Calculation Of Heat Generated By Control Panel Elements

04/25/2012 1:17 AM

how can i calculate heat generated by control panel elements like contactors & overloads

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: Calculation of heat generated by control panel elements

04/25/2012 1:38 AM

The manufacturer's catalogues give these values usually. Here are a couple of samples from ABB....

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Member

Join Date: Apr 2012
Location: mumbai
Posts: 8
#2
In reply to #1

Re: Calculation of heat generated by control panel elements

04/25/2012 1:44 AM

Dear sir

can u tell me the calculation procedure for heat generation of all the equipments

Register to Reply Off Topic (Score 5)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3
In reply to #2

Re: Calculation of heat generated by control panel elements

04/25/2012 2:18 AM

They are measured, not calculable usually. Lots of experimental data is always available with good manufacturers.

Maybe with new Thermal FEA software, one can perhaps calculate, but in my days, we did not achieve any high level of confidence in the calculation.

Please remember, manufacturers give pessimistic values. Actual wattloss figures are likely to be lower.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Member

Join Date: Apr 2012
Location: mumbai
Posts: 8
#4
In reply to #3

Re: Calculation of heat generated by control panel elements

04/25/2012 2:35 AM

actually i want to connect an ac to my control panel so what will be its temp. rating i want to calculate

Register to Reply Off Topic (Score 5)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#5
In reply to #4

Re: Calculation of heat generated by control panel elements

04/25/2012 2:47 AM

i think you need to give more information.

What is the AC (i assume you mean an airconditioner) supposed to cool...the whole control room? or the control panel?

For the purpose of deciding the AC, you say you need the wattloss figures of components used in the panel. Why? And, what about busbars, enclosure class(IPxx) etc. ?

Details, with proper punctuation, will help.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Member

Join Date: Apr 2012
Location: mumbai
Posts: 8
#7
In reply to #5

Re: Calculation of heat generated by control panel elements

04/25/2012 3:00 AM

i have to provide the ac for control panel.The details are given bellow.

Contator

25A-2

12A-2

9A-3

MPCB

20-25A-2

2.5-4A-3

4-6.3A-2

CHOKE(15HP)-2

CONTROL TRANSFORMER-1(450VA)

PLC-

CPU-1,DI/O MODULE-1,AI/O-1

3 1-P MCB,1-2POLE MCB

2 - vfd's of 11kw

Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12
In reply to #7

Re: Calculation of heat generated by control panel elements

04/25/2012 4:49 AM

Calculate the power flowing into the panel and the power flowing out. Subtract one from the other and that figure will be the power dissipated within it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14
In reply to #4

Re: Calculation of heat generated by control panel elements

04/25/2012 4:50 AM

Air conditioning is to provide comfort control.

Cooling is provided by increasing the ventilation, perhaps using (a) fan(s).

In either case, basic data such as the local ambient atmospheric conditions is a cornerstone to the sizing!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#6

Re: Calculation of heat generated by control panel elements

04/25/2012 2:58 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Member

Join Date: Apr 2012
Location: mumbai
Posts: 8
#9
In reply to #6

Re: Calculation of heat generated by control panel elements

04/25/2012 4:22 AM

Thanks for the help sir

Register to Reply Off Topic (Score 6)
Member

Join Date: Apr 2012
Location: mumbai
Posts: 8
#10
In reply to #6

Re: Calculation of heat generated by control panel elements

04/25/2012 4:31 AM

Dear sir, what will be the heat generated if we connect a contactor of 24v dc for 30 min.

Register to Reply Off Topic (Score 6)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11
In reply to #10

Re: Calculation of heat generated by control panel elements

04/25/2012 4:47 AM

No-one can answer the question without knowing the resistance of the contactor coil.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Member

Join Date: Apr 2012
Location: mumbai
Posts: 8
#13
In reply to #11

Re: Calculation of heat generated by control panel elements

04/25/2012 4:50 AM

Ok sir i ll give u the resistance of the contactor on friday

Register to Reply Off Topic (Score 4)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#15
In reply to #13

Re: Calculation of heat generated by control panel elements

04/25/2012 4:53 AM

The calculation can be done right now!

  • Power dissipated is the voltage squared divided by the load resistance.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: Calculation of heat generated by control panel elements

04/25/2012 4:09 AM

As an order-of-magnitude first estimate, take the incoming voltage and multiply it by the panel's measured current.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#16
In reply to #8

Re: Calculation of heat generated by control panel elements

04/25/2012 4:54 AM

Do the same for the power leaving the panel to various loads. The difference is the power dissipated.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#17

Re: Calculation Of Heat Generated By Control Panel Elements

04/26/2012 2:13 AM

The Switchboard/MCC/Control panel manufacturer should calculate and provide ventilation facilities for his panel considering ambient conditions.

__________________
pnaban
Register to Reply
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#18

Re: Calculation Of Heat Generated By Control Panel Elements

04/26/2012 5:50 AM

http://cr4.globalspec.com/thread/71067#newcomments

Schneider Climasys

go to download documents & then download the software...

or go here schneider enclosures

i think these should help u out assuming you are asking about cooling the panel and not the entire room.....and why do u want to provide AC ? ventilation Fans are enough for control panels.

__________________
shamith gambhir, electrical engineer
Register to Reply
Member

Join Date: Apr 2012
Location: mumbai
Posts: 8
#19
In reply to #18

Re: Calculation Of Heat Generated By Control Panel Elements

04/26/2012 11:29 AM

i want to calculate as per the costumer requirement.

they needs it i.e. how much heat is generated during the work

Register to Reply Off Topic (Score 5)
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#20

Re: Calculation Of Heat Generated By Control Panel Elements

04/26/2012 1:03 PM

Quickest way is to assume the worst case and provide enough cooling to take care of it.

If you have a control power transformer or DC power supply, ASSUME that 100% of the rated capacity of that device is turning into heat INSIDE of the control panel. The only thing that would not be is anything that the control circuit is powering that is OUTSIDE, such as solenoids or external sub-control assemblies. So if you have a 1000VA CPT and nothing being powered outside of the panel, you ASSume that you have 1000W of heat rejection inside. Might be overkill because rarely are CPTs fully loaded, but it's a safe bet for A/C sizing. Alternatively if you use line power for your controls look up the data on each and every coil or power supply or pilot light in the panel and look at the watts consumption or rating. Again, 100% of that energy is going into the control panel in one form or another.

Then look at the power devices such as contactors, switches and circuit breakers and ASSume 0.1% voltage drop across each of the power contacts, anything more and the mfrs are in trouble (the value should always be in milivolts). Then calculate the resistance that represents and using your expected line voltage, calculate the worst case watts loss that represents.

If you have circuit breakers or overload Relays that have bi-metal thermal sensing elements, they are figured at 9W per phase each, that's the maximum design allowances for manufacturers, anything more and they get in trouble with regards to component sizing. If you use solid state OLs or CBs, don't count them, no heat losses to speak of.

If you have VFDs or other types of drives, assume 3% of the max power rating of the drive as heat rejection into the box. So if it is a 10kW VFD, assume 300W of heat rejection.

If you have a soft starter or other SCR based power device WITHOUT a bypass contactor, assume 4W per running load amp per phase; with a bypass contactor, assume it is the same as any contactor per the above.

If it is anything big enough to have bus bars, most likely it's a switchboard or Motor Control center, and the mfr will have guidelines on determining heat rejection.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**