Solar Management Question

05/29/2012 1:11 AM

Dear Fellow CR4'ers,

I cannot get enough power from our solar panels into the grid. The problem is that the grid supplies most of the time 245 to 246 volts (122.5 to 123 between phase and neutral)

The inverters are limited to 250 Volts. First I tried to higher this limit, but it costed me dearly on Power Mosfets.

This is now the test solution I figured out:

I charge a big battery bank and run the inverters out of this. When I have enough storage, I put quite a lot of power back in the grid when it is already dark and the line voltage drops.

The current supply from the panels at 24 volts can run up to 400 Amps. This goes over a contactor relay that disengages when the grid is off. (12o Volts AC coil)

If I keep feeding DC the inverters are in danger.

The batteries need a automatic controller: during the day

When the battery becomes high in voltage, I feed DC to more inverters - I range it per 250 Watts each - In the circumstances here 24 Volts 200Ah works well with 4 125 Watts panels and 2 inverters.

What I need is a kind of multi threshold set points voltage detection, say in steps of 0.4 to 0.5 volts from 22 Volts DC and up (the batteries are deep cycle hermetic) to 28 Volts.

Sort like a bar VU meter that supplies outputs per section.

At 29.2 volts the pressure valves of the batteries open and that is a scary sound. My ears still whistle.

The outputs should control a latch relay (electromechanical - e.g motorized) to save power for each group of inverters.

Is this something on the market or is there maybe a PLC (low budget !!) solution?

All help is welcome.

Thanks. D.

__________________
Plenty of room here
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Solar Management Question

05/29/2012 7:14 AM

A little thought experiment suggests that when the grid voltage is high, it doesn't seem to need any more power from the solar panels. So it is better to store the harvested energy and supply it to the grid when the voltage is low. So, rather than keep changing knackered MOSFETs, increase the storage to the economic limit of practicability and stop there.

Someone must have designed the system to work within the available parameters. What about a telephone call to talk it through with that individual?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#2
In reply to #1

Re: Solar Management Question

05/29/2012 8:15 AM

Thanks PW: The system as you describe works fine with some neighbors.

Their voltage is like 235- 238. It is in this small difference that the problems arise. The inverters need to absorb and ventilate the extra energy when the voltage is too high in the grid. I figured out that an extra fan helps me out but not enough to be on the safe side. The biggest concern now is to keep the battery voltage in acceptable limits. There must be some comparator circuitry to take care of it. It works fine when I am standby and keep the battery between 25 and 27.5 volts. Heavy duty DC relays need also close to .8 amps. At the end causing lots of wasted power. A call to supplier learned me that this is the design voltage.

__________________
Plenty of room here
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Solar Management Question

05/29/2012 8:23 AM

<...Solar Management Question...fan...comparator...>

Not a timeswitch, then? Why not export at night?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Nov 2006
Location: Ontario, Canada
Posts: 146
Good Answers: 1
#8
In reply to #2

Re: Solar Management Question

05/29/2012 11:51 PM

I'm surprised the charging controller doesn't have a dumping load. You should check with the mfg, maybe it is an addable option.

__________________
Logic is the art of going wrong with confidence. -- Morris Kline
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#10
In reply to #8

Re: Solar Management Question

06/06/2012 1:52 AM

I do not control the solar charging. The panels are connected to the batteries.

I try to keep the charge between the battery limits with switching more inverters on and off, but need a reference like a VU bar meter with 20 A relais.

__________________
Plenty of room here
Register to Reply
2
Power-User

Join Date: Jun 2009
Posts: 134
Good Answers: 11
#4

Re: Solar Management Question

05/29/2012 12:50 PM

The grid is AC, so what is the problem with using an auto transformer to step the voltage up or down a small amount?

However they say that the correct way to add power to the grid, is to have the power source phase lead the grid phase by a small amount. Have you discussed this with whoever designed your solar system?

Register to Reply Good Answer (Score 2)
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#5
In reply to #4

Re: Solar Management Question

05/29/2012 8:47 PM

Thanks also. The only night option is a problem, the batteries can easily get overloaded during the daytime. It can happen in 10 minutes with the sun we have here. It is just a matter of clouds or no clouds. I pick it up later. Have an urgent matter.

__________________
Plenty of room here
Register to Reply
Power-User

Join Date: May 2012
Posts: 159
Good Answers: 14
#6
In reply to #4

Re: Solar Management Question

05/29/2012 10:57 PM

That is close to how we coupled generators to power grids when I was a Naval nuclear engineer. The generator to be coupled to the grid would be running at a slightly higher frequency than the grid. There was a meter that showed whether they were in phase or out of phase and by how much. When they were close to in phase, but with the generator being brought on line slightly faster (higher frequency) and slightly leading, the connection was made. It was done manually.

Register to Reply
Power-User

Join Date: Nov 2006
Location: Ontario, Canada
Posts: 146
Good Answers: 1
#7
In reply to #6

Re: Solar Management Question

05/29/2012 11:40 PM

That works fine with a mechanical generator because it will automatically sync itself to the line through inductive slip and loading of the engine but inverters have to sense the line to stay in sync. I'm sure his inverter(s) are designed to do this but if they only go up to 250V (is that RMS?) then the current is going to be limited.

I think an autotransformer should take care of it but OP should consult the mfg. Surely OP is not the first person to have this problem.

__________________
Logic is the art of going wrong with confidence. -- Morris Kline
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#9
In reply to #4

Re: Solar Management Question

05/30/2012 3:59 PM

I owe you all more info:

Total panels installed: 40 pieces - Max available power: 6.800 Watts.

Battery bank: 24 Volts, 6 groups parallel 1.200Ah.

Inverters: 26 in parallel - 13 over each phase to neutral.

The inverters measure the grid at a frequency of 16.000 Hz (quartz crystal triggered) and immediately send a pulse, higher than the measured value back into the grid.

This allows a cos phi of 0.99 to 1.

This frequency can be measured at the output but completely disintegrates after meeting the first line transformer.

In full sun, currents from the panels can run up to 200 Amps to the batteries. Critical is when the batteries are getting charged, close to Upper limit. The panel curve moves closer to the MPPT ( 17,3 X 2 Volts) and the output increases faster and faster then.

__________________
Plenty of room here
Register to Reply
Register to Reply 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Carl Pugh (1); dvmdsc (4); GordieGii (2); jerrys (1); PWSlack (2)