LT HT Panel Rear Clearance

07/04/2012 2:09 AM

What factors decide whether rear access for a LT (415 V) panel is required or not.

As a general rule, we provide

(a) rear access of 1 M for all HT breakers

(b) Rear access of 1 M for LT Panels (415 V) when it has an ACB(Air circuit breaker) as an incomer.

Any IS/IEC or standard code available for this ? Kindly clarify.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: LT HT panel rear clearance

07/04/2012 3:18 AM
  • Does it need to stand against a wall?
  • Does it need to stand back-to-back with another panel?
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Sep 2008
Posts: 39
Good Answers: 1
#2
In reply to #1

Re: LT HT panel rear clearance

07/04/2012 7:28 AM

I am asking this general querry. This is not related to any particular project as such. I have also mentioned the general practices followed in our company with ref. to clearances.

Kindly clarify if there there is any code or standard with related to this

Register to Reply
Power-User

Join Date: May 2010
Location: Bhilai,Dist.-Durg,Chhattisgarh,INDIA
Posts: 104
Good Answers: 5
#3

Re: LT HT panel rear clearance

07/04/2012 10:02 AM

You may refer latest Indian Electricity Rules.

Rear access is required for attending the components, bus bars,cable terminations etc from rear side of the panels for routine checking and maintenance.The rear clearance should be adequate for a person to perform the above work .The same should also be more than the width of the hinged type rear door of the panels.

__________________
Learning is a never-ending process.
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#4
In reply to #3

Re: LT HT panel rear clearance

07/05/2012 1:18 AM

If there are hinged doors then there needs to be enough space for them to open and to pass behind when in the open position.

You can't have too much space.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Power-User

Join Date: May 2010
Location: Bhilai,Dist.-Durg,Chhattisgarh,INDIA
Posts: 104
Good Answers: 5
#6
In reply to #4

Re: LT HT panel rear clearance

07/05/2012 3:09 AM

That depends on the width of the rear door.For a width of 800 mm,a rear clearance of 1000 mm is OK .

__________________
Learning is a never-ending process.
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 131
Good Answers: 5
#5

Re: LT HT Panel Rear Clearance

07/05/2012 1:27 AM

Rear clearance is required if the panel has back access. This depends on the design of the panel where cable chamber and bus bar connections are on the back side of the panel.Clearance should not be less than 75 cm at the back. There shall be a clear passage on both sides of the panel of at least 75 cm width with a head clearance of 1.8 M. This is as per clause no. 37 (chapter IV) of CEA regulation, 2010, applicable for all installations in India with voltage class more than 650V.

However, if the space permits it is better to have back clearance of 1M for ease of maintenance. Front clearance for LT and HT switch board is generally kept as 1.5M and 2M respectively considering ease of maintenace with drawout type panels.

Register to Reply
Associate

Join Date: Sep 2008
Posts: 39
Good Answers: 1
#7
In reply to #5

Re: LT HT Panel Rear Clearance

07/05/2012 7:18 AM

Good answer sir.

Thanks

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#8

Re: LT HT Panel Rear Clearance

07/08/2012 3:08 AM

Vide the Indian Electricity Rules, 1956, Rule No. 51 (1) (c)Every switchboard shall comply with the following provisisons, namely:-

(i) a clear space of not less than 1 metre in width shall be provided in front

of the switchboard;

(ii) If there are any attachments or bare connections at the back of the switchboard, the space(if any)behind the switchboard shall be either less than 20 centimetres or more than 75 centimetres in width, measured from the farthest outstanding part of any attachment or conductor;

(iii) If the space behind the switchboard exceeds 75 centimetres in width, there shall be a passage-way from either end of the switchboard, clear to a height of 1.8metres.