Lighting Circuits Without Neutral

05/15/2012 5:39 AM

Hello.

Is it possible to create a lighting system without neutral.

Actually in my case i have a 3Phase 3 Wire system with isolated neutral.

How do i power the lighting circuits without a neutral.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Lighting Circuits Without Neutral

05/15/2012 6:01 AM

Consider the installation of a zig-zag transformer with which to provide a neutral.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Lighting Circuits Without Neutral

05/15/2012 8:28 AM

You've missed out the most important detail. What is the line to line voltage?

Just out of interest why is the neutral isolated?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Active Contributor

Join Date: Feb 2011
Posts: 12
#21
In reply to #2

Re: Lighting Circuits Without Neutral

05/17/2012 2:41 AM

The line to line voltage is 230 V

the neutral is isolated since thats what the client wants :P

Register to Reply
Guru

Join Date: Dec 2010
Location: 1° North Singapore
Posts: 568
Good Answers: 17
#3

Re: Lighting Circuits Without Neutral

05/15/2012 8:33 AM

You can, but the Phase-phase voltage will be Sqrt(3) x 230 V for 230 V system. You can use 2 pc of lamp in series . one lamp will have only 200V. Incandescent and Energy saving lamp will work well, ES lamp best, Incand lamp slightly dimmer than on 230 V.

FL lamp or compact FL lamps with magnetic ballast may have start up problem.

__________________
Sharing knowledge is one thing that defies basic arithmetic logic --- the more you share, the more you get!
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: Lighting Circuits Without Neutral

05/15/2012 8:40 AM

Do encourage the original poster to use double-pole or triple-pole overload circuit breakers!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Apr 2007
Location: Hyderabad, India
Posts: 596
Good Answers: 12
#5

Re: Lighting Circuits Without Neutral

05/15/2012 8:44 AM

very simple: take three 100w single phase bulbs (of say 230V), connect them is star and connect each bulb to each phase (of say 415V) and leave neutral point in isolation... there you have done it.

__________________
Subramanyam
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #5

Re: Lighting Circuits Without Neutral

05/15/2012 8:58 AM

100W bulbs are no longer available.

What does srikanthuk do about switching, isolation and overcurrent protection?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#14
In reply to #5

Re: Lighting Circuits Without Neutral

05/16/2012 5:58 AM

That works if the supply voltage = √3*bulb voltage. But he hasn't told us either voltage. If bulb voltage = supply voltage he can just connect between any 2 phases.

__________________
Give masochists a fair crack of the whip
Register to Reply
3
Guru
Hobbies - DIY Welding - New Member

Join Date: Apr 2008
Location: Bristol, Tennessee
Posts: 1177
Good Answers: 58
#6

Re: Lighting Circuits Without Neutral

05/15/2012 8:50 AM

I come across a lot of 220 volt lighting fixtures. My high pressure sodium, metal halide, and 12 volt halogen lights all work on 220 volt. I'm sure the new LED fixtures and even the new electronic fluorescent fixtures probably can be found 220 volt. No neutral is required as far as I know for this type fixture, just a ground for safety.

__________________
mike k
Register to Reply Good Answer (Score 3)
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#8

Re: Lighting Circuits Without Neutral

05/15/2012 12:14 PM

You do not need a neutral. Just choose the lights that are rated for the phase to phase voltage. It is a common installation in the US.

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#9

Re: Lighting Circuits Without Neutral

05/15/2012 1:14 PM

I'm going to take a different tactic here.

Just pick any two wires and connect them to your lighting fixtures. Don't worry about supply voltages, or fixture ratings. They will just get you confused. The engineers who designed the fixtures had to plan for unlicensed electricians using their product in random ways, so if you get anything wrong their protection circuitry should work. Make sure you try changing a lamp once this is installed.

Ok, enough with the absurdity response.

Yes, it is possible to make a lighting system without a neutral.

The question should be will a lighting system without a neutral meet the electrical wiring code for your location? I do not know. I do not know where this lighting system will be so I cannot tell you.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#10

Re: Lighting Circuits Without Neutral

05/16/2012 12:04 AM

Professional installations use separate, to single phase transformer and breaker panel for light and general use. That normally is the code.

In your scheme you string up some light for, say 380 or 450V. The lightbulb voltages do not add up right. Then one day an unsuspecting electrician comes along, treats it as a normal 110V circuit, and get fried. What you think, who will be blamed?!? YOU.

Register to Reply
Associate

Join Date: Nov 2007
Posts: 53
Good Answers: 1
#12
In reply to #10

Re: Lighting Circuits Without Neutral

05/16/2012 1:09 AM

If the source is Y or 4 wire delta there is a neutral. If not, then select fixtures that run on the available output. If that is not practical, then install a transformer that will give the desired voltage...Clintb

__________________
Clintb3252
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#11

Re: Lighting Circuits Without Neutral

05/16/2012 1:05 AM

Connect between phase and earth,bypassing RCD.

__________________
pnaban
Register to Reply Off Topic (Score 8)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13
In reply to #11

Re: Lighting Circuits Without Neutral

05/16/2012 3:19 AM

Yeah, great. One loose connection on the earth lead and the next person to touch something on it gets electrocuted. Brilliant suggestion.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#16
In reply to #11

Re: Lighting Circuits Without Neutral

05/16/2012 9:07 AM

That has to be on of the most stupid statements I've ever read on this board!

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#15

Re: Lighting Circuits Without Neutral

05/16/2012 7:42 AM

Not clear. Please elaborate how the Neutral is isolated.

Is your distribution in Delta " Δ" ?

or

"Y" without the 4th wire= N in your system.

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#17
In reply to #15

Re: Lighting Circuits Without Neutral

05/16/2012 10:55 AM

What do you mean by distribution? Star or delta doesn't apply to the mains supply. Mains is 3 wires with a certain line-line voltage, and maybe a neutral. It's the rated voltage of the load compared with the supply voltage that determines how the load is connected.

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#23
In reply to #17

Re: Lighting Circuits Without Neutral

05/17/2012 8:02 AM

Regards.

Star and Delta surely apply to mains supply distribution.

In your country like ours it is Star [Y] 3+1 RST+N and domestic distribution is

normally single Φ; Φ & N; R+N; S+N or T+N.

In Europe it is UVW and somewhere it may be ...

In USA it Δ delta; Φ + Center-tap of Φ;

But Isolted Neutral is not understood.

Can you explain please?

Welcome for related answer. !!!!!

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#24
In reply to #23

Re: Lighting Circuits Without Neutral

05/18/2012 8:53 AM

I don't think star or delta is inherent in the mains supply. There are 3 phases with (in Europe) 400 volt between any 2. On a 3-phase motor, connection can be in star or delta depending on motor design, but if it's star it does not need a neutral as the star point is not connected to anything.

I agree a neutral is needed for single-phase (phase-neutral) use, but that doesn't mean the system is star. That's my take, somebody might disagree. The power company tries to share the single-phase loads between all 3 phases, so the current in the neutral to the transformer is small.

By isolated neutral I assume OP means there is no neutral wire in his mains lead, so single-phase operation is not possible, hence his question.

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#29
In reply to #24

Re: Lighting Circuits Without Neutral

05/19/2012 1:50 PM

I think let the OP say what he means.

I have not seen any country which only supplies Φ to Φ domestic supply.

I have no more explanation.

Regards

Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#18

Re: Lighting Circuits Without Neutral

05/16/2012 12:16 PM

This sounds like an industrial system. The most common non-residential service in the US is 480V 3-phase/3-wire supplied by a delta connected transformer bank. A delta-star lighting transformer supplied from the 480V service is used to provide a 3-phase/4-wire power supply with a neutral for lighting and receptacles.

If you insist on using 3-phase/3-wire, lighting can be installed across the line if the voltage rating of the fixture is appropriate to the mains voltage. Many marine installations do not use a neutral, but the equipment is only accessed by crew, not passengers. I would not recommend using an ungrounded system where non-electrical professionals have access.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply
Guru
Hobbies - RC Aircraft - New Member Hobbies - Automotive Performance - New Member Hobbies - DIY Welding - New Member

Join Date: Jul 2007
Location: Fort Lauderdale Florida
Posts: 5708
Good Answers: 123
#19

Re: Lighting Circuits Without Neutral

05/16/2012 12:21 PM

I taught my children that they need to either know the answer, or know where to get the answer.

If the OP has to ask, he should not do it.

__________________
Bob
Register to Reply
Active Contributor

Join Date: Feb 2011
Posts: 12
#22
In reply to #19

Re: Lighting Circuits Without Neutral

05/17/2012 2:47 AM

Honestly that is very bad advice, sometimes asking can get you a lot of help and will be beneficial in the futur.

Some advice from me, if you can't help its better not to comment.

Register to Reply
Active Contributor

Join Date: Feb 2011
Posts: 12
#20

Re: Lighting Circuits Without Neutral

05/17/2012 2:40 AM

Thanks to everyone who posted a reply.

The line to line voltage is 230V. So i guess we can use a bulb rated at 230V and get the lighting circuit working. Just so used to connecting phase and neutral. Thanks

We are not allowed to distribute the neutral through the system thats why we're not using a lighting trasnformer to obtain a neutral

Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#25

Re: Lighting Circuits Without Neutral

05/18/2012 10:35 AM

Hey, srika, you do what the customer supposedly want. Never mind the national and local code. When the s*** hits the fan, and you are sued, please report back to us on your misapprehension. Get it?

Have a good life, in the meantime.

Register to Reply
Active Contributor

Join Date: Feb 2011
Posts: 12
#26
In reply to #25

Re: Lighting Circuits Without Neutral

05/19/2012 1:27 AM

Your comment is just sad, hope you have a good life too and your negativity helps you in the future.

The client requirement of the neutral not being distributed and the Lighting circuits also as IT distribution has been discussed and they maintain they want it. Its nice right when people on the internet supposedly knows what other people need. There are National and Local codes for IT Distribution btw. If you go towards the North Africa Side you may notice they follow an IT network. I don't know about Europe.

But hey you seem to be a genius, maybe when i ave the lawsuit i could contact you for law advice, you seem to know what to do.

Cheers

Register to Reply
3
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#28
In reply to #26

Re: Lighting Circuits Without Neutral

05/19/2012 9:03 AM

Wait just one cotton picking minute here.

You understand that there are different electrical wiring standards around the world. You also understand that these regional standards should be followed or one will have either an unreliable or dangerous wiring installation. Yet you do not tell us what region this installation will reside.

You've gone from childishly annoying to completely and utterly useless here. People ask questions here because they need more information to answer a question. Sometimes the missing information gets lost because the translation into English of technical details does get lost. This scenario often leads to a series of Q&A that ultimately breaks through the language barrier. Far more often the Original Poster being asked a question by us instead of being provided an answer by us, will now demonstrate a lack of understanding of their problem that leads some of us to try to answer the original question with random suppositions of the missing information while some of us complain that this might lead to a dangerous situation.

You, srikanthuk, do not tell us where this lighting circuitry will be installed so we might be able to tell you which code to follow or if the appropriate code will permit lighting without a neutral. You instead refuse to answer any question posed to you. You attack one of the members who is frustrated with your repeated refusal to answer a simple question. Ironically your attack poses the very same question we have been directly and indirectly asking you.

Please, take your love of argument elsewhere.

http://www.youtube.com/watch?v=yTl9zYS3_dc

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 3)
Active Contributor

Join Date: Feb 2011
Posts: 12
#27

Re: Lighting Circuits Without Neutral

05/19/2012 1:40 AM

Does anyone know a good technical book to read about IT distribution system in Plants and how to go about it.

Could spare a lot of people here the headache.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#30
In reply to #27

Re: Lighting Circuits Without Neutral

05/21/2012 6:11 AM

Wikipedia.

It saves hiring a locally-qualified electrician!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 30 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: