how can i know each of them. i have 4 wires into the trip unit but i can not have a look on them ( they are hidden). can i differentiate between them by any other way.
Re: C.B. current and voltage transformer
04/13/2012 3:54 AM
  • Make?
  • Model?
  • Part number?
04/13/2012 4:02 AM
it is a merlin gerin C.B. ST 206D trip unit
04/13/2012 4:29 AM
thanks for that cataloge . but i need a wiring for the trip unit to know where could be the ct is connected.
if u have a site where i can download datasheets from it that would be very kind of u
Thanks
04/13/2012 4:36 AM
What about using the equipment manufacturer's telephone number, as stated on the equipment datasheet?
Good Answers: 38
04/13/2012 4:38 AM
if you don't have a schematic, start measuring!
04/13/2012 4:44 AM
how can i measure each to differentiate.
04/13/2012 4:51 AM
So, we're in 1250A switching territory and the principles of operation are unknown? It's time to delegate this task to an appropriately-qualified local Electrician, for the sake of safety.
04/13/2012 5:15 AM
what could happen 4 the c.b if the current transformer had gone opened.
04/13/2012 5:40 AM
High voltages on the current transformer wiring. Please stop immediately and involve a qualified electrician in this matter before someone gets hurt/killed.
04/13/2012 4:13 PM
i understand well what u mean. open secondary of current transformer will lead to C.T. corruption and may explode. but what i need to know how can i cancel the operation of that trip unit of the C.B.?
04/16/2012 3:26 AM
Why is it there, then?
Good Answers: 38
Re: C.B. Current and Voltage Transformer
04/15/2012 8:57 PM
I agree with PWslack if you are not an certified high voltage engineer, then stay away from the live wires. i was assuming you would measure it in a powered down state and making sure that any lingering charge has been discharged.
04/15/2012 9:13 PM
hey. it is a low vlotage circuit breaker. not a high voltage circuit breaker. and the client asked from me to cancel the work of that trip unit. and i had done that by removing its mechanism arm.