IN single phase(we say 220v ac) but why don't we say 660v ac(for 3 phase)? why do we say 440v ac???
Because the phase-to-phase voltage is root 3 times the phase-to-neutral voltage.
Addition of Vectors is different from normal addition like addition of numbers
I am trying to explain further the point raised by PWSlack in his reply.
In a three phase system we have three vectors say
V = Va + Vb +Vc
Va= Vo e^(j. 0)
Vb= Vo e^(j. 2pi/3)
Vc= Vo e^(j. 4pi/3)
Now Phase to Phase Voltage =Vab= Va - Vb=?
Vab= Vo [ {cos(0) +jsin(0)} - {cos(2 .pi/3) +j sin (2.pi/3)} ]
Vab= Vo [{1} - {-1/2 +j (square root 3)/2}]
Further solving gives the result as
Vab =Vo (square root 3)
So where we have Phase to neutral voltage 230 V we have
Vab = 230 * 1.732 = 400 V
As Vectors are involved so it is 400V instead of 460 V.
As three phase system is Specified by Phase to Phase voltage. For Example
1.If Phase to Neutral is 230 V , then in a Three phase system it should specified by 400 V (Phase to phase Voltage).
2. If Phase to Neutral is 400 V , then in a Three phase system it should specified by 690 V (Phase to phase Voltage).
3 phase is specified as phase to phase voltage; which is root 3 times the phase voltage.