Transformer Frequency

04/10/2012 1:33 AM

Is it possible for a 60 hz transformer to operate on 40 hz? under what conditions?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Dec 2010
Location: 1° North Singapore
Posts: 568
Good Answers: 17
#1

Re: Transformer Frequency

04/10/2012 2:03 AM

The voltage rating will have to go down proportionately, as Vrms=4.44*B*A*N*f

B, A, N fixed value by design.

__________________
Sharing knowledge is one thing that defies basic arithmetic logic --- the more you share, the more you get!
Register to Reply
Associate

Join Date: Sep 2011
Posts: 47
Good Answers: 2
#2

Re: Transformer Frequency

04/10/2012 2:19 AM

Yes you can .If winding/Insulation of transformer are able to withstand the increased current (due to decrease in winding reactance).

-------------------------------------------------------------------------------------

Correct me, if i am WRONG .

Punctuation Mark plays an important role..... !

Register to Reply
Guru

Join Date: Dec 2010
Location: 1° North Singapore
Posts: 568
Good Answers: 17
#4
In reply to #2

Re: Transformer Frequency

04/10/2012 2:30 AM

It is not just the reduction in reactance, the flux in the core will be higher and nearer to saturation, when core saturates, the output voltage waveform will be distorted, causing high harmonics , overheating may result. When transformer core saturates, even without loading, the transfomer may be damaged.

__________________
Sharing knowledge is one thing that defies basic arithmetic logic --- the more you share, the more you get!
Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#3

Re: Transformer Frequency

04/10/2012 2:21 AM

At about 2/3's the input voltage would work too.

(but there's no alphabet in that equation.)

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Transformer Frequency

04/10/2012 3:25 AM

At reduced output.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#6

Re: Transformer Frequency

04/11/2012 3:42 AM

TCM has the only correct answer, and here's the alphabet soup he's referring to. The Voltz/Hz ratio should not be allowed to exceed the ratio at rated voltage and rated frequency. So for numbers' sake 120V/60Hz=2 therefore at 40Hz 2=V/40 or V=80, which is 2/3 of 120 (you could also take 40/60 and get the same answer).

Why is V/Hz important? Because of operating too far into the hysteresis curve of the laminations of the core and the subsequent distortion of the sine wave and resulting high harmonic levels and heating of the core and surrounding structures..

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.