Hotel Water Distribution - Pressure Issues

04/17/2012 3:45 AM

We have a booster pump system in our 4 storyed hotel for distribution of hot and cold water to rooms, we are facing an issue that while using the bath room shower mixer, user is getting fluctuating alternate supply of hot and cold water. the pressure settings of the booster pumps for hot and cold is 3.5 bar for cut off and 2. bar is for initializing the supply.

Kindly suggest workable solution to this issue.

Kind regards.

Anand.

Register to Reply
Pathfinder Tags: Hotel - water distribution
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Hotel water distribution - pressure issues.

04/17/2012 3:49 AM

Swap the shower mixer inlet connections over. The issue is one of the temperature controller inside it oscillating from full hot to full cold, because the pipes are connected the wrong way round.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Mar 2007
Location: Bangalore, India
Posts: 141
Good Answers: 1
#2

Re: Hotel water distribution - pressure issues.

04/17/2012 3:53 AM

1)Check if the connections are taken before the booster pumps. Need to understand the piping circuit. Generally, booster pumps sucks and hence there will not be any water down the line.

2) Also if the pressure difference in hot and cold water is high, the high pressure will not allow the low pressure and hence the fluctuation.

3) The pressure difference should not be very high

__________________
Best Regards, Shivaram
Register to Reply
Power-User

Join Date: Dec 2010
Posts: 377
Good Answers: 20
#3

Re: Hotel water distribution - pressure issues.

04/17/2012 4:53 AM

This is happening due to thermostat valve in the mixure assembly. Check the pressure rating of the Mixure assembly in suitable units. PWslack may be correct. You can swap the connections and then check for the problem.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4

Re: Hotel Water Distribution - Pressure Issues

04/17/2012 10:48 AM

Turn the hot water off.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#5

Re: Hotel Water Distribution - Pressure Issues

04/17/2012 1:28 PM

Get a roof tank...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#6
In reply to #5

Re: Hotel Water Distribution - Pressure Issues

04/17/2012 2:08 PM

Absolutely agree. Best way to stabilize water pressure. I will even award you a GA for that.

As a bonus, a large roof tank will dampen building sway. The water in the tank will create an inertia movement opposite to the building movement. Might not be a big problem in a four story building, but it can't hurt (as long as the structure and the water supply system both support it).

[edit] I'm reconsidering... only a four story hotel... won't really get much pressure, maybe 25 psi at the ground level... oh, hell, it's still an idea worth considering.

__________________
Semper Ubi Sub Ubi
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#7
In reply to #6

Re: Hotel Water Distribution - Pressure Issues

04/17/2012 3:47 PM

It would be for availability of water rather than pressure boost, although some boost as you said will occur....Normally you wouldn't need a tank on a building less than 6 stories, but there seems to be a problem with water availability in the quantity needed...They have water tanks on one story buildings in Mexico...In this case the roof tank would feed the existing booster pump...Then again it could be a valve problem, as somebody said...but maybe just undersized or obstructed water lines feeding the building....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: May 2007
Location: Geelong, Australia
Posts: 1084
Good Answers: 54
#10
In reply to #6

Re: Hotel Water Distribution - Pressure Issues

04/17/2012 11:53 PM

"As a bonus, a large roof tank will dampen building sway"

No, it will change the frequency of oscillation. This may be useful if the resonant freq of the building is a problem. But is not necessarily a good thing.

__________________
If there's something you don't understand...Then a wizard did it. As heard on "The Simpsons".
Register to Reply
Guru

Join Date: Feb 2006
Location: Piney Flats, Tennessee
Posts: 1740
Good Answers: 23
#8
In reply to #5

Re: Hotel Water Distribution - Pressure Issues

04/17/2012 11:05 PM

I agree a roof tank for the cold water

__________________
If you never do anything you never have problems.
Register to Reply
Guru

Join Date: Feb 2006
Location: Piney Flats, Tennessee
Posts: 1740
Good Answers: 23
#9

Re: Hotel Water Distribution - Pressure Issues

04/17/2012 11:07 PM

Is this well water ? Does it have a lot of minerials in the water like Lime from the rock ?

__________________
If you never do anything you never have problems.
Register to Reply
Guru

Join Date: May 2007
Location: Geelong, Australia
Posts: 1084
Good Answers: 54
#11

Re: Hotel Water Distribution - Pressure Issues

04/18/2012 1:31 AM

I'd suggest running the hot water line in a ring.

Hot water is continually circulated back to the boiler so there are no hot/cold spots in the pipe. That way the local shower temperature controllers will have steady conditions to work with.

It also means your guests don't have to run the "hot" water for 10 minutes before the water heats up.

__________________
If there's something you don't understand...Then a wizard did it. As heard on "The Simpsons".
Register to Reply Score 1 for Good Answer
Associate

Join Date: Mar 2012
Posts: 31
Good Answers: 1
#12

Re: Hotel Water Distribution - Pressure Issues

04/18/2012 9:27 AM

Simple solutions are often over looked. Adjusting the hot water temperature to 105 Deg. F, and not mixing any cold for your bathing will result in a comfortable shower for most folks; it will save money, and prevent people from getting scalded.

Register to Reply
Guru
Hobbies - DIY Welding - New Member Hobbies - Target Shooting - New Member Engineering Fields - Civil Engineering - New Member United States - Member - New Member

Join Date: May 2009
Location: Red Hook, New York (Mid-Hudson River Valley)
Posts: 4362
Good Answers: 179
#13

Re: Hotel Water Distribution - Pressure Issues

04/18/2012 9:39 AM

1. With a 4 story building the available water pressure from a roof mounted water storage tank will be insufficient in the upper stories of the building.

2. The existing structure may not be structurally viable to support the additional load of stored water + tank Dead Load. Additionally, with a tank atop the building, the existing structural elements may not be robust enough to withstand the inertial forces induced by a seismic event.

3. Aren't rooftop water storage tanks primarily used for fire flow requirements in lieu of providing adequate domestic water flow and pressures throughout a tall building, like what we see in NYC?

Why not install hydro-pneumatic tanks on both the cold and hot water supply lines to equalize the water pressure differentials induced by the booster pumps? Just a thought....and I'm not a Mechanical Engineer by any stretch of the imagination.

Just adding my 2 Cents worth!

__________________
"Veni, Vidi, Vici"; hendiatris attributed to Gaius Julius Caesar, 47 B.C.
Register to Reply
Active Contributor

Join Date: Feb 2011
Posts: 11
#14

Re: Hotel Water Distribution - Pressure Issues

04/18/2012 10:09 AM

It looks like more than one issue; temperature and pressure.

Temperature should be regulated at the shower valve if the proper valve is installed. Setting all the hot water at 105 degrees F is not the answer as other areas of the hotel may need higher temperature requirements. The temperature at the lavatories is not mentioned.

Pressure: Could be several things; suction lift or continious pressure on the suction side of the pump. Most problems with pumps are on the suction side. Water softeners are not mentioned which can have a substancial pressure reduction. Is there a booster pump on both the hot water and cold water? Usually a pump or pumps should be on the cold water at the water supply to the building.

A return line circulator on the hot or tempered water is a great idea. as is insulated water piping.

It is difficult to make an imformed decision without full specifications and piping layout.

The water tower may work but would be costly and still would need a pump to raise the water to this greated height.

YAR

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#15
In reply to #14

Re: Hotel Water Distribution - Pressure Issues

04/19/2012 7:16 AM

<...Setting all the hot water at 105 degrees F is not the answer ...>

Quite. Water needs to be stored at >=60degC/140degF to kill-off any bacteria within it. This setting is too hot for comfort when issuing from a shower head.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Mar 2012
Posts: 31
Good Answers: 1
#17
In reply to #15

Re: Hotel Water Distribution - Pressure Issues

04/19/2012 8:59 AM

Let me speculate you only drink water that is 140 deg. F., or greater to avoid the bacteria that is found in cold water. Washing Dishes or laundry in a commercial setting, would require elevated water temperatures to disinfect (because of bacteria introduced to the these items). Water is chlorinated and tested to control the pathogens that could make you sick.

Register to Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#18
In reply to #17

Re: Hotel Water Distribution - Pressure Issues

04/19/2012 9:08 AM

Don't forget, water heated with microwave energy is bad for you.

__________________
Semper Ubi Sub Ubi
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#19
In reply to #18

Re: Hotel Water Distribution - Pressure Issues

04/19/2012 9:18 AM

I've been avoiding this thread, mostly because the OP likely doesn't want to spend even a penny to solve his problem of poor design or build.

so, I think they are all safe from microwaved water. $$$$

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#16

Re: Hotel Water Distribution - Pressure Issues

04/19/2012 7:18 AM

Well? Were the inlet pipes inadvertently crossed over?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Mar 2009
Location: Egyptian in Saudi Aarabia
Posts: 112
Good Answers: 12
#20

Re: Hotel Water Distribution - Pressure Issues

04/25/2012 4:04 PM

we have faced the same issue in a hospital water supply system. after several trials we found one damaged shower mixer. cold water passes to hot water pipes through the mixer .in such case it will affect the near rooms for the damaged mixer .

__________________
don't tell me who are you , what do you know is enough.
Register to Reply
Register to Reply 20 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

CaptMoosie (1); dadw5boys (2); Doorman (2); ffej (2); khairy Aish (1); lyn (2); Mukesh0861 (1); PWSlack (3); shivaganti (1); SolarEagle (2); Thomas J. Becker (2); Yar (1)

Previous in Forum: What is Difference Between Propeller and Impeller Shaft?   Next in Forum: Spiral Wound Gasket Center Ring (Outer Ring)

Advertisement