Dear Fellow CR4'ers,
I cannot get enough power from our solar panels into the grid. The problem is that the grid supplies most of the time 245 to 246 volts (122.5 to 123 between phase and neutral)
The inverters are limited to 250 Volts. First I tried to higher this limit, but it costed me dearly on Power Mosfets.
This is now the test solution I figured out:
I charge a big battery bank and run the inverters out of this. When I have enough storage, I put quite a lot of power back in the grid when it is already dark and the line voltage drops.
The current supply from the panels at 24 volts can run up to 400 Amps. This goes over a contactor relay that disengages when the grid is off. (12o Volts AC coil)
If I keep feeding DC the inverters are in danger.
The batteries need a automatic controller: during the day
When the battery becomes high in voltage, I feed DC to more inverters - I range it per 250 Watts each - In the circumstances here 24 Volts 200Ah works well with 4 125 Watts panels and 2 inverters.
What I need is a kind of multi threshold set points voltage detection, say in steps of 0.4 to 0.5 volts from 22 Volts DC and up (the batteries are deep cycle hermetic) to 28 Volts.
Sort like a bar VU meter that supplies outputs per section.
At 29.2 volts the pressure valves of the batteries open and that is a scary sound. My ears still whistle.
The outputs should control a latch relay (electromechanical - e.g motorized) to save power for each group of inverters.
Is this something on the market or is there maybe a PLC (low budget !!) solution?
All help is welcome.
Thanks. D.