Need Details Regarding Infra-Red Sensors

06/22/2012 3:44 AM

We are having 4600 series Infra-Red sensor of Hasentek make for our coal conveying system. We do not how it works and requiring maintenance manual. If possible please me details regarding the standards for installing IR sensor for fire detection and its communication to main controller.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Mar 2012
Location: Hot Humid Houston
Posts: 229
Good Answers: 29
#1

Re: Need details regarding Infra-Red sensors

06/22/2012 3:59 AM

Pradheep - Because Hasentek is making the 4600 series for you, tell them to send you the manuals and the installation guides.

Then, repost that you have the manuals and I (or other CR4 members) will contact you so you can send us the information. Then, maybe we can help you.

I will say this - I think you are going to get a wide variety of comments about the proper application of IR detectors for Fire Detection in or around a Coal Conveyor unless you have a very good control on your dust situation. Once the IR detectors are covered in coal dust... I think you have a problem.

Get in touch with Hasentek and make sure they know what you intend to do with their sensor. Did they recommend this specifically? Did a Fire Suppression/Detection Specialist or MEP Engineer design this?

Lots of questions, right? And we don't even have the manuals, and you don't either!!!

After it is decided this is the right detector for the application, THEN you can start worrying about the communication to the controller.

Get the manuals and re-post, okay? We will try to help you out.

__________________
txmedic3338
Register to Reply Score 1 for Good Answer
2
Guru
Popular Science - Biology - New Member Hobbies - Musician - New Member APIX Pilot Plant Design Project - Member - New Member Hobbies - CNC - New Member Fans of Old Computers - ZX-81 - New Member

Join Date: Jan 2007
Location: Centurion, South Africa
Posts: 3921
Good Answers: 97
#2

Re: Need details regarding Infra-Red sensors

06/22/2012 5:09 AM

Try Hansentek

www.hansentek.com/design_2_detail.html

www.hansentek.com/brochures/Brochure_4600SolarBlind.pdf

__________________
Never do today what you can put of until tomorrow - Student motto
Register to Reply Good Answer (Score 2)
2
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#3

Re: Need Details Regarding Infra-Red Sensors

06/22/2012 11:59 AM

Infra-red sensors are normally "dark environment" sensors. In other words, they work best when they cannot see ANY ambient light. The detector you have selected can work adequately in the presence of ambient light.

These detectors are considered "spark" detectors. They only "see" energy emitted in the infra-red spectrum, and characteristic with a carbon fire.

When designing your system, I recommend the following:

1. Take into account the half power cone of vision of the device (don't try to cover more area with a device than recommended by the manufacturer).

2. If your environment includes lots of suspended particulate dust, consider the air purge option for the lenses. If air purge is unworkable for you, monitor the lens surface closely for the first few months of operation to determine the cleaning frequency required.

3. Install test lamps at each detector location. These devices will emit Infra-red radiation when activated, allowing you to prove the devices are working. These should be activated by test activation switches at your controller. You should also have "detector active" LED's at the controller to prove that they are working when testing.

4. You should have a water spray nozzle installed down-conveyor from the detectors. The distance will be calculated based on the conveyor velocity and the time in milliseconds for the water solenoid to open fully from time of detector activation.

5. Install a flow switch in the water line with a flow indicator at the controller. The system is useless if the solenoid has failed. Install a solenoid disconnect switch at the controller, that will place the controller into a trouble state when activated. You can now test the detectors without flowing water. The trouble indicator will remind the operator to re-engage the solenoid when testing is complete.

6. The entire system should be arranged as "non-latching". The system should be able to extinguish a spark and self reset to a "ready and working" condition.

7. I recommend a spark counter be employed. If a given number of sparks are counted in a given time period (say 25 sparks in 1 minute) the system shuts down the conveyor for inspection.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply Good Answer (Score 2)
Associate

Join Date: Jul 2011
Posts: 30
#4

Re: Need Details Regarding Infra-Red Sensors

06/23/2012 1:58 AM

I have got the Engineering and installation manual. But how to upload manual, here i am unable to understand uploading of manul.

Register to Reply
Register to Reply 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Hendrik (1); pradeepdhoni (1); txmedic3338 (1); WJMFIRE (1)

Previous in Forum: Temperature Control Process   Next in Forum: Differential Pressure Created by Orifice

Advertisement