selects either single phase or three phase- check that this switch is in the correct position.

The manual does not talk about using a Potential Transformer- their diagrams show direct connection to lines L2 and L3 with standard probes. Maybe you are using a different version of the meter than the manual I am looking at?

Register to Reply
Guru

Join Date: Feb 2011
Location: Atlanta, GA
Posts: 1053
Good Answers: 110
#9
In reply to #7

Re: Problem Encountered During Measurement of Energy by a Energy Meter

03/29/2012 1:13 PM

Clamping an ammeter around one phase is pretty standard, as is using probes on any two wires to measure voltage. I think the OP will need to supply additional details. Seems odd to use a potential transformer on something as small as a drilling machine.

__________________
Think big. Drive small.
Register to Reply
Guru
Panama - Member - New Member Hobbies - CNC - New Member Engineering Fields - Marine Engineering - New Member Engineering Fields - Retired Engineers / Mentors - New Member

Join Date: Dec 2006
Location: Panama
Posts: 4273
Good Answers: 213
#10
In reply to #9

Re: Problem Encountered During Measurement of Energy by a Energy Meter

03/29/2012 1:35 PM

My confusion stems from the manual's instructions to measure voltage across L2 and L3 while measuring current in L1. Of course, they specify that this is for balanced 3 phase only (an animal I have never met in the wild). All of my 3-phase measurements have involved simultaneous measurement of three currents and voltages (either across lines, or line to ground, depending on whether one is dealing with delta or star distribution).

Register to Reply Off Topic (Score 5)
Guru

Join Date: Feb 2011
Location: Atlanta, GA
Posts: 1053
Good Answers: 110
#12
In reply to #10

Re: Problem Encountered During Measurement of Energy by a Energy Meter

03/30/2012 1:24 PM

I think the Nanovip is a simpler instrument that you are accustomed to.

Because it can only measure one phase at a time, the phases must be balanced for the measurement to have much validity. I think (but am not sure) that their picking L2 and L3 is arbitrary, because they assume the lines are balanced.

__________________
Think big. Drive small.
Register to Reply Off Topic (Score 5)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#11
In reply to #9

Re: Problem Encountered During Measurement of Energy by a Energy Meter

03/29/2012 1:49 PM

I agree that most drilling machines do not draw much power. Most drilling machines do not draw a significant amount of power unless something is about to break. There are a few notable exceptions though.

But once again we know next to nothing about the drill or anything that the OP is trying to measure. I have more hope that the 7 train will be extended by this tunnel boring machine than I do that the East Side access will ever be complete. I have more hope that the East Side access will be completed before we find out what the OP is actually doing.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Score 1 for Off Topic
Guru

Join Date: Feb 2011
Location: Atlanta, GA
Posts: 1053
Good Answers: 110
#13
In reply to #11

Re: Problem Encountered During Measurement of Energy by a Energy Meter

03/30/2012 4:57 PM

Wow! If that drill bit in the background is big, let's say 3/4", then those people would have to be really tiny -- maybe only 1/4" high and as big around as toothpicks!

__________________
Think big. Drive small.
Register to Reply Off Topic (Score 5)
Guru
Belgium - Member - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: Aug 2006
Location: Glabbeek, Belgium
Posts: 1480
Good Answers: 28
#14
In reply to #13

Re: Problem Encountered During Measurement of Energy by a Energy Meter

04/02/2012 3:19 AM

No, just a trick of the light.

__________________
"Here we are now, entertain us"
Register to Reply Off Topic (Score 5)