I'm estimating new tpn in my plant... ranges like 200A,300A,500A, like that some standard ratings.. can send that... i have a different loads.. i have apply for that...
Do you need only the busbar? Or also supports, enclosure, fishplates.....? Don't you need switchgear?And, why do you need a 1000A system when your load is only 400A?
Busbars (and most other stuff) are available in Renard #10 series of preferred numbers.
__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Do you mean a Distribution Board (DB) something like this one ?
It has a 3P MCCB as an incomer, with a separate neutral bar. Individual single-pole or three-pole MCBs/MCCBs are plugged in. Many manufacturers are available.
You need only 600A. 1000A is overkill.
__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Your load current is 400A only. You can use 650 Amp MCCB or 800 MCCB. Basicially for the neutral, we always use neutral link with a copper bar. Not necessary to put up a TPN as the cost is very expensive. You needmore space for the TPN.