Unstable Flow Problem in Magnetic Flowmeter

05/15/2012 6:56 AM

Dear All,

We have installed a magnetic flowmeter in a water line. There is a manual valve on upstream & a control valve on Downstream. When flowmeter gives pulse to control valve, valve closes rapidly. At this time, for a few seconds, flowmeter does not show the value of flow. after about 5 ~ 10 seconds, flowmeter begins working smoothly & show value accurately. Also we have installed the flowmeter as per instruction given by manufacturer. Please let me advise that what could be the reason of this problem???? & how can we rectify????

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#1

Re: Unstable flow problem in magnetic flowmeter

05/15/2012 7:14 AM

It strikes me that it's not a problem, it's to be expected.
A sudden disterbance causes a sudden disturbance.
Two Three solutions:-
1. Close the valve slowly.
2. Fit a load of smaller bore pipes inside the pipe upstream (maybe downstream too?)of the flow meter to help laminarize the flow (did I just make up that word?)
3. Ignore the 'problem'
my preference is for number 3.
Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Unstable Flow Problem in Magnetic Flowmeter

05/15/2012 7:18 AM

Has the response indication of the flowmeter been slugged in any way? Some details of the flowmeter would assist.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#10
In reply to #2

Re: Unstable Flow Problem in Magnetic Flowmeter

05/17/2012 6:00 AM

<groan>
You haven't answered any of the other questions.
If you want good answeres you need to respond and interact.
The fundamental question seems to be, are you trying to stop the flow or regulate it?
It you are trying to regulate it, you shoul n't be slamming the valve shut.
post#1 point#1 probably covers it, but in the absence of comment I shall unsubscribe from this discussion.
Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#3

Re: Unstable Flow Problem in Magnetic Flowmeter

05/15/2012 7:51 AM

>control valve, valve closes rapidly

When the downstream control valve slams shut the flow rate goes to zero or near zero.

The flow meter probably has a low-flow cutoff setting. Any flow below the low-flow cutoff setting is set to zero.

>flowmeter does not show the value of flow

Is this the local indicator display value? What does the 4-20ma analog output value show when this situation happens?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Unstable Flow Problem in Magnetic Flowmeter

05/15/2012 8:23 AM

What is the relationship between the flowmeter measurement and the change-in-flow pulses?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5

Re: Unstable Flow Problem in Magnetic Flowmeter

05/15/2012 12:33 PM

"When flowmeter gives pulse to control valve, valve closes rapidly."

At this point flow meter should show zero flow. That's normal isn't it?

My question is, is the flowmeter supposed to regulate the flow or stop it?

Register to Reply
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#6

Re: Unstable Flow Problem in Magnetic Flowmeter

05/15/2012 6:08 PM

The flowmeter output response time could also be affecting the signal that you "see". We have megnetic flowmeters in multiple locations with response times adjusted to suit the application. Some are set at miliseconds while others are at seconds. We datalog the lines to then get minutes/hours averaegs and so on.

__________________
Just an Engineer from the land down under.
Register to Reply
Power-User

Join Date: Mar 2011
Location: oz
Posts: 252
Good Answers: 10
#7

Re: Unstable Flow Problem in Magnetic Flowmeter

05/15/2012 7:36 PM

MAg flow meters work on velocity, this then is converted to flow when you enter your pipe size.If you do not achieve the min. velocity the meter will not read correctly.You can prove this by setting the output to measure velocity instead of flow and check if you are getting above min. value(manual).If this is the case ,use a smaller flow tube with reducers.

Register to Reply
Guru

Join Date: Jun 2011
Location: Mossel Bay, SA
Posts: 777
Good Answers: 21
#8

Re: Unstable Flow Problem in Magnetic Flowmeter

05/16/2012 3:09 AM

When flowmeter gives pulse to control valve, valve closes rapidly.

If this the intended design, the flowmeter is operating correctly.

If you don't want the valve to slam shut, you can adjust the positioner/ fit it with a valve positioner to slow down the action, or limit the valve travel for 'fully shut' to remain 10% open.

Register to Reply
Power-User

Join Date: Dec 2010
Location: Tulsa, OK
Posts: 184
Good Answers: 2
#9

Re: Unstable Flow Problem in Magnetic Flowmeter

05/16/2012 9:07 AM

When you close suddenly a valve you can have water hammer effect, drop of flow so sudden it upsets the measurement and most importantly what are the response characteristics of the mag meter electronics.

Even though you are measuring a flow, the electronics are set up so that minute changes are eliminated by filters, these same filters are trying to read your flow changes even if they are abrupt and will show the last stable indication prior to the change till it stabilizes.

Register to Reply