Class of Neutral CT

06/26/2012 5:55 AM

I would like to know, if I am having a Restricted Earth fault protection for a 11/.433kV,1600kVA transformer, and I am having the phase CTs of class PS, should the neutral CT be of the same class PS?

Generally, the phase CTs are provided in the 11kV VCB panel by the panel manufacturer and neutral CT by the transformer manufacturer. how do i ensure that the parameters like knee point voltage and saturation levels are same for phase CTs and neutral CTs? Or in first place, do they need to be same?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Active Contributor

Join Date: Aug 2009
Posts: 11
#1

Re: Class of Neutral CT

06/26/2012 7:31 AM

Not necessarily, but it will surely make your life easier. Test the CTs and compare the magnetising curves. If different, ensure your relay settings suit the configuration.

__________________
A wise man didn't become wise over night.
Register to Reply
Associate

Join Date: Sep 2008
Posts: 39
Good Answers: 1
#2

Re: Class of Neutral CT

06/28/2012 9:08 AM

"should the neutral CT be of the same class PS?"

Answer: Yes

" how do i ensure that the parameters like knee point voltage and saturation levels are same for phase CTs and neutral CTs?"

Answer: You need to specify the parameters of Neutral CT while tendering. Even after the award of purchase order you can provide these details to the transformer vendor.

For NCT you need to specify, CT ratio, class of accuracy, Knee Point voltage and Magnetising current Im.

For this particular case, specify 2500/1 A , PS class CT.

knee point voltage vk should be greater than or equal to 2 If(Rct + 2RL)

If is fault current reflected on CT secondary side. For 1600 kVA, the impedance is 6.25 %. With this we get fault current of 34.13 kA. Hence If is (1/2500)*34.13kA = 13.65 A

Here Rct CT secondary resistance. Get this from CT supplier. Usually transformer manufacturer outsources this CT from some vendors.

RL -- lead resistance of cable from CT to relay(For REF ANSI no.64). This you can calculate by finding the distance between HT Panel and Transformer. Use 4 Sq.mm or 2.5 sq.mm wire Copper.

Magnetising current should be less than 30 milli Amp @ Vk/2.

Prashanth

Register to Reply Score 1 for Good Answer
Participant

Join Date: Jun 2012
Posts: 3
#3
In reply to #2

Re: Class of Neutral CT

07/02/2012 3:48 AM

thank you sir.

i presume that the knee point voltage for the CTs in phase busbars shall be similar to the value computed by the formula for NCT and the same should be specified in specifications being given to panel manufacturer while ordering.

Register to Reply
Register to Reply 3 comments