Selection of a Distribution Transformer

03/30/2012 4:20 AM

Dear Friends,

what are the points to be considered in selection of a Distribution Transformer

for the factory load

having connected load of 3000 KW,

expected maximum demand 2625 KVA and

aload factor of 1900 KVA

regards

Subhash

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster #1
#1

Re: selection of a Distribution Transformer

03/30/2012 4:21 AM
Register to Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#2

Re: Selection of a Distribution Transformer

03/30/2012 9:24 AM

Your total load is 3000KW which is about 4,900 Amps at 415V therefore your Distribution transformer will be about 4MVA capacity. If you want to consider for the further additional load then you need to redesign your electrical loading system.

If you don't have any experiences. pls engange a consultants to do it for you.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Selection of a Distribution Transformer

03/30/2012 10:21 AM

I would size it like this:

Anticipated Maximum Demand x a factor of cushion, (say 1.2)

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#4

Re: Selection of a Distribution Transformer

03/31/2012 12:24 PM

Who calculated/assumptions made the max demand and load factor?. What kind of load is it supplying?. Are there big motors,what type of starters are used,give more details.

__________________
pnaban
Register to Reply
Active Contributor

Join Date: Nov 2011
Posts: 19
#5
In reply to #4

Re: Selection of a Distribution Transformer

04/05/2012 1:14 AM

Dear pnaban,

It is a factory load, which is having all sort of loads such as motors ranging from 0.375 Kw to 250 Kw, at 415 volt, 50 Hz supply, heating load of approximately 500 Kw, HVAC system, AHU etc.

load factor considered is 0.7.

Is this information is enough to calculate the KVA rating of the transformer?

Subhash

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#6
In reply to #5

Re: Selection of a Distribution Transformer

04/05/2012 2:05 AM

If your max demand is 2625kVA,3MVA transformer would be OK provided the number of large motors(250kW) is not much.You should consider starting methods used for large motors to limit starting/inrush current. No breakdown of HVAC load was given.Information provided by you is inadequate.

__________________
pnaban
Register to Reply
Active Contributor

Join Date: Nov 2011
Posts: 19
#7
In reply to #6

Re: Selection of a Distribution Transformer

04/05/2012 2:17 AM

2 Hvac system having following loads

1. Supply and Exhaust blower motors rating are 55 kw X 2 and 30 Kw X 4 numbers.

2. air condition load is of 20Kw X 2 nos and

3. heating load of around 20 KW X 2 set

Register to Reply