in one of my power plant project . we have a battery charger with inbuilt DCDB. the rating of battery is 400Ah .

After commissioning the battery charger we found that 220V DC supply output found good and the system is running fine.

Suddenly one day we found that 230VAC supply is getting mixed up with DC output bus . after checking we found that AC supply is back feeded from a panel due to wrong wiring .

now my douts are as follows :

1) can AC supply mix up with DC Supply ?

2) whether it will affect my DC equipments like relay , solenoid coil , trip coil etc ,.?

3) one of my solenoid coil has got De-energised and now my client is saying that this has happened due to this the AC supply mix up with DC Supply . Is it due to that ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: 230V AC Supply has got mixed with 220V DC SUPPLY

05/15/2012 3:22 AM

Why did the overcurrent protection device not operate?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: 230V AC Supply has got mixed with 220V DC SUPPLY

05/15/2012 3:41 AM

A1) yes.

A2) yes.

A3) yes.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 2)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#9
In reply to #2

Re: 230V AC Supply has got mixed with 220V DC SUPPLY

05/16/2012 8:04 AM

GA. Short and accurate!!

LOL !!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Apr 2007
Location: Hyderabad, India
Posts: 596
Good Answers: 12
#3

Re: 230V AC Supply Has Got Mixed With 220V DC Supply

05/15/2012 8:32 AM

very confusing. how can dc mix up with ac? ac and dc (currents) can flow in same conductor. if you pass dc through ac solenoid it will burn. if pass ac through dc solenoid it will not burn.

__________________
Subramanyam
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#4

Re: 230V AC Supply Has Got Mixed With 220V DC Supply

05/15/2012 3:17 PM

Are you sure there is a physical circuit wiring problem and not just an AC signal being inductively coupled onto the DC bus?

__________________
jack of all trades
Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#5

Re: 230V AC Supply Has Got Mixed With 220V DC Supply

05/15/2012 11:29 PM

Are you sure, that one of the rectifier / regulator is not internally defective? A shorted rectifier or DC regulator component can put AC hum onto its DC output. If in doubt, simply measure the current components.

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#6

Re: 230V AC Supply Has Got Mixed With 220V DC Supply

05/16/2012 12:59 AM

In the wire where both ac & dc got mixed connect a data logger/power analyser and record the waveform.

__________________
pnaban
Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#7

Re: 230V AC Supply Has Got Mixed With 220V DC Supply

05/16/2012 7:49 AM

Regards.

Please have a 2nd look into your system and clarify what the DC power is doing here?

Are you using the UPS or Inverter for your system?

Or .... ?

Register to Reply
Power-User

Join Date: Apr 2011
Posts: 188
Good Answers: 6
#8

Re: 230V AC Supply Has Got Mixed With 220V DC Supply

05/16/2012 8:01 AM

If no changes were made to the system to cause this, I'd seriously suspect a rectifier...

Register to Reply Score 1 for Good Answer
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (1); corbinstein (1); Haajee (1); jack of all trades (1); kvsubramanyam (1); leveles (1); pnaban (1); PWSlack (2)

Previous in Forum: On & Off a Light Using Switches   Next in Forum: Lighting Circuits Without Neutral

Advertisement