Fire Door Closing

05/16/2012 3:31 PM

The counterweight/closing mechanism on the fire door at my Church has broken. The door is the type that rolls on a sloped track. The counterweight incorporated a fusible link, a short length of rope, and a cable. Why was the rope used? I can't find any specs old enough (circa 1920s) to give me any information. Can someone tell me where these specs can be found? All I have found so far is modern information. Thanks.

__________________
Lehman57
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: fire door closing

05/16/2012 3:59 PM

The rope was cut to release door manually?

There's gotta be some old codger here who would know.

We didn't have fire doors back on the farm. Not even at the church.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: Fire Door Closing

05/16/2012 4:03 PM

Probably a backup release mechanism....If sprinkler systems have been installed and/or water curtain, this may have changed code requirements...DASMA is the trade group association for doors, you might find useful info from their website...

http://www.dasma.com/

http://evanjacover.com/archives/category/engineering

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Engineering Fields - Nuclear Engineering - New Member

Join Date: Sep 2009
Location: Louisville, OH
Posts: 1925
Good Answers: 36
#8
In reply to #2

Re: Fire Door Closing

05/16/2012 8:34 PM

I see where you got the picture. Our installation is similar, but the left-most cable goes up to near the ceiling, around another pulley, then to the right over the door opening where the rope section and fusible link are. All except the fusible link and rope is steel cable.

__________________
Lehman57
Register to Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#9
In reply to #8

Re: Fire Door Closing

05/16/2012 8:40 PM

Sounds like the patent drawings above.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#14
In reply to #8

Re: Fire Door Closing

05/17/2012 12:21 AM

Yes this is an original design with all rope in the same configuration....The fusible link(160º), which is a modern upgrade used on fire doors and dampers today, releases on heat, the rope for flame...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Power-User

Join Date: Sep 2009
Location: N38º3', W085º3'
Posts: 326
Good Answers: 19
#18
In reply to #8

Re: Fire Door Closing

05/17/2012 6:04 AM
[quote]

===similar, but the left-most cable goes up to near the ceiling, around another pulley, then to the right over the door opening where the rope section and fusible link are.---

[quote]

Could the extra pulley and rope have been added later to move the counter weight nearer to opening as a makeshift exit device? I can see this modification as it might not take as many people to get tthe door open enough to get through.

just a thought from the sidelines.

__________________
There's a theory stating if anybody discovers exactly what the Universe is for & why it is here, it will instantly disappear & be replaced by something even more bizarre & inexplicable. There's another theory stating this has already happened.D Adams
Register to Reply
Anonymous Poster #1
#40
In reply to #2

Re: Fire Door Closing

01/21/2013 6:33 AM

At what price did you get that from DASMA?

_________________

foam system

Register to Reply Off Topic (Score 5)
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#3

Re: Fire Door Closing

05/16/2012 4:05 PM

"Why was the rope used?" You don't really tell us about the setup. Is the weight suspended from the rope? Is the piece of rope a sort of splice in the cable? Does the rope look like it is intended by the manufacturer to be there?

"Can someone tell me where these specs can be found?" Manufacturer? This will probably be of little value; these gravity doors were often fabricated at some local steel shop to a project specific specification.

"The counterweight/closing mechanism on the fire door at my Church has broken." What, exactly, is broken? Is it a worthwhile effort to repair it?

__________________
Semper Ubi Sub Ubi
Register to Reply
Guru
Engineering Fields - Nuclear Engineering - New Member

Join Date: Sep 2009
Location: Louisville, OH
Posts: 1925
Good Answers: 36
#10
In reply to #3

Re: Fire Door Closing

05/16/2012 8:46 PM

"Why was the rope used?" You don't really tell us about the setup. Is the weight suspended from the rope? See my reply to #2. Is the piece of rope a sort of splice in the cable? No. Does the rope look like it is intended by the manufacturer to be there? Yes, but I don't know whether original or modified.

"The counterweight/closing mechanism on the fire door at my Church has broken." What, exactly, is broken? Is it a worthwhile effort to repair it? I haven't found who discovered the problem to find out what actually broke, but I suspect fatigue in the cable from running around the pulley. It probably has to be repaired to keep the fire inspector happy. Besides, I like to have old junque functional.

__________________
Lehman57
Register to Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#20
In reply to #10

Re: Fire Door Closing

05/17/2012 9:22 AM

I haven't found who discovered the problem to find out what actually broke,

Well, okay. When you do there may be some helpful input from the forum, instead of our already assembled collection of guesses.

It probably has to be repaired to keep the fire inspector happy.

Prolly. Remember, it it does not latch it will not pass... See NFPA 101. No, a church is not exempt from building codes.

__________________
Semper Ubi Sub Ubi
Register to Reply
2
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#4

Re: Fire Door Closing

05/16/2012 4:07 PM

Think I found it.............interesting. See #5.

http://sfmvm.com/museum-renovation-tour/hall-of-americas-renovation/

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5
In reply to #4

Re: Fire Door Closing

05/16/2012 4:16 PM

Belt and suspenders? Rope and FL.

