Neutral to Earth is Aprox 4 Volt

04/10/2012 1:32 AM

Dear All

My self SAWAN CHOPRA, working in INDIA.

Last week i found the neutral to earth voltage is very high its was around 7 Volt at both output raw power and UPS power (because in my UPS neutral is looped direct from RAW power its designed by manufacturer) and we have 36Nos. of SPM machine (which is electronics base) and per me the voltage of neutral to earth should not more then 1 volt after this finding i followed few steps as below -

  1. 1st we checked the earthing resistance of Transformer Neutral, Transformer Body, UPS, DG Neutral and body but found all these are under 1 ohm.
  1. However we filled the water and salt in the earth pit to decrease the more earthing resistance but the neutral to earth voltage had same
  1. 2nd we discussed with our earthing installation contractor XYZ then he suggested us that checked the earthing resistance after disconnected the earthing strips (Checked the earthing resistance in open condition)
  1. 3rd we checked all the above earth pit resistance after disconnected the earthing strips (checked earthing pit resistance in open condition) then we found it reached up to 6 or 7 ohm. Then XYZ advised us that fill in the entire above pit more salt and charcoal with water. He also told us after this exercise if the resistance will decrease or decrease the voltage between neutral and earth then its ok otherwise we may dig new earth pits.
  1. Then after 3 days we found the neutral to earth voltage 4.5 voltage.
  1. One more thing we found the unbalanced load (approximate 10 to15 Amps high in Y Phase) at LT Panel but now we also had done the load balanced at LT Panel.
  1. And after the load balancing we found the neutral to earth voltage became 3.2 Voltage.
  2. And earthing resistance now became 3 to 4 ohm in open earth pit.

Kindly guide me that how may i decrease the voltage between neutral to earth.

SAWAN CHOPRA
CR4 Admin - email address removed

From the CR4 Rules: Do not post phone numbers or email addresses. The CR4 Admin will delete all phone numbers and email addresses posted in threads or comments. You can share this information via the CR4 internal messaging system.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Dec 2010
Location: 1° North Singapore
Posts: 568
Good Answers: 17
#1

Re: Neutral to earth is aprox 4 volt

04/10/2012 1:59 AM

IT is due to 3 phase imbalance loading, causing current flow in Neutral line. Some imbalance is unavoidable. You must try to balance th3 3 phase loading as much as possible.

__________________
Sharing knowledge is one thing that defies basic arithmetic logic --- the more you share, the more you get!
Register to Reply Score 1 for Good Answer
Associate

Join Date: Apr 2012
Location: Haridwar, INDIA
Posts: 27
#2
In reply to #1

Re: Neutral to earth is aprox 4 volt

04/10/2012 2:37 AM

Dear Mr. Bravo

First of all thank you

I would like ask you few more questions

It means my earthing pit resistance is ok now which is around 3 to 4 ohm after opening or disconnected with earthing strips, there is no need to more improve my earthing pit?

What is the right method to check my earth pit resistance -

1. Without opening the earthing strips or after opening the earthing strips?

2. What should be earth pit resistance?

3. What should be neutral to earth voltage?

Kindly guide

Thanks & Regards

SAWAN

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Neutral to earth is aprox 4 volt

04/10/2012 3:28 AM

The neutral voltage is simply the expression of the neutral current and the earth loop impedance. To reduce it, either reduce the earth loop impedance or the neutral current or both.

The neutral current is simply the vector sum of all the phase currents and an expression of phase loading imbalance.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster #1
#4

Re: Neutral to Earth is Aprox 4 Volt

04/10/2012 8:56 AM
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#5

Re: Neutral to Earth is Aprox 4 Volt

04/10/2012 2:17 PM

The resistance of the earth pit has nothing to do with your readings. The earth pit is a zero reference point. When you have current flow in the neutral you have a voltage drop. This makes the point where you measured the voltage at a higher level than the earth pit. The only way to reduce the voltage difference is the reduce the neutral current flow. Or you could increase the neutral conductor size. 3.2 volts is not that high. Unless the current in the neutral is zero, you will always have a voltage difference.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Mar 2012
Location: Hot Humid Houston
Posts: 229
Good Answers: 29
#6

Re: Neutral to Earth is Aprox 4 Volt

04/11/2012 2:36 AM

Are you concerned about the voltage on the neutral relative to earth zero reference, or are you measuring 7 volts on the building steel and grounding system relative to the earthing pit? These are two different problems.

What is the voltage between the building steel and the earthing pit? If you are reading 7 volts there, then you may have great neutrals and a rapidly decaying building due to galvanic corrosion.

If 7 volts on the neutral is too high for your equipment... You will have to achieve better load balancing, or use larger or better bonded neutrals. Your spec of 1 volt may be ambitious. On the other hand, 7 volts on the grounding system relative to earth would be cause for all kinds of concerns.

1) Is the total series resistance under 1 ohm from panel LT to transformer neutral to bonding point to earth pit, or just the series from TN-TB-UPS-DG?

1.1) If the resistance did not change then you did not measure correctly, or the point where you measured is not connected to the grounding system is not connected, or the entire earthing pit is lined with an insulator which is preventing contact with earth relative to the power source. It must - must - change if you change the ion concentration up or down by adding water or salt. Are you certain the earthing system is absolutely bonded to the earthing pit, or have you somehow measured the system above ground, and the "other system" below ground, but not across the two tied together? You suggest you removed the connection to the earthing strips...

1.3) And then you saw a change to 7 ohms but on what side - the earthing system or the building earth bonded to the transformer neutral?

I suspect that what you really have is a connection between neutral and earth beyond the panel due to a skinned neutral or whisker or nicked jacket, perhaps even in an underground pipe which may have a lot of moisture or water in it. We just pulled underground line out of a building that had the same problems you describe. One tiny nick from sloppy electrical work had us chasing 7 volts one day, 20 the next, 2 or 3, then 30, all depending on how much water was in the pipe or humidity in the air.

Have your neutrals meggered again. Check all your insulation integrity. I bet you will find that your pit is fine, and your earthing system is fine up to the transformer and up to the panel.

__________________
txmedic3338
Register to Reply
Associate

Join Date: Apr 2012
Location: Haridwar, INDIA
Posts: 27
#7
In reply to #6

Re: Neutral to Earth is Aprox 4 Volt

04/11/2012 5:59 AM

1. no all are separate not in series

i want to describe you in detail we have one 400KVA D/Y transformer, 11KV/415V

for this transformer we have 2 body GI plate earthing and 2 neutral copper earthing.

From the pics you can understand and same for DG set and for LT & UPS we have only 2 body earthing for each.

Register to Reply
Commentator

Join Date: Jun 2011
Posts: 67
Good Answers: 2
#8
In reply to #7

Re: Neutral to Earth is Aprox 4 Volt

04/11/2012 7:18 AM

You must bond all earthpits including those for lightening protection together. This will achieve a better earth resistance.Secondly check the harmonic content of the system. If it is high, it should be corrected by using appropriate measures. If even after that the problem persists then increase the neutral to ground conductor size.

Register to Reply
Participant

Join Date: Sep 2011
Posts: 2
#9

Re: Neutral to Earth is Aprox 4 Volt

04/11/2012 7:37 AM

Dear Mr.Sawan

Could you throw some light on the installation details like the vector group of the transformer,the primary earthings done at your installations ,details of your distribution boards,whether 3/4 pole Breakers/MCCB's etc used.What about your neutral earthing?What is the system of earthing adopted?You may have to have the Parallel neutral earthings done at Transformer ends.Is your neutral -Body earths mixed?What is the capacity of the UPS and what about the neutral of the UPS?

Kindly have me some details.

radhakrishnan k a

Register to Reply
Associate

Join Date: Apr 2012
Location: Haridwar, INDIA
Posts: 27
#10
In reply to #9

Re: Neutral to Earth is Aprox 4 Volt

04/11/2012 8:07 AM

System of neutral earthing is Copper plate earthing (600x600x5) CU with charcoal and salt in 12 feet of dig.

Yes we have Parallel neutral earthings done at Transformer ends.

no mixing between body and earth

Capacity of UPS is very small 20 KVA Make - DELTA, 3Phase In and 1Phase out and output neutral is directly loop with the raw power.

Elect Single Line Distribution

Regards

SAWAN

Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#11
In reply to #10

Re: Neutral to Earth is Aprox 4 Volt

04/20/2012 8:40 AM

Dear Sawan,

The circuits are not clearly visible. But in your original post you have mentioned that there are 36 nos. SPM machines( electronics based) as loads. Please note that neutral to earth voltage is simply multification of current thro' neutral and earth loop impedance. You have already reduced the earth impedance also balanced the three phase loads. Therefore, it is apprehended that, due presence of high quantum of third harmonic component(due to electronic SPM machines) which are passes thro' neutral to ground, this voltage drop may occur. So please arrange to check third harmonic component in the power supply.

Thanks,

Manindra.

__________________
Manindra
Register to Reply
Associate

Join Date: May 2012
Posts: 52
#12

Re: Neutral to Earth is Aprox 4 Volt

05/15/2012 3:24 AM

hello sawan , charcoal and salt mix water is good for grounding system, but you need to dig 12meters deep to solve that problem, and the verygood reading of grounding system is 5 to zero ohms that is the standard grounding, and we incounter that kind of problem before by follwing this spec, and also pls retigh all electrical terminal so you will preventing high amp / voltage reading

keep up the good job guys !!!!

__________________
i want ot helf piple need assistance and to share my knowleged in technical
Register to Reply
Commentator

Join Date: Jun 2011
Posts: 67
Good Answers: 2
#13

Re: Neutral to Earth is Aprox 4 Volt

05/15/2012 6:18 AM

Sawan,

Please carry out harmonic analysis of your loads. The zero sequence currents due to third harmonics are additve i.e all three phase currents add up in the neutral and generally these are the cause of high neutral current and consequent voltage drop. Eliminating third harmonics with proper supression or filter will take care of your problem.

Register to Reply
Register to Reply 13 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); bravo88 (1); ka_rkrishnan (1); Learner42 (2); manindra (1); PWSlack (1); sawan.chopra (3); toink (1); txmedic3338 (1); wareagle (1)

Previous in Forum: Rusted Spade Plug Connections   Next in Forum: Transformer Frequency

Advertisement