Does a Cable Have Minimum Current Requirement to Conduct

04/06/2012 7:32 AM

Does a cable have minimum current requirement to conduct? If so how can we calculate it?

for eg taking 0.5mm2 (20AWG) having ampacity of 4A, what must be the minimum current above which the cable conductors allow to pass?

If i have a 0.5mm2 cable with me, but my load takes a current of only 20mA, then could i use this cable? the voltage drop for it is very low.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: CABLE

04/06/2012 7:37 AM

No.

N/A

N/A

Yes.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Commentator

Join Date: Aug 2011
Posts: 93
#2

Re: Does a Cable Have Minimum Current Requirement to Conduct

04/06/2012 8:31 AM

What is the Electrical standard used in India?

Is it IEC, NEC or IEEE?

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3
In reply to #2

Re: Does a Cable Have Minimum Current Requirement to Conduct

04/06/2012 10:09 AM

It is the Indian Standards published by the Bureau of Indian Standards (BIS), read in conjunction with the Indian Electricity Rules, 1956 and The National Electric Code (of BIS), 2011.

Register to Reply
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#4

Re: Does a Cable Have Minimum Current Requirement to Conduct

04/06/2012 10:10 AM

Well, minimum electric charge in nature IS the electron's charge Qe=(-1.6 × 10-19 coulombs) and since cable does have self capacitance (in short, depending on it's dimensions), you do need a minimum voltage for an electron to move in or out of it, and twice as that for both, so to have the smallest possible charge flow or else "current". Also since electric disturbance propagates at (near) the speed of light (C) , the minimum time that the "disturbance" is transformed to "current", because of the above is (almost) solely depended on cable's length. So there is a minimum current: electron's charge*cable's length/C (LOL) S.M.

__________________
Life is complex. It has a real part and an imaginary part.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#5

Re: Does a Cable Have Minimum Current Requirement to Conduct

04/06/2012 10:40 AM

There is not a minimum current for conduction in the cable. However, depending on the connector and contacts that are part of the circuit one can have oxide build up problems that prevent a small current from being established every time.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6

Re: Does a Cable Have Minimum Current Requirement to Conduct

04/06/2012 1:23 PM

Just think of it in terms of a water pipe. If you have a pipe full of water, it's full. If you add one drop of water to one end of the pipe, a drop of water will be forced out the other end. Just don't try to put water into both ends of the pipe at the same as this may cause distress in the piping.

Don't try to put 20mA in both ends of the conductor, either, as that will cause distress in the conductor.

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#7

Re: Does a Cable Have Minimum Current Requirement to Conduct

04/06/2012 7:26 PM

Sorry, folks, but in the context of the OP, we are Not talking band gap, contact resistance or anything fancy except "can I use 0.5mm2 cable to carry 20mA?".

I'm getting fed up with the "deep dicussions" which generally start with something more akin to "My Chevvy Won't Start" that to anything very technical.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#8
In reply to #7

Re: Does a Cable Have Minimum Current Requirement to Conduct

04/06/2012 7:36 PM

So, "My Chevvy Won't Start" is OK, but anything more than "Check your fuel gauge" is not? S.M.

__________________
Life is complex. It has a real part and an imaginary part.
Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#9
In reply to #8

Re: Does a Cable Have Minimum Current Requirement to Conduct

04/06/2012 7:59 PM

Didn't say or imply that. OP axed "will 0.5mm2 do the job?". Answer is "yes".

There are obviously many reasons why a Chevvy won't start, but there are very few reasons why a bit of 0.5mm2 wire won't be serviceable for conducting 20mA. There is no reason to go further (except technical masterbation).

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#10

Re: Does a Cable Have Minimum Current Requirement to Conduct

04/06/2012 8:04 PM

Nobody liked my hose analogy?

Technical masterwhat..............?

Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#11
In reply to #10

Re: Does a Cable Have Minimum Current Requirement to Conduct

04/06/2012 8:18 PM

Love it! Will go back and deliver a GA. You've exemplified the lack of depth required for a good answer to the OP's question .

(but axing for a GA is sooo infra dig!).

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#12
In reply to #11

Re: Does a Cable Have Minimum Current Requirement to Conduct

04/06/2012 8:39 PM

OH, Thank you sooooooooo much. I have a boundless lack of depth which comes into play here often.

It's nice when someone recognizes that talent when they see it.

Register to Reply
Guru

Join Date: Feb 2009
Location: West Coxsackie, NY
Posts: 533
Good Answers: 10
#14
In reply to #12

Re: Does a Cable Have Minimum Current Requirement to Conduct

04/07/2012 12:58 AM

OK, while were off topic here and I have a "Problem" or Potential problem and have not been able to resolve it yet. I design and build electro propulsion systems for Elco Motor Yachts.

Been doing this for several years. Now getting into higher voltages and HP's than in the past and running in to Ignition switch issues. Currently I am using a Key switch/Ignition switch rated for 12VDC 15A. Past voltages 12, 24, 36, 48. Now 72, 96, 108, 144. Amps Non inductive loads are 1.5A for 30mS (caught on scope) then .176mA. It's not just this. The contactors I am using are also not rated for more than 96V and yet I have yet to have a failure yet and pushing the 350+ Amp threshold on these contactors. I've been doing electric boats since 2006, my company has been doing electric boats since 1892. Up till 2006 we only went to 8HP @ 48VDC with a DC motor. Now we are doing 3 Phase 24V - 144V AC 3Phase motors up to 100HP and expanding, with DC input of 24-144V. I need an Ignition switch that can handle 150V .126A switching. We are actually writing the ABYC compliance protocols as we are working out the higher voltage/HP issues since ABYC is only up to 48VDC. If any one out there has more experience in this area, I am all ears out. I would appreciate any input in any direction possible. And 12V is not an option, I figured I' dthrow this in as this is already a dead study in the wiring. There is no 12V seperate system to pull from. We have 24, 36, 48, 72, 108 and 144VDC to contend with. HP= 2, 6, 7.5, 10, 20, 35, 100. And working on 250+.

__________________
"Real Bass Players" do not use picks
Register to Reply
Power-User

Join Date: Jun 2011
Posts: 135
Good Answers: 7
#13
In reply to #10

Re: Does a Cable Have Minimum Current Requirement to Conduct

04/07/2012 12:26 AM

I loved your pipe analogy. I'll vote for a GA on that one. I don't agree that "You've exemplified the lack of depth required for a good answer to the OP's question ." You simply phrased your answer in a way that the OP would understand. It seems that electricity is not their strong suit, so you went with plumbing, frequently a good choice. Most people start with an understanding that 'water' flows downhill, and can build from there.

Now if this was a cooking forum we could be talking about 'Master Bakers'

__________________
It gets interesting when you put fuel and oxygen in the same molecule, without allowing them to react, YET!
Register to Reply
Active Contributor

Join Date: Dec 2010
Location: Brasil
Posts: 21
#16
In reply to #10

Re: Does a Cable Have Minimum Current Requirement to Conduct

04/07/2012 10:04 AM

I like it.

Would like to add a question on the simple thinking: what will happend if our fellow use a 50sqmm instead of 0,5sqmm cable?

He will waste maney in cooper, have difficulto to connect it, and others on suports and space. But the cable will do the job.

Register to Reply
Commentator

Join Date: Aug 2011
Posts: 93
#15

Re: Does a Cable Have Minimum Current Requirement to Conduct

04/07/2012 1:46 AM

Well from all your suggestions, what i got is that there will be no problem in using a cable size of high rating, for smaller current applications. It all matters in the expense and application, for smaller rating we have to use only cable corresponding to it. If we require an increase in length correspondingly we have to increase the size of the cable for a shorter voltage drop and power loss.

Here i have submitted the question with an example of 0.5mm2 so that everbody can understand what i m trying to ask.

If there is any thing wrong in what i understood written above, please correct me and add more suggestions if available. thank you...........

Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#19
In reply to #15

Re: Does a Cable Have Minimum Current Requirement to Conduct

04/09/2012 10:26 PM

Sir,

Redfred gave a good point to consider in his #5 post. You need to look at the possible resistance of oxidation or bad connections, and make sure that the total resistance is less than the source's available voltage so it can drive the required amount of current.

Another point to consider would be the "signal/noise ratio". This has to do with the amplitude of the signal or current you are applying and how much noise or interference there may be from other sources. If your signal is low or the voltage driving it is low, then there is a greater possibility that it can be buried in induced or coupled noise on the wire. I have seen this happen in 4-20mA signals over telephone lines (as one example).

You are the only one in a good position to consider the importance of these two points, because your original question was in the form of a hypothetical.

--JMM

Register to Reply Score 1 for Good Answer
3
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#17

Re: Does a Cable Have Minimum Current Requirement to Conduct

04/09/2012 7:37 AM

Well, the minimum current for a cable to conduct is zero amps, Boss. I'm not sure I understand the question.

__________________
Good moaning!
Register to Reply Good Answer (Score 3)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#18
In reply to #17

Re: Does a Cable Have Minimum Current Requirement to Conduct

04/09/2012 8:34 AM

Touché

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 5)
Power-User

Join Date: Aug 2010
Location: Omni-present via the internet!
Posts: 122
#20

Re: Does a Cable Have Minimum Current Requirement to Conduct

04/10/2012 3:09 AM

Well the minimum current is zero. Either there is current or there is none! Look at Lynn's hose comparision.

__________________
Never stop asking questions.
Register to Reply
Commentator

Join Date: Apr 2012
Posts: 75
Good Answers: 6
#21

Re: Does a Cable Have Minimum Current Requirement to Conduct

04/11/2012 12:19 AM

YES and NO.

The question is faulty first off, "current to conduct" is contradictory. One is the same as the other, and one cannot exist without the other.

Its possible to inject current in a cable and get nothing out the other end, if its AC and the frequency is such that the capacitive effects lose the current. that would be a function of applied voltage and capacitance. A VERY weak signal might be absorbed in the nearest insulator to the driven end. I dont know of any such application thats useful.

There would be a minimum energy needed to force a current flow through a conductor, but its extremely small, and a function of the voltage required to knock the first few valence electrons loose in the material to then allow conduction. Again, pretty much useless. Thats getting into semiconductor physics where its possible to inject electrons and lose them in the material.

Might make good University EE test questions.

Register to Reply
Register to Reply 21 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Crabtree (1); daveca (1); electricalexpert65 (1); Jimh77 (1); jmueller (1); JohnDG (4); KalbBR (1); Lapin (1); lyn (3); mathewkyle (1); redfred (2); SimpleMind (2); sujinvipin (2)