AC-DC

06/04/2012 4:01 AM

what's the effect of using ac mcb's in dc ckt? (with picture)

Register to Reply
Pathfinder Tags: dc mcb
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Ac-dc

06/04/2012 4:35 AM

Arc quenching is more difficult with DC than AC, so AC MCBs might not be sufficient.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Commentator
France - Member - New Member

Join Date: Feb 2012
Location: Grenoble, France
Posts: 76
Good Answers: 4
#2

Re: Ac-dc

06/04/2012 5:46 AM

An AC breaker limits the current value and the voltage / current phase shift by adding an arc resistance in the circuit, which is usually highly inductive. Thus it accelerates the arrival of a zero of current, which appears anyway naturally at every half cycle.

In DC, there is no natural zero of current, therefore the arc voltage must be much more important ( and at the end reach an infinite value) to force the current to zero.

Short circuit interruption in DC is much more difficult in DC than AC, this is why manufacturers have different designs.

Of course, all this is mainly related to voltage, a 690 Vac breaker should work easily at 12 V DC ... and even a bit more ;-)

But , at equal voltage, chances are high than an AC breaker simply never interrupts a DC short circuit if important .. and explodes .

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: AC-DC

06/04/2012 11:49 AM

Under normal current carrying condition, there shall not be any problem though. When breaking short circuit currents, in DC applications, the AC MCB is highly de-rated as DC current interruption is quite challenging (you know! no current zeroes in DC as in AC). Moreover, the instantaneous release setting may have to be reviewed.

Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#4
In reply to #3

Re: AC-DC

06/08/2012 6:46 AM

IEC code allows use of AC MCBs in DC circuits and provides derating that is necessary.

__________________
Raghunath
Register to Reply