05/28/2012 9:14 AM
why in LT system nuetral is solid grounded and why not in HT system (6.6KV in my case)
Re: why in LT system nuetral is solid grounded and why not in HT system (6.6KV)
05/28/2012 9:19 AM
  1. How many 6.6kV hand-held appliance socket outlets are there locally?
  2. How many single phase loads are connected to the 6.6kV?
Good Answers: 181
Re: Why in LT System Neutral is Solid Ground and Why Not in HT System?
05/28/2012 10:17 AM
To keep fault currents to manageable levels. By using a NGR the current is limited while the fault protection relays take over and cut the supply.
05/28/2012 12:14 PM
Pw's and Tony's answers give good reasons for no neutral but in addition HT systems are usually connected to transformers and these connections are delta and no need for a neutral.
05/29/2012 7:23 AM
on LT system were 3ph 4wire system (Star Connected on Secondary) is used, you need a solid grounded neutral and the neutral currents must be monitored by NEM with NER and the Adit relay, to trip your CB when your neutral current exceed the set value.
On HT System: is normally a Delta connected 3ph 3wire. but if there is any need for the neutral wire on the Delta connected TRNF, Neutral compensator can be used (and the above will be applied)
Dan Segami
05/29/2012 8:53 AM
sir,
actually we are having 16MVA transformer of 33KV/6.6KV Delta star in which nuetral is grounded through NGR.
and 2MVA transformer of 6.6KV/415V Delta star in which nuetral is solid grounded.
i want to know what is the difference in two systems of grounding and why ?
Good Answers: 181
05/29/2012 10:12 AM
Look at my answer for the 33/6.6KV transformers.
As for the LV transformer, you do not restrict the earth loop impedance under most circumstances (it's against most national codes) due to the danger of touch potential to earth.