Off Grid Start-Up

04/13/2012 1:01 AM

I work in a surface mine(equipment operator) in the Pacific Northwest. I'm trying to save some of our jobs by cutting costs. Any help with my idea would really be appreciated.

We have ten 200 HP motors with Toshiba soft starts. 480 Volt 3 Phase. We start them one at a time. Each draws around 700 Amps for about a minute as they come up to speed. (I say around because the meter pegs at 600 Amps and the breakers are 800 Amp). We are billed according to these spikes on the grid. I'm told we work long days to justify start up costs.

Q:Could we use one generator to start each motor then transfer it to the grid and start the next and so on?

Thanks in advance for "any help"

Scott

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Off grid start-up

04/13/2012 2:42 AM

I like you're sentiment but the collateral costs would be astronomical in relation to the savings recouped. It's not just the cost of the generator, the switch gear to control the set up would be a substantial investment.

Keep trying on the cost saving.

I wish you all the very best.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Off grid start-up

04/13/2012 3:29 AM

Rather than clutching at straws like this one, concentrate on the basics of loss prevention first:

"A place for everything and everything in its place. Nothing there that shouldn't be there." - Anon

Some call it "housekeeping".

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#3

Re: Off Grid Start-Up

04/13/2012 7:03 AM

Have you installed PFCC?. During starting as there is more VD fix another capacitor via a timer only during the starting period.

__________________
pnaban
Register to Reply
Participant

Join Date: Apr 2012
Posts: 3
#4

Re: Off Grid Start-Up

04/13/2012 7:56 AM

We are billed according to our max demands on the grid. It's the start up we pay for. If it cost 100K to set this up and we cut our costs by even 15% it would be a viable alternative.

Our soft starts are fairly state of the art. I'm thinking the capacitors are pretty close to what they need to be but I'll learn more about that and see.

Thanks all for your input

Register to Reply
2
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#5

Re: Off Grid Start-Up

04/13/2012 8:37 AM

Can you work at night?

I'm wondering if you could split into shifts and leave them running?

What time of the day are you starting them? The electric company may cut you a break if you do your starting during off-peak hours.............like 4:00 AM or something.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply Good Answer (Score 2)
Guru

Join Date: Feb 2009
Location: West Coxsackie, NY
Posts: 533
Good Answers: 10
#9
In reply to #5

Re: Off Grid Start-Up

04/13/2012 11:40 PM

Great Idea, this is what our local Cement company does when they re-start their kiln.

Volts: 34000, 3Ph 7200A, HP: 760 Line drop, 23% on each start up, 4 kilns. Recovery time: 37 mins. Power company jumps through many hoops. Amazing site. You have to see it to appreciate it. All happens in the middle of the night and only the clocks take a hit from the 60Hz. Over time you will need to reset your clock. Only happens a few times a year when the Kiln has to be re-Lined.

__________________
"Real Bass Players" do not use picks
Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6

Re: Off Grid Start-Up

04/13/2012 11:27 AM

If you are in Washington State, you are NOT being billed for "Instantaneous" peak demands, you are being billed based on a sliding 15 minute demand window. So starting the motors with a generator and then switching to utility power will not change your Peak Demand penalty situation. Once you have all of them on line, THAT is when you will register the demand, not the short term peaks on starting. Sorry, it's a common myth.

The soft starters are necessary because SEPARATE from the Demand Charges, the utility limits you to a specific amount of starting power measured in kVA/HP in order to avoid voltage drops to yourself and your neighbors. So you must have the soft starters, but they are not going to affect your Peak Demand penalties.

A better approach, since you DO have the soft starters, is to turn OFF the machines whenever they are not in full use. Another aspect of this myth is that "it's cheaper to leave things running than it is to turn them off and back on." Not true. If it's not being used at peak performance, turn it off. So being a mine, I can imagine these are primary and secondary crushers, maybe some SAG Mills, Ball Mills or Rod Mills. Usually the mills need to run continuously, but you may be able to stagger your crusher operations a little. Only run the crushers when you have a stockpile behind them that can keep them running continuously. That saves considerable energy if what you have been doing is leaving them running even if there is nothing feeding into them.

If everything is running at full tilt boogie all the time, then this is just your cost of operations. Sorry.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#7

Re: Off Grid Start-Up

04/13/2012 4:27 PM

From the rough estimations you give, I assume that these motors start a huge inertia system. Also assume you can reduce or even eliminate the actual load (apart from the load due to inertia at start) If both those conditions apply, I believe you can double or triple the soft starting time and significantly reduce starting current, even close to normal working current. But do verify your billing system details before doing anything. S.M.

__________________
Life is complex. It has a real part and an imaginary part.
Register to Reply Score 1 for Good Answer
Guru
Hobbies - HAM Radio - New Member United Kingdom - Big Ben - New Member Fans of Old Computers - Altair 8800 - New Member Canada - Member - New Member

Join Date: Jun 2006
Location: Toronto
Posts: 3968
Good Answers: 120
#8

Re: Off Grid Start-Up

04/13/2012 11:19 PM

a battery bank and a 3 phase UPS of the line following type as used to run large data centers would work here.

You would need to inspect the cost from suppliers of large UPS equipment. I know it can be done, but there needs to be a detailed cost out for it, someone else commented that the cost of the switching and line phase matching equipment may well kill the concept.

200 Hp = 150 Kilowatt hours per hour, at 10 cents per KWH (what is your rate?) = $15 per hour each

ten motors = $150 per hour, if you have 150 workers per shift = $1 per hour per worker, more or less, as the number of workers differs from my guess.

So management might be engaged in driving the workforce with lies?

__________________
Per Ardua Ad Astra
Register to Reply Score 1 for Off Topic
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#10
In reply to #8

Re: Off Grid Start-Up

04/14/2012 2:46 AM

What will be the voltage drop in UPS battery when you start a large motor of given capacity,how long will it take to recharge?.

__________________
pnaban
Register to Reply
Member

Join Date: Mar 2011
Posts: 6
#11

Re: Off Grid Start-Up

04/14/2012 4:33 AM

What about synchronizing a smaller size with the grid say half the rated for a 200hp motor and retransfer the total load to the grid once it reaches it's operating speed.

Register to Reply
Participant

Join Date: Apr 2012
Posts: 1
#12

Re: Off Grid Start-Up

04/14/2012 9:16 AM

Hello,

You could look into 'variable speed drive' for each motor to save energy cost. Please see "en.wikipedia.org/wiki/Variable-frequency_drive" for more information.

Register to Reply Score 1 for Off Topic
Participant

Join Date: Oct 2011
Posts: 1
#13

Re: Off Grid Start-Up

04/14/2012 9:41 AM

Yes, you can use one large enough(500 kw) genset to start up the 200hp motors

individually, then synchronize the genset to the grid and smoothly transfer the motor

to the grid, then repeating the process for the other motors. BUT big BUT, CONSIDER

THE COST OF OPERATING THE DIESEL GENSET AND OF THE PROCESS OF THE MOTOR

TRANSFER TO THE GRID. WILL IT OFFSET THE GRID BILLING?

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#14

Re: Off Grid Start-Up

04/15/2012 4:56 PM

Posts #6 and #7 make good sense.

I note on #6, J. Raef's, point that 10 motors at a minute each, started at 90 second intervals would fill up the 15 minute window, while 9 motors running plus the last starting may be 150% of the steady final load current if your start is not very "soft".

So could automating the starts sequence (minimum time between starts) to reduce overall start time or breaking up start into two groups of 5, spaced 5, 10 or 15 minutes apart dodge the charge rules?

Capacitor Power factor compensation to unity of each of 10 motors, gives a capacitor current enough to cancel the lagging current of one motor starting compared to no-compensation.

So lots of thinking time on charging rules and operating practice could be imminent!

Register to Reply
Participant

Join Date: Apr 2012
Posts: 3
#15

Re: Off Grid Start-Up

04/16/2012 12:23 AM

I think JRaef nailed it and others have concurred. I need to find out for myself how the billing actually works instead of going on hear-say from someone who is supposed to know because it's their job.

But a HUGE thanks to all you guys! Some posting for their first time(like me) You really have an awesome forum here and have given me a lot of incentive to keep learning.

Pnaban, check out Corvus-energy.com They could meet this discharge with a bank of Lithium Ion batteries that would re-charge in 30 min. Awesome!

Scandrews, two of our crushers do just that. They have two motors. One starts the bowl then the other joins in.

Register to Reply
Commentator

Join Date: Jun 2011
Posts: 67
Good Answers: 2
#16

Re: Off Grid Start-Up

04/16/2012 4:51 AM

You could use a large flywheel storage system coupled to a motor which could rev it up in say 15 minutes. Once it is running at peak speed, a generator coupled to this flywheel could be synchronised with mains. Starting your 200HP motor on this setup will eliminate your starting peak due to flywheel feeding the energy. Flywheeel energy storage systems upto 1000KVA are available. You may read more about it in:

http://en.wikipedia.org/wiki/Flywheel_energy_storage

Register to Reply
Register to Reply 16 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (1); aurizon (1); banned (2); Ignacio B. Fabia (1); Jimh77 (1); JRaef (1); kramarat (1); Learner42 (1); pnaban (2); PWSlack (1); scandrews (1); SimpleMind (1); TonyS (1); ziptiger (1)