0.55 KW Single Phase Exhaust Fan Motor Cable

06/01/2012 12:04 AM

Dear All,

Kindly tell me that if I can use 1.5 mm cable for starting of single Phase Exhaust fan Motor through DOL.

Best Regards,

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: 0.55 KW Single Phase Exhaust Fan motor cable

06/01/2012 12:33 AM

What voltage? What is the FLC? What does your local Code say? How long a cable?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Associate

Join Date: Apr 2012
Posts: 37
#2
In reply to #1

Re: 0.55 KW Single Phase Exhaust Fan motor cable

06/01/2012 1:15 AM

Dear Tornado,

The voltage is single phase 230 Vac. The FLC as I have mentioned through KW is 2.3 A. The maximum length of the cable is 10 metres. I could not find the local codes but I think that international standards are ok and applicable anywhere.

Best Regards,

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #2

Re: 0.55 KW Single Phase Exhaust Fan motor cable

06/01/2012 3:44 AM

<...international standards are ok and applicable anywhere...>

There is no such thing as an international code, and therefore it is inapplicable. The North American electrical codes do not apply in Europe, and vice-versa, for example.

In the absence of a local electrical code one might apply the principles embraced by British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: 0.55 KW Single Phase Exhaust Fan motor cable

06/01/2012 1:34 AM

Yes, 1.5 mm2 wiring should work for this motor.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5

Re: 0.55 KW Single Phase Exhaust Fan Motor Cable

06/01/2012 8:06 AM

The simple answer is yes.

You will have .29% volt drop.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Participant

Join Date: May 2012
Posts: 2
#6
In reply to #5

Re: 0.55 KW Single Phase Exhaust Fan Motor Cable

06/06/2012 2:16 AM

1.5 sq.mm is okay

but 2.5 Sq.mm copper 50/.25 ( as per IS 694 std)

current carrying capacity up to 21A

Voltage Drop/A/m - 29millivolt

Register to Reply