Dear All
My self SAWAN CHOPRA, working in INDIA.
Last week i found the neutral to earth voltage is very high its was around 7 Volt at both output raw power and UPS power (because in my UPS neutral is looped direct from RAW power its designed by manufacturer) and we have 36Nos. of SPM machine (which is electronics base) and per me the voltage of neutral to earth should not more then 1 volt after this finding i followed few steps as below -
- 1st
we checked the earthing resistance of Transformer Neutral, Transformer
Body, UPS, DG Neutral and body but found all these are under 1 ohm.
- However
we filled the water and salt in the earth pit to decrease the more
earthing resistance but the neutral to earth voltage had same
- 2nd
we discussed with our earthing installation contractor XYZ then he suggested us that checked the earthing
resistance after disconnected the earthing strips (Checked the earthing resistance in open condition)
- 3rd
we checked all the above earth pit resistance after disconnected the
earthing strips (checked earthing pit resistance in open condition) then
we found it reached up to 6 or 7 ohm. Then XYZ advised us that fill
in the entire above pit more salt and charcoal with water. He also told us after this exercise if
the resistance will decrease or decrease the voltage between neutral and
earth then its ok otherwise we may dig new earth pits.
- Then after 3 days we found the neutral to earth voltage 4.5 voltage.
- One more thing we found the unbalanced load (approximate 10
to15 Amps high in Y Phase) at LT Panel but now we also had done the load
balanced at LT Panel.
- And
after the load balancing we found the neutral to earth voltage became 3.2
Voltage.
- And earthing resistance now became 3 to 4 ohm in open earth pit.
Kindly guide me that how may i decrease the voltage between neutral to earth.