Dear All,
Could somebody explain me about the cable size between Transformer Neutral to NGR and NGR to Ground. I have used the formula I^2xSqrt(t)/K for the cable between Neutral to NGR. I dont know whether the same cable can be used between NGR to ground. Please guide me I will be very thankful to you. Please correct me if I am wrong.
Regards,
D. Madhu
Re: Cable size between Transformer to NGR and NGR to Ground
07/04/2012 3:55 AM
It's all in British Standard 7671, as has been indicated in these fora 7671 times now....
Re: Cable Size Between Transformer to NGR and NGR to Ground
07/05/2012 1:54 AM
Yes. If the earth fault current is restricated to 500A say, by using NGR and earth fault withstand time is 3 sec, then minimum cross section will be 500 x 1.732/ k . Value of k for Al or Cu to be substituted in the formula to get the result
07/05/2012 7:57 AM
What does NGR stands for?
may be, NGR stands for Netral grounding resistance.
07/05/2012 11:58 PM
Yes. NGR stands for Neutral Grounding Resistor.
Good Answers: 170
07/08/2012 3:01 AM
Pl. check your formula. It is not I2 Root 't' / K, but only I Root 't' / K.