UPS Undervoltage Issues

06/26/2012 12:25 AM

Hi all,

I have a APC 650VA 400W ups. The battery needed replacement however the battery does not give any specs on it. The only data i could find regarding the battery is that it is 108VAh. I repalced the battery with a 12V 8Ah battery and let the battery get charged. Upon switching to back up i observed that the output delivered was 140 V instead of 220V. The UPS did not indicate any faults. What could be the issue. Any help would be greatly appreciated.

Regards

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: UPS Undervoltage Issues

06/26/2012 1:08 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Associate

Join Date: Nov 2011
Posts: 48
#2
In reply to #1

Re: UPS Undervoltage Issues

06/26/2012 1:16 AM

Thanks SolarEagle.

As you see the battery specs mention only 108 Volts-Amp-Hours. It doesn`t mention the voltage and the amp-hours seperately. I couldnt find the RBC 17 battery in my markets.

Register to Reply
Anonymous Poster #1
#3

Re: UPS Undervoltage Issues

06/26/2012 3:05 AM
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#4

Re: UPS Undervoltage Issues

06/26/2012 9:01 AM

APC's battery replacement services are quite excellent. They know exactly what battery is required for each of their models, and will (for a reasonable cost) ship it to you with a pre-paid return mailer for the old battery so that it can be recycled. I have done this on several of my APC UPSs over the years, and it is a very simple process. Contact them (at the links other posters have provided).

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#5

Re: UPS Undervoltage Issues

06/26/2012 6:14 PM

Nightshade,

First issue, for UPS Battery replacement, contact the vendor or check their website (APCs is excellent) and you can't go wrong.

Second issue, when you pulled the case off to replace the battery, you possibly pulled a connector or bumped the voltage selector switch at the back of the unit.

I am assuming you checked the the original batteries before you removed them to see if they were serial or parrallel connected and then connected them the same way.

If the Battery input is now 12VDC as opposed to 24VDC or 48VDC this will case you problems too, although this would likely leave the UPS non functional it is a possibility.

If you still have issues take it to your nearest APC Service Centre and they will happily fix it for you.

Regards,
Sapper

__________________
It's all about the Boom! - MythBusters
Register to Reply
Associate

Join Date: Nov 2011
Posts: 48
#6
In reply to #5

Re: UPS Undervoltage Issues

06/27/2012 12:04 AM

Thanks guys.

I have contacted APC services. Will revert when i get a reply

Register to Reply
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#7

Re: UPS Undervoltage Issues

06/27/2012 1:52 AM

If you observe the top of the battery you will see 6 caps for the internal vents, this would indicate 6X2=12Volts.

Something is wrong test the battery volts whilst running a faulty couple of cells would drag the output down. otherwise your ups has a problem.

__________________
Dont get on to the roundabout if you dont know how to get off
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#8

Re: UPS Undervoltage Issues

06/27/2012 1:56 AM

Your UPS is most probably working fine.

This UPS has a modified sine wave output (stepped sine wave).

Your regular AC voltmeter is designed to show proper RMS voltage only for sine-waves at regular mains frequencies. That is why you are getting what appears to be a low reading.

Plug an incandescent lamp into your UPS output to see if it illuminates as brightly as it would directly to mains.

Most small UPS are like this.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Associate

Join Date: Nov 2011
Posts: 48
#9
In reply to #8

Re: UPS Undervoltage Issues

06/27/2012 4:24 AM

Wal

You have a very valid point here. How ever i plugged the UPS to a 22W flourescent light and it did not operate. Will run some checks again when i get home from office.

Thanks

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#10
In reply to #9

Re: UPS Undervoltage Issues

06/27/2012 5:01 AM

Hmm. Reactive load perhaps? Some induction motors don't take kindly to modified sin wave... never noticed fluoro lethargy though....

My UPSs are all online true sin wave units so can't confirm. Anyone else?

__________________
Difficulty is not an obstacle it is merely an attribute.