Anonymous Poster #1

Instrumentation Grounding

06/04/2012 4:07 AM

why do we have a separate grounding network for instrumentation and control, we cannot connect the instumentation equipments directly with the main grounding grid.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#1

Re: instrumentation grounding

06/04/2012 6:05 AM

On instrumentation usually low amplitude and high impedance signal world, a few millivolts is enough percentage to ruin the result. And since ground is often used as AC or as DC signal reference, and neither dimensionless nor zero impedance conductors have to be used for grounding, those few mV are easy to pick in an EMI rich environment, so "ground" is NOT always and everywhere in your system at ZERO potential. Not to mention the relativistic latencies and reflections that get more significant as system bandwidth goes up and everything becomes a transmission line, or the potential danger to use a power ground with low enough impedance to protect user from mains leaks, but really crappy on surges and EMI for the circuit. Now one practical way to minimize problems like noise susceptibility and instability is by avoiding "ground loops", and use one point as ground, connect everything that must be grounded there, star-like. What we mainlly achieve by that is unknowingly common mode cancelling of picked-up and thus unwanted interference (either from outside, or from other parts of the cirquit, like from a noicy digital bus). Making loops, you form coils AND antennas, cancelling is ruined, and of course chance of instability and oscillations due to delay mismatch-phase shifts increases (...) S.M.

__________________
Life is complex. It has a real part and an imaginary part.
Reply Good Answer (Score 2)
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Instrumentation Grounding

06/04/2012 11:46 AM

GROSSLY INCORRECT. Vide IEEE 1100, it is "improper" to have a dedicated, clean, isolated earthing system for any sensitive electronic equipment. Even IEC 60364 terms this practice improper.

Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#3
In reply to #2

Re: Instrumentation Grounding

06/04/2012 12:54 PM

I think SM is correct.

Note that he did not say "earth".

He recommended a classic "star" ground, with one end of drain/shield floating. I have systems with miles of shielded cable, and that is what I usually do. Nary a problem, even around rotating electrical equipment.

I give him a GA for accurately helping the OP.

__________________
An obstacle is something you see when you take your eyes off the goal.
Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#4

Re: Instrumentation Grounding

06/05/2012 1:18 AM

As engineers from different parts of the world participate in this forum it is better if they quote references (code/standards-NEC/BS/IEC/VDE etc) with their replies.

__________________
pnaban
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Instrumentation Grounding

04/26/2023 8:52 AM

Because one doesn't generally want an earth fault of several tens of kiloamperes appearing in the instrumentation circuits; such a fault tends to cause unwanted catastrophic and unplanned self-disassembly issues there.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply