Knee Point Voltage for PS Class CT

06/26/2012 3:23 AM

Dear All,

Please guide me for the calculation of knee point voltage for PS Class CT (for REF Protection of Trafo)

Transformer Rating:10MVA,33/11.5kV,Dyn11, CT Ratio Selected 50/5,5,5A as Phase CT and the system to be protected for Restricted Earth Fault protection)

My Questions are

1) What should be CT Ratio of the NCT to be mounted in the Transformer and its knee point voltage.

2) What should be Neutral Current transformer Voltage Level (11kv or 0.415kV)

3) Should the Phase CT mounted at HT Panel and NCT should be of same Specifications?

Kindly guide me.

__________________
anandsmm
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Nov 2011
Posts: 171
Good Answers: 1
#1

Re: Knee point voltage for PS Class CT

06/26/2012 4:59 AM
Register to Reply
Member

Join Date: Feb 2010
Location: Gurgaon
Posts: 9
#2
In reply to #1

Re: Knee point voltage for PS Class CT

06/27/2012 1:40 AM

@nobodysomebody47
In the link you have posted, Vs = If (RCT + 2RL)
But I've come across the following formula
Vs = If (RCT + RL+Rr)where Rr is the relay resistance
Can you explain?
If is Fault current converted to CT secoondary. What is 3200 in the calculation below?
If = (Ifp*5)/3200 =39.52A

Register to Reply
Participant

Join Date: Jun 2012
Posts: 3
#4
In reply to #2

Re: Knee point voltage for PS Class CT

07/05/2012 4:45 AM

[3200] is the no. of turns on secondary side of CT. i.e., 3200/5A is the CT ratio. 'Ifp' is the fault current on the primary side and 'If' is the current reflected on the secondary side which will be [5/3200] times the primary fault current.

the voltage across relay Vs is the voltage across relay terminals and should not include relay internal resistance Rr. It is considered while calculating the knee point voltage of the CT.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#3

Re: Knee Point Voltage for PS Class CT

06/29/2012 8:48 AM

Dear anandsmm,

The (3) point as mentioned by you is the correct answer.

Regards,

Manindra

__________________
Manindra
Register to Reply
Participant

Join Date: Nov 2012
Posts: 4
#5
In reply to #3

Re: Knee Point Voltage for PS Class CT

11/15/2012 12:08 PM

Hi mr. mahindra,

What if the Knee point voltage of both end cts are different.??

Register to Reply
Associate

Join Date: Mar 2013
Posts: 31
#6
In reply to #5

Re: Knee Point Voltage for PS Class CT

07/15/2014 2:57 AM

In case of through faults the secondary currents of both the end CTs will not match due to saturations and hence differential relay will trip which ultimately is unstable operation.

Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

avnishnarula86 (1); evangelist (1); manindra (1); nobodysomebody47 (1); PRS (1); vyral2311 (1)