Nice find.

Register to Reply
Guru

Join Date: Jun 2006
Posts: 501
Good Answers: 8
#19
In reply to #4

Re: Fire Door Closing

05/17/2012 6:42 AM

Then it appear that the rope was the original safety link and a temperature senitive fusable was added at a later time.

Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#6

Re: Fire Door Closing

05/16/2012 4:21 PM

The rope was the original "fusible link" that would burn to release the door. Sometime later the rope was partially cut off and replaced with the new fusible link, which was an advance in technology.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Nuclear Engineering - New Member

Join Date: Sep 2009
Location: Louisville, OH
Posts: 1925
Good Answers: 36
#11
In reply to #6

Re: Fire Door Closing

05/16/2012 8:54 PM

Possible, but I don't know that. If the fusible link was added, it may have been to take care of high temperatures without the flames to burn the rope.

__________________
Lehman57
Register to Reply
Guru
Engineering Fields - Nuclear Engineering - New Member

Join Date: Sep 2009
Location: Louisville, OH
Posts: 1925
Good Answers: 36
#13
In reply to #6

Re: Fire Door Closing

05/16/2012 9:01 PM

Quite possible, but this was well before my time there. The link would have been added to take care of high temperatures without flames.

__________________
Lehman57
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#33
In reply to #13

Re: Fire Door Closing

05/17/2012 2:33 PM

Those type doors were developed after the Chicago fire. The rope was the original fusible link. It was unreliable, let the fires burn too long in large areas until the temperature reach a level to cause combustion of the rope and failure of the rope after years of service had people replacing it with what ever was at hand the rope was never really spec out. A better fusible link was developed. In mandating it's use by the fire departments. On older door the rope was left. I guess they looked at the rope as back up if the fusible link did fail. Cheaper too then replacing the whole wire cable.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru
Engineering Fields - Nuclear Engineering - New Member

Join Date: Sep 2009
Location: Louisville, OH
Posts: 1925
Good Answers: 36
#38
In reply to #33

Re: Fire Door Closing

05/17/2012 2:53 PM

Thank you. This is the type of information I was hoping for. My son, who is a firefighter, never heard of the rope. Having it as a backup after better technology was developed makes sense.

__________________
Lehman57
Register to Reply
Guru
Hobbies - RC Aircraft - New Member Hobbies - Automotive Performance - New Member Hobbies - DIY Welding - New Member

Join Date: Jul 2007
Location: Fort Lauderdale Florida
Posts: 5708
Good Answers: 123
#39
In reply to #38

Re: Fire Door Closing

05/18/2012 1:52 PM

The extra pully system may have been added along with the fuseable link. The link needed to be as high as possible to detect heat sooner.

__________________
Bob
Register to Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#7

Re: Fire Door Closing

05/16/2012 4:54 PM
__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Guru
Engineering Fields - Nuclear Engineering - New Member

Join Date: Sep 2009
Location: Louisville, OH
Posts: 1925
Good Answers: 36
#12
In reply to #7

Re: Fire Door Closing

05/16/2012 8:59 PM

Interesting! I think the old building where I used to work had some sort of latch, but I don't know it used whether a fusible link or something else.

__________________
Lehman57
Register to Reply
Guru

Join Date: Jun 2006
Posts: 501
Good Answers: 8
#15

Re: Fire Door Closing

05/17/2012 12:24 AM

The cable was too short and the rope jury rigged to make up the lenght.

Register to Reply
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#16

Re: Fire Door Closing

05/17/2012 2:58 AM

Presumably the fusible link is what actually breaks in event of fire. You don't want the rope to break or burn through else the door won't shut.
Therefore use a thin wire cable (bowden cable).
The only spec is :- It must withstand the weight and still work in a fire.

I can't actually see the problem, unless gravity has stopped working in the region of the door.
Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Guru
Engineering Fields - Nuclear Engineering - New Member

Join Date: Sep 2009
Location: Louisville, OH
Posts: 1925
Good Answers: 36
#35
In reply to #16

Re: Fire Door Closing

05/17/2012 2:35 PM

The fusible link and the rope are in series--either can break and disable the counterweight. The way it has been hooked up for years is that the door is always closed; the counterweight just makes it easier to open, but gravity will still close it. That means the cable is moving around one pulley with every opening, and eventually fails due to fatigue.

__________________
Lehman57
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#17

Re: Fire Door Closing

05/17/2012 5:23 AM

Does this failure mean that the theft and fire insurance is invalid until it is fixed?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Nuclear Engineering - New Member

Join Date: Sep 2009
Location: Louisville, OH
Posts: 1925
Good Answers: 36
#32
In reply to #17

Re: Fire Door Closing

05/17/2012 2:29 PM

Invalid fire insurance--I sure hope not. It was re-hooked up by some unknown person so that the door works, but it is illegal because the fusible link is beside the door, not over it. I have new cable, still have to find suitable rope, then re-do the hookup. That's why I asked here--to see if I can use some suitable sash cord, or whether I need to seek something made for fire doors. Looks like a suitable diameter sash cord (cotton) will be sufficient.

