Why in LT System Neutral is Solid Ground and Why Not in HT System?

05/28/2012 9:14 AM

why in LT system nuetral is solid grounded and why not in HT system (6.6KV in my case)

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: why in LT system nuetral is solid grounded and why not in HT system (6.6KV)

05/28/2012 9:19 AM
  1. How many 6.6kV hand-held appliance socket outlets are there locally?
  2. How many single phase loads are connected to the 6.6kV?
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Why in LT System Neutral is Solid Ground and Why Not in HT System?

05/28/2012 10:17 AM

To keep fault currents to manageable levels. By using a NGR the current is limited while the fault protection relays take over and cut the supply.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3

Re: Why in LT System Neutral is Solid Ground and Why Not in HT System?

05/28/2012 12:14 PM

Pw's and Tony's answers give good reasons for no neutral but in addition HT systems are usually connected to transformers and these connections are delta and no need for a neutral.

Register to Reply Score 1 for Good Answer
Associate

Join Date: Oct 2009
Location: kuruman NC. SOUTH AFRICA
Posts: 51
Good Answers: 1
#4

Re: Why in LT System Neutral is Solid Ground and Why Not in HT System?

05/29/2012 7:23 AM

on LT system were 3ph 4wire system (Star Connected on Secondary) is used, you need a solid grounded neutral and the neutral currents must be monitored by NEM with NER and the Adit relay, to trip your CB when your neutral current exceed the set value.

On HT System: is normally a Delta connected 3ph 3wire. but if there is any need for the neutral wire on the Delta connected TRNF, Neutral compensator can be used (and the above will be applied)

__________________
Dan Segami
Register to Reply
Associate

Join Date: Mar 2010
Posts: 28
#5

Re: Why in LT System Neutral is Solid Ground and Why Not in HT System?

05/29/2012 8:53 AM

sir,

actually we are having 16MVA transformer of 33KV/6.6KV Delta star in which nuetral is grounded through NGR.

and 2MVA transformer of 6.6KV/415V Delta star in which nuetral is solid grounded.

i want to know what is the difference in two systems of grounding and why ?

Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6
In reply to #5

Re: Why in LT System Neutral is Solid Ground and Why Not in HT System?

05/29/2012 10:12 AM

Look at my answer for the 33/6.6KV transformers.

As for the LV transformer, you do not restrict the earth loop impedance under most circumstances (it's against most national codes) due to the danger of touch potential to earth.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

DannyD (1); PWSlack (1); TonyS (2); venu kodeboyina (1); wareagle (1)

Previous in Forum: Float Test   Next in Forum: Solar Management Question

Advertisement