Unbalancing of Power Transformer

06/01/2012 12:09 AM

can a delta star 33/11 KV unbalanced power transformer be balanced with some modification inexisting set-up. so that load get always balance current.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: unbalancing of power transformer

06/01/2012 3:40 AM

Yes, it is possible. The way to do it is to make sure that the same load on the LV system downstream is present on each of the three phases. Then the neutral current will be zero. In practice, this can never be achieved as by their very nature, LV single phase loads come and go.

  • When adding single phase loads to existing LV distribution boards, the tendency is for the electrician to start at the top-left in the absence of other instructions. In the UK, the chances are that this will be the red (pre-2006 terminology) or brown (post-2006 terminology) phase, so this phase will usually be more heavily loaded than the others. To balance the load, simply move some of these onto one of the other two phases.

Only local investigation can determine what is the correct thing to do, and how much of it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Unbalancing of Power Transformer

06/01/2012 8:02 AM

How out of balance is the transformer output, what problems is it causing?

Only you can determine if the loads can be swapped between phases, we don't have access to your system.

__________________
The reports of my death are greatly exaggerated.
Register to Reply