Multiple Generators in Parallel

05/31/2012 6:08 AM

When generators are operating in parallel , neutral contactors are interlocked with generator breakers to ensure that only one generator's neutral is connected to earth to eliminate circulating currents. What happens if prime mover the generator, of which,neutral is connected to earth fails and breaker do not trip

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Member

Join Date: May 2012
Posts: 5
#1

Re: Multiple Generators in Parallel

05/31/2012 10:06 AM

What I understood - the prime mover of the generator of which neutral is connected to earth has failed. Since there are other generators connected in parallel, the generator for which the prime mover has failed and breaker has not opened, will draw active and reactive power from the system and will work as a motor. Under this situation if a ground fault occurs in the system, the ground fault current will flow through the generator of the faulty unit.

Register to Reply Off Topic (Score 3)
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: Multiple Generators in Parallel

06/01/2012 11:25 AM

The sequence of events is unclear but it sounds like the prime mover has tripped and the generator breaker(s) failed to open. A one-line diagram would help but without it we have to assume that the Stuck-Breaker/backup protective relaying scheme would initiate tripping of all individual generator breakers and the next zone out; i.e., the high-side of the generator step-up transformer, so as to isolate the remainder of the switchyard from the failed generation. Until the fault clears the generator on the failed prime mover will draw real and reactive power from the remaining generation and the grid as the answer from Arishkdhar stated. (Editorial remark: I'm not sure why his answer was flagged as "off-topic'.)

The NGR scheme would play no part in any of this unless OP had specified that there was a ground fault somewhere in the first protective zone. If this was an interview question it was designed to to test the depth of the interviewee's specific knowledge of generation and switchyard protective relaying, there is no way to fake your way through this one.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 2)
2
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#3

Re: Multiple Generators in Parallel

06/02/2012 1:39 AM

Dear Sir

I am repeating your query for easy understanding.

There are 3 DG sets namely DG1,DG2 and DG3.

Whenever you are paralleling these 3 sets you have to make the first set to be Master.In this case let us say DG1.

The neutral of the Master DG set (DG1) will be connected to the System Neutral.The neutral of other two DG sets DG2 and DG3 will be floating.

Under such circumstances if the DG1 trips or stops, There will not be any neutral for the system, and any single phase loads connected to the system will be affected/ damaged.

It is ,therefore, advisable to open other two DG sets from the system immediately on failure of Master Set .

This is more common on 3 phase 4 wire LT systems.The system should not operate with out any neutral even for a second other wise single phase loads will be affected and get damaged due to over voltage.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply Good Answer (Score 2)