Until 15 years back air insulated Busducts were installed for connecting the transformers and the switch boards.There were not any failures of Busducts.
But of late most of the installations have been provided with Sandwich type Busducts especially in India.Failures are more in these type of sandwich type Busducts.
On Analysis I have observed that the bus bar sizes used in the Sandwich Busduct seems to be less.
For example ,in Sandwich Busducts for 1000Amps the size of Aluminium Busbar used is 100 mm x 6 mm.The open air rating of Aluminum busbar of size 100 x 6 mm is only 1260Amps.
The deration factor for temperature rise and enclosure to be taken into consideration.This will be 0.635, for temperature rise of 55 deg C over an ambient of 50 deg C.(This is only for Sandwich type.For Air insulated it will be 35 deg C rise for an ambient of 50 deg C)
After applying deration factor the current carrying capacity of busbar is only 800 Amps.
Similarly in air insulated busducts,for joints there will be fishplate joints.this will be overlapping type.The contact area will be adequate with sufficient bolting (minimum 4 nos)to have very good joint such that there will not be much contact resistance.
Whereas in Sandwich type there is no bolting but there is only pressure plate with only one bolt to have adequate pressure on the plate.Even the contact area is less.
My query is how and why Manufacturers of Sandwich type Busduct incorporate less cross sectional Bus bars?
What is the basis?
In chennai,India, I have noticed many highrise buildings,Software parks have been provided with these type of Sandwich Busducts and in most of the installations some failure or other occured.This may also be attributed to very poor installation.