Hi to all.
For one of our projects work, we took two (high & low) level switch contacts through reed switches with 24vac supply through the wires. Control panel & the level switch tank are away from around 400Mtrs. from each other. (200Mtr. cable is 4 core, flexible, 1 sq. mm in cross section & the remaining was around 200Mtr. 7 core, Armoured, 1&1/2sq. mm in cross section joint with each other). Through those reed switch contacts, we have connected two contactors (for high & low) of 24vac supply. But at the end we received only 10.5 vac supply which was unable to operate the contactors.
Then we replaced the 24vac contactors with 12vac operated relays. But at the end we received around 21.5 vac supply which could damage the relay.
Then we inserted two wire wound resistors of around 68 ohms in series with each of the ralays & dropped the voltage upto 11.5 & 13.5vac for resp. relays. Now the system works ok.
Is this because of voltage drop then what is the equation for it? What should be the problem & what is the solution for it.