Feeder Pillar Panels

05/23/2012 11:10 PM

This is requirement in India. For a New residential Colony there is a requirement of Feeder Pillar panels. No of pillars are 1000 nos (approx). Each Pillar will have one incomer of 200 Amps MCCB and and 6 nos of outgoing with one 63 Amps MCB and Energy meter for every outgoing.

The customer has specified outdoor type Feeder pillar panel with modular type of construction .( Each feeder will have separate compartment and individual door)

Apart from the above there will be outer Door.

My query is "What is the practice followed by others elsewhere?"

My thinking is Modular type is not required and simple Feeder Pillar will suffice the requirement

I would like to have the latest trend.

Thanks in advance.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Feeder Pillar Panels

05/23/2012 11:54 PM

I think one must distinguish between regulatory and customer requirements. So long as the customers' requirements do not conflict with regulations, they can ask for whatever they wish, even if legally superfluous. And then the prospective contractor can explain how a simpler (and less expensive) system will comply with the regs. It then becomes a matter of negotiation.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#2
In reply to #1

Re: Feeder Pillar Panels

05/24/2012 12:04 AM

Dear sir

Thanks for your prompt reply.

I am not finding fault with the customer.For convincing the customer only I have approched CR4 forum to get the Trend /latest developments in other parts of the world,so that I can suggest to the customer.

May be experts like you can inform us the latest trends.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 131
Good Answers: 5
#6
In reply to #2

Re: Feeder Pillar Panels

05/24/2012 11:59 PM

Technically speaking compartmentalised arrangement has an advantage that in the event of any short circuit within a particular module, other modules and the panel as a whole don't get affected. However this will be costlier arrangement than a non-compartmentalised feeder pillar panel. If this was not specified in the enquiry specification, you can negotiate the commercial implications with the customer.

Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#8
In reply to #6

Re: Feeder Pillar Panels

05/25/2012 2:36 AM

Dear Sir

Thanks for your response.

I also do agree with you that compartmental design will be better and any short circuit will not get spread to other areas.But the cost will be high because of additional sheet metal work.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#3

Re: Feeder Pillar Panels

05/24/2012 1:47 AM

Discuss with Consultant the economic advantage of single compartment for 6 outgoing instead of 6 compartments which occupy more space. Also ask him why he want that way.Check his credentials(his past experience etc).

__________________
pnaban
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#4

Re: Feeder Pillar Panels

05/24/2012 12:38 PM
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#5
In reply to #4

Re: Feeder Pillar Panels

05/24/2012 1:11 PM

Dear Sir

Thanks for the Link.This is really useful to us.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#7
In reply to #4

Re: Feeder Pillar Panels

05/25/2012 1:16 AM

This is made to American standard, do you have a link to similar document in BS or VDE?.

__________________
pnaban
Register to Reply
Active Contributor

Join Date: Feb 2012
Location: Norfolk, England
Posts: 11
#9

Re: Feeder Pillar Panels

05/25/2012 2:38 AM

My company use Merin Gerin (Schneider) SAIF feeder pillars. These can be designed to suit requirements including MCCB, metering and load shedding as required. They are designed to be IP2X compliant and allow some works to be carried out while the panel is live (dependent on individual risk assessment and method statement) They also allow individual circuits to be isolated and earthed while working on them and come with lighting and heaters as required.

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#10
In reply to #9

Re: Feeder Pillar Panels

05/25/2012 3:21 AM

Can you show some drawings/pictures of different models?.

__________________
pnaban
Register to Reply
Commentator
France - Member - New Member

Join Date: Feb 2012
Location: Grenoble, France
Posts: 76
Good Answers: 4
#11

Re: Feeder Pillar Panels

05/25/2012 3:37 AM

Feeder pillar usage , in the IEC world (i e outside North America) , is only seen in British influenced public distribution networks (UK, Ireland, Australia, India, gulf ........).

Usually, each feeder is not compartimented individually.

In your case, as you have energy meter for every outgoing, which is not always the case, your customer may want that different people have access to different feeders metering, which could be a good explanation for this request.

Register to Reply
Commentator

Join Date: Jun 2011
Location: Hyderabad, India.
Posts: 92
Good Answers: 2
#12

Re: Feeder Pillar Panels

05/25/2012 4:08 AM

Mr. Obouill has given the almost good answer.

Before giving my reply, I would like to have some more information on outgoing MCBs that whether it is 3-Pole or 3-Phase or 1-pole or single Phase. From calculation based on MCCB Amps rating & MCB amps rating it looks as single phase type. In Saudi Arabia Feeder Pillar Panel is all 3phase due to the electricity is available one of the cheapest in cost in the world

__________________
B.E, M.I.E, M.S
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#13
In reply to #12

Re: Feeder Pillar Panels

05/25/2012 5:01 AM

Dear sir

It is 3 phase 4 wire system and the MCB to be incorporated would be 63 Amps 4 pole.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Participant

Join Date: Jan 2012
Posts: 3
#14

Re: Feeder Pillar Panels

05/25/2012 4:16 PM

can you post a picture of a "feeder pillar"?

Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#15
In reply to #14

Re: Feeder Pillar Panels

05/26/2012 10:19 AM

The link below is picture and details by a manufacturer

http://www.unimeeceng.com/modular-power-distribution-panel-958025.html

Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#16

Re: Feeder Pillar Panels

05/26/2012 10:37 AM

Recently in India the the trend is for modular compartmental unit for each flat or house in newly built colonies to protect from malpractices which you know. This is not a real technical requirement and I feel not required in US or UK as such tampering never happens there . So they do not think to design such feeder pillar boxes which costs more. In US mostly power distribution is normally overhead and small pole mounted transformers are installed for three four houses and service wire are taken directly to the house meter board and from there to the DB inside the house. And for large buildings normal indoor type DB are used.

Register to Reply
Active Contributor

Join Date: Feb 2012
Location: Norfolk, England
Posts: 11
#17

Re: Feeder Pillar Panels

05/26/2012 5:57 PM

Page to view Schneider SAIF feeder pillar http://www.schneider-electric.co.uk/sites/uk/en/products-services/electrical-distribution/products-offer/low-voltage-switchgear-feeder-pillars/switched-insulated-fusegear/saif-switched-insulated-fusegear.page Hope this helps

Register to Reply
Register to Reply 17 comments