__________________
Lehman57
Register to Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#34
In reply to #32

Re: Fire Door Closing

05/17/2012 2:35 PM

You know, this just occured to me.

Why not have the local fire inspector come over and have a look, and sign off on it when it's right?

Why risk being denied insurance money in the event of a fire?

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Power-User

Join Date: Sep 2008
Posts: 196
Good Answers: 6
#21

Re: Fire Door Closing

05/17/2012 10:23 AM

Maybe it was all that was available to use at the time.

More than likely the rope was used as a fuseable-link.

Ideally the fire would burn the rope into removing the counterweight and thereby making the door more difficult if not impossible to open.

This is a simple way of keeping the fire from spreading to adjacent areas and to discourage/prevent personnel from opening a door and being immediately exposed to the affcets of a fire.

Register to Reply
Guru
Hobbies - RC Aircraft - New Member Hobbies - Automotive Performance - New Member Hobbies - DIY Welding - New Member

Join Date: Jul 2007
Location: Fort Lauderdale Florida
Posts: 5708
Good Answers: 123
#22

Re: Fire Door Closing

05/17/2012 11:29 AM

Have you tried N.F.P.A.?

__________________
Bob
Register to Reply Score 1 for Good Answer
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#23

Re: Fire Door Closing

05/17/2012 11:39 AM

Jeez why is something so simple causing so much confusion and dithering.
Gravity...fusible...link...heavy door.
C'mon guys it's not rocket science.
Maybe I've been posting in invisible ink again?
THE ONY RELEVAN SPEC IT THAT OF THE FUSIBLE LINK, and to check the door will actually roll shut and close under it's own weight. The rope is a red herring, a chain is only as strong as the weakest link and in this case it should be the 'designed for purpose fusible link'
Get a grip for pities sake.
Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply Off Topic (Score 4)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#24
In reply to #23

Re: Fire Door Closing

05/17/2012 11:49 AM

Rope preceded fusible metal links in fire door closure technology.

Would wood work?

Register to Reply Off Topic (Score 5)
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#25
In reply to #24

Re: Fire Door Closing

05/17/2012 11:58 AM

My suggestion would be to lose the fusible link and post an expert archer in every room. In case of fire.....................shoot the rope in two, dropping the weight and allowing the door to close. Looks like the best solution to me.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply Off Topic (Score 6)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#28
In reply to #25

Re: Fire Door Closing

05/17/2012 12:23 PM

I'll take one of those. It looks like a fine solution to the problem, whatever it was.

Register to Reply Off Topic (Score 5)
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#29
In reply to #25

Re: Fire Door Closing

05/17/2012 2:07 PM

Most appealing answer currently, where do you get your archer pics from?.

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#30
In reply to #29

Re: Fire Door Closing

05/17/2012 2:10 PM

Del. He's trying to teach me the finer points of archery.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#31
In reply to #30

Re: Fire Door Closing

05/17/2012 2:18 PM

Archery hell. That's Debarchery, with a K.

Register to Reply
Guru
Engineering Fields - Nuclear Engineering - New Member

Join Date: Sep 2009
Location: Louisville, OH
Posts: 1925
Good Answers: 36
#37
In reply to #25

Re: Fire Door Closing

05/17/2012 2:48 PM

I suspect that the maintenance costs of the archer (food, restroom, enhancements, etc, even if volunteer) would exceed the costs of the present system!

__________________
Lehman57
Register to Reply Off Topic (Score 5)
Guru
Hobbies - RC Aircraft - New Member Hobbies - Automotive Performance - New Member Hobbies - DIY Welding - New Member

Join Date: Jul 2007
Location: Fort Lauderdale Florida
Posts: 5708
Good Answers: 123
#26
In reply to #24

Re: Fire Door Closing

05/17/2012 12:03 PM

Would wood work?

Only in Woodward.

__________________
Bob
Register to Reply Off Topic (Score 5)
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#27
In reply to #24

Re: Fire Door Closing

05/17/2012 12:21 PM

Did you hear about the fella who built a wooden car? Wooden wheels. Wooden bodywork. Wooden engine, even.

And when he started it up it wooden go!

__________________
Semper Ubi Sub Ubi
Register to Reply
Guru
Engineering Fields - Nuclear Engineering - New Member

Join Date: Sep 2009
Location: Louisville, OH
Posts: 1925
Good Answers: 36
#36
In reply to #24

Re: Fire Door Closing

05/17/2012 2:43 PM

This adds weight to the thought that the metal fusible link was added sometime after construction. The building was built in 1923; do you have any idea when the codes suggested a fusible link?

__________________
Lehman57
Register to Reply Off Topic (Score 5)
Register to Reply 40 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: