Battery Bank Charging Query

04/30/2012 10:39 AM

Dear support team,

I have concern about the battery charging of banks. In our solar project there are 3 banks, 2 x 48V x 800 AH & 1x48V x 600AH. We would like to connect all banks in parallel to charge controller of the inverter.

As 2 banks are identical while other 1 no. is less in capcity i.e 600 AH, so what will be the impact on the system?

Is there any problem for equlise charging, any impact on charge controller or on battery's bank, etc?

Regards
ASAD

Register to Reply
Pathfinder Tags: Battery bank charging quiery
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster #1
#1

Re: Battery Bank Charging Query

04/30/2012 4:42 PM

You should mount the "1x48V x 600AH" battery approximately 7 feet above the "2 x 48V x 800 AH" batteries, depending on the elevation, declamation, and inclination of the of the installation. Latitude, Longitude and attitude will also come into play.

The added elevation will balance out the battery size and allow both batteries to charge and discharge with just the right balance. You'll need to use larger wire on the up-hill leg. In some cases, you may need a choke on the - side of the system to slow things down. This is rare.

You should hire an engineer.

Chao, Baby.

Register to Reply Off Topic (Score 6)
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#2
In reply to #1

Re: Battery Bank Charging Query

05/01/2012 12:20 AM

If I were saying garbage like that, I too would want to post anonymously!

I don't have enough experience in this area to give a good answer to the question, but I do have enough experience to know that post #1 is NOT a good answer!

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#4
In reply to #1

Re: Battery Bank Charging Query

05/01/2012 12:27 AM

Are you hallucinating? Get medical help.

__________________
Plenty of room here
Register to Reply Off Topic (Score 6)
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#3

Re: Battery Bank Charging Query

05/01/2012 12:24 AM

This is very little info to start with. To charge batteries you need a good controller with MPPT. This will take care of the optimal charge in different situations. If you want to keep it simple, you install your panels and connect groups in series so that you have more than 48 volts available to charge the batteries. My 48 volts groups are theoretically 4 X 12 volts, but I have more than 60 volts on a sunny day. This of course kills the batteries unless you protect these against overcharging. On the other hand it means also that there is more amperage available to connect eventually a bigger bank of batteries. To get more specifics, check the supply data of your panels. (current and voltage supplied)

Supply more information:

What is the composition of the banks: type of batteries - differences in cell capacities.

Your panels and controllers

Success

__________________
Plenty of room here
Register to Reply
Power-User
Popular Science - Weaponology - New Member Canada - Member -

Join Date: Dec 2006
Location: In the sticks of the Central Kootenays, BC, Canada
Posts: 266
Good Answers: 20
#5

Re: Battery Bank Charging Query

05/01/2012 2:00 AM

You should be considering a separate charge controller for each 48V string of batteries, or at least one on the 600AH string and one on the two 800AH strings, assuming the two 800AH strings are composed of identical batteries.

The idea is to optimize the charging of each type of battery, which each charge controller can do for only one type at a time.

The charging is a separate issue from the harvesting of energy from the solar panels...that is a different set of parameters that are sometimes at odds with what the batteries need. However, a previous poster is correct--you want a MPPT (Maximum power point) controller that holds the voltage and amperage from the panels at the maximum power the panels can deliver. The controller will change the voltage from whatever the panels deliver, (usually, down) to the voltage the battery bank requires with very little loss.

As it sounds like you already have the control equipment, you would be best off to contact the manufacturer of the equipmen to get their recommendations about charging connections to battery strings of differing AH capacities.

Jon.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6

Re: Battery Bank Charging Query

05/01/2012 2:09 AM

I'm not an expert, but I think parallel is inadvisable. It could lead to unequal charging currents for the individual cells.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#8
In reply to #6

Re: Battery Bank Charging Query

05/01/2012 6:52 AM

You are right, most manufacturers do not recommend it at all. Even the banks he has now are not optimal and could easily result in shorter life spans of individual batteries as weaker cells get damaged.

To the OP:-

The absolute best way to charge (but physically impossible on most modern batteries) is to charge each CELL as an individual.....also very expensive!

But even having a 12 volt (nominal) charger for each separate 12v battery would increase the life substantially of all.

Batteries always fail first at the weakest cell due to reverse polarisation of the cell when it is the first one discharged. This applies to all battery types that I know of. Therefore its best NOT to take a battery down to the minimum, even leisure batteries live longer when handled well....

Also NOT charging LA batteries to 100% charge increases their life dramatically too, I work with max 70%, that is before gassing starts for most LA batteries.....Also I don't discharge below 12.5 volts as sulfating starts around that time. Which is why when a battery goes below this level it should be recharged as soon as possible.

See the manufacturer's literature.

Whether this applies or not to other battery types I cannot say for sure, but if ANY battery gets warm, that is usually a bad thing!!!! So don't charge too fast or for too long!!

Leisure batteries are more forgiving of deep discharges....but also more expensive.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Posts: 1460
Good Answers: 30
#7

Re: Battery Bank Charging Query

05/01/2012 4:42 AM

This sounds like a scaled-up version of the problem with which every electric model aircraft fan is familiar, of how to charge series and parallel connected lithium cells rapidly. In that world the battery chargers now contain balancers, so that no individual cell is overcharged. The same idea is possible for charging in parallel. I have found this firm which claims to make a device to do your job of balancing parallel 12 V batteries:

http://www.cbcdesign.co.uk/batteq.html

though I have no personal experience of the product.

Register to Reply Score 1 for Good Answer
Participant

Join Date: Apr 2012
Posts: 3
#9

Re: Battery Bank Charging Query

05/01/2012 3:35 PM

As far as the batteries are concerned has anyone seen this link?

http://www.ted.com/talks/donald_sadoway_the_missing_link_to_renewable_energy.html

Look ma, one big battery which is very tolerant of overcharging!! Also it is promised to be VERY cheap in price.

Register to Reply Off Topic (Score 3)
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#10
In reply to #9

Re: Battery Bank Charging Query

05/01/2012 5:01 PM

I for one had not! Really impressive!

Magnesium is indeed less dense than salt, so that checks out. The main problem I see is that the melting point of Mg is just over 1200°F, so there is going to have to be some method of heating it; presumably the charging current will do that. Of course the thing is going to need some major insulation to minimize heat losses, and you certainly are not going to use one to power your laptop or cellphone! The melting point of copper is closer to 1100°F, so there will have to be some alloying of the connectors/electrodes.

Then of course it is a DC device; I don't know much about the current status of inverters for producing AC at these energy levels...

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply Off Topic (Score 4)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#11
In reply to #9

Re: Battery Bank Charging Query

05/01/2012 5:45 PM

Agreed, that was a great talk. It will be interesting to see if/when/how it develops in the marketplace.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Anonymous Poster #2
#12

Re: Battery Bank Charging Query

05/01/2012 11:10 PM

Hi,

As for my experience, the AH rating rating should not matter to the charge controller.

Since the V is same [48 Volts] and AH are different for battery banks, the single charge controller can take care of charging/discharging the battery banks.

Here is an example:

If 800Ah bank requires a constant current charge of 15A and 600AH bank needs 10A, than Charge controller will decides how ampere to push in to battery banks.

Remember since u have battery bank, not all banks are charged/discharged once.

It depends on priority you have set.

Thanks

Ravindra.R

Register to Reply
Active Contributor

Join Date: Nov 2009
Posts: 17
#13
In reply to #12

Re: Battery Bank Charging Query

05/01/2012 11:33 PM

Dear All,

Find reply I received from Alan Fidler
CBC Design

There isn't much of an implication for the charging system but unfortunately there is for the batteries!
It is not possible to parallel up sets of differing capacities. The reason for this is that the cells in parallel try to maintain a balance with the net result that one set will overcharge whilst the other undercharges. The result will be a wild imbalance between the uneven capacity cells.

Only cells packs of equal capacity can be connected in parallel with other cells packs.

Regards
ASAD

Register to Reply
Guru

Join Date: Oct 2009
Posts: 1460
Good Answers: 30
#14
In reply to #13

Re: Battery Bank Charging Query

05/02/2012 6:10 AM

I'm sure your expert is correct, but it would be nice if he could explain the reasoning behind his words of wisdom. He is, after all, in the business of selling balancers, and the advice might be slanted in the direction of selling more of them. I appreciate that when a discharged cell is paralleled with a charged cell, then there will be briefly a very high current which probably does no good at all, but when they are permanently tied in parallel that situation does not apply. The equivalent hydraulic model is filling two water tanks, with an interconnecting pipe, from a single tap.
Incidentally, paralleling a discharged cell with a full cell is exactly what happens when one uses jump leads to start a car with a flat battery.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#16
In reply to #14

Re: Battery Bank Charging Query

05/02/2012 8:35 AM

You would compare a parallel connection made for less than a minute to a 24/7 connection?

Not a good idea....

Also, generally cars have a single 12 volt battery, not 3 or more 12 volt Batteries in series......though this will change in the near future I am told to 48 volts (waitup till a new car jump starts an old one.......it will happen I am sure!)

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 1460
Good Answers: 30
#17
In reply to #16

Re: Battery Bank Charging Query

05/02/2012 1:03 PM

You would compare a parallel connection made for less than a minute to a 24/7 connection?

I do indeed, my theory being that an intermittent parallel connection is much more dangerous to the batteries than a permanent one. You have to explain to me the error in my thinking.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#19
In reply to #17

Re: Battery Bank Charging Query

05/02/2012 3:50 PM

You have to explain to me the error in my thinking.

Why must I improve your education? I am sure that nothing I say will change your flawed opinion...... So I won't bother....

Stay with this blog and I am sure you will learn a lot!!!

Have a great day.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#15
In reply to #13

Re: Battery Bank Charging Query

05/02/2012 8:26 AM

....and all bought from the same manufacturer on the same day from the same manufacturing lot......

Many forget this!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Canada - Member - New Member Hobbies - Musician - New Member

Join Date: Dec 2006
Location: Western Canada
Posts: 1863
Good Answers: 39
#21
In reply to #13

Re: Battery Bank Charging Query

05/02/2012 4:08 PM

Asad wrote:

"Only cells packs of equal capacity can be connected in parallel with other cells packs".Regards ASAD

Why then did you bother post your question? You already knew the battery banks were not of equal size. There seems to be a disconnect in your logic. Common sense should have told you it would not work. Would you place wheels of different size on either side of a car? Especially one fitted with only one engine!

__________________
Elnav
Register to Reply Score 1 for Good Answer
Guru
Canada - Member - New Member Hobbies - Musician - New Member

Join Date: Dec 2006
Location: Western Canada
Posts: 1863
Good Answers: 39
#18

Re: Battery Bank Charging Query

05/02/2012 3:41 PM

I am surprised that this group of experts did not give the most obvious explanation of all. Mechanics and electricians having any experience with multi battery banks will tell you that charging several batteries in parallel will result in premature failure of the bank as a whole, because one battery will fail within two years. This has been common knowledge for at least 20 years that I know of. At least that is when I first got told about it by an old mechanic.

The electrical explanation being that in any system of multiple parallel paths the current will divide according to Kirchovs law. This means one battery will charge faster than the others and the battery with the highest internal resistance will charge the slowest. Since only one charge controller is trying to feed two or more batteries it will respond to the voltage sensed in the highest level battery. If it is a smart controller it will alter the charge rate leaving the low battery insufficiently charged.

The end result is the weak battery fails first and prematurely. This in turn tends to affect the remainder of the batteries in the bank.

I used to work for one company where new batteries seldom lasted 18 months in service powering inverters because they were invariably paired up with old batteries. When we began replacing all batteries in a bank at the same time, duration between bank failure improved dramatically. With an entire fleet to maintain it was not difficult to find use for individual batteries instead of in banks powering inverters.

This is about as non technical an explanation as I can come up with. There is plenty of details regarding the electro-chemical activity involved but this tends to get somewhat tehcnical.

__________________
Elnav
Register to Reply Score 1 for Good Answer
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#20
In reply to #18

Re: Battery Bank Charging Query

05/02/2012 3:52 PM

GA. Good explanation Elnav.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Register to Reply 21 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (5); Anonymous Poster (2); ASAD MALIK (1); dkwarner (2); dredwinphd (1); dvmdsc (2); elnav (2); phph001 (3); sawmilleng (1); Tornado (2)