Previous in Forum: CT Burden Calculation   Next in Forum: Multiple Generators in Parallel
Close
Close
Close
10 comments
Rate Comments: Nested
Commentator

Join Date: Nov 2009
Posts: 89

How to Connect DGPT2

05/31/2012 4:40 AM

I have a Type F4 Feeder typical, within the typical is a trip coil rated at 24V DC. The terminal block for the typical drawer has connections for remote Fault, remote Status and trip coil (MX). Presently i want to connect a DGPT2 to the trip coil terminal point but DGPT2 requires 48V DC and the trip coil is rated at 24V DC.

My point is how the DGPT2 is going to get 48V DC such that when there is an internal fault in the liquid insulated transformer, the DGPT contacts change state and the trip coil is actuated into operation to trip the breaker. Please anyone with better understanding should please help me out.

The drawer is in 400V distribution board (Schneider Electric).

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: How to connect DGPT2

05/31/2012 6:11 AM

What did Schneider Electric say in response to the telephone call?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Nov 2009
Posts: 89
#2
In reply to #1

Re: How to connect DGPT2

05/31/2012 6:59 AM

We have not gotten any response from Schneider. We're trying to work things out on our own for now.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3
In reply to #2

Re: How to connect DGPT2

05/31/2012 11:09 AM

Strange way to work it out yourself. Asking a bunch of strangers.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#4

Re: How to Connect DGPT2

05/31/2012 4:39 PM

Does the DGPT2 transformer protection relay not have dry contact alarm outputs for you to use to switch a separate 24VDC supply to control the trip coil?

Why can't you do this?

__________________
jack of all trades
Register to Reply
Commentator

Join Date: Nov 2009
Posts: 89
#5
In reply to #4

Re: How to Connect DGPT2

06/05/2012 9:44 AM

Thank you very much to everyone. You want me to use one of the alarm contacts, Probably like the first tempearature alarm output contacts to switch a 24V supply.

Please can u elaborate more on how u think the connection should be. If possible with a diagram or a link where i can read more on this issue.

Email: benotype@yahoo.com

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#6
In reply to #5

Re: How to Connect DGPT2

06/05/2012 3:30 PM

Come on now this is really basic stuff, just read the manuals for the transformer alarm and breaker - the alarm contact is being used to switch a CONTROL voltage which is used to control your trip coil, this is standard industrial control practice and what the equipment is designed for.

If we need to show you how then you likely aren't qualified to be doing the work.

Also please don't post your email on a public forum (due to potential spam issues).

__________________
jack of all trades
Register to Reply
Commentator
France - Member - New Member

Join Date: Feb 2012
Location: Grenoble, France
Posts: 76
Good Answers: 4
#7
In reply to #5

Re: How to Connect DGPT2

06/07/2012 4:40 AM

benotype,

if you wish to connect to Schneider experts, I can help you finding the right contact, plse send me the type of switchboard (IEC, NEMA, ...?) and country of installation.

Register to Reply
Commentator

Join Date: Nov 2009
Posts: 89
#8
In reply to #7

Re: How to Connect DGPT2

06/07/2012 5:31 AM

LV Switchboard (INDOOR)

Rated Service Voltage: 400V AC

Rated Power: 2500KVA

Rated Current: 3920A

Frequency: 50HZ

Number of Source: 2

Rated Shrt Circuit Current: 70KA RMS

Rated Peak WIthstand Current: 154KA

Earthing System: IT

Nigeria

My interest is on a drawer in the LV Board.

Typical: F4

How to connect a DGPT as stated in my question.

Register to Reply
Commentator
France - Member - New Member

Join Date: Feb 2012
Location: Grenoble, France
Posts: 76
Good Answers: 4
#9
In reply to #8

Re: How to Connect DGPT2

06/07/2012 5:46 AM

I understood from what you said that the switchboard was produced by Schneider.

So any data allowing to trace to the orginal plant and schematics would make life much easier ...

Register to Reply
Commentator

Join Date: Nov 2009
Posts: 89
#10
In reply to #9

Re: How to Connect DGPT2

06/09/2012 8:09 AM

Thank you very much.This is all the infomation i could get from the document.

Department: Systemes Equipments Tableux Base Tension

Document Number By Schneider: TV240100

Register to Reply
Register to Reply 10 comments
Copy to Clipboard

Users who posted comments:

benotype (4); jack of all trades (2); obouill (2); PWSlack (1); TonyS (1)

Previous in Forum: CT Burden Calculation   Next in Forum: Multiple Generators in Parallel

Advertisement