Distribution Transformer Transformer Voltage Unbalance

07/10/2012 11:02 AM

1000kva 13.8kv/0.4 kv 3phase Delta/star distribution transformer

Dear respected friends in my network transformer as i mention above, their is problum between neutral & earthing appearing 220vac actually it must be ov,

between phase to phase 400vac, is normal

phase to neutral 220vac , is normal

Earth to neutral 220vac, that is completly abnormal

and Earth to L1, Phase=180 Earth to L2, Phase=250 Earth to L3, Phase=248

also if we will check by 220vac screw driver tester,as in neutral full lamp light appearing, and Phase L1, light Not Appearing, But another L2 & L3 Light Appearing.

please if someone have answer so help me, because my suspect of transformer secondry star winding neutral left inside, so must be replaced transformer or what please reply.

Reply
User-tagged by 1 user
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: distribution transformer transformer voltage unbalance

07/10/2012 11:18 AM

It sounds as though either:

  • the thing is disconnected from its loads and the neutral is disconnected from earth, or,
  • L1 is connected to earth and the neutral is not.

Is that a silly DMM or something sensible, like an analog meter with a decent lump of resistance between its legs?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Active Contributor

Join Date: May 2011
Posts: 16
#2
In reply to #1

Re: distribution transformer transformer voltage unbalance

07/10/2012 2:00 PM

respacted friends this transformer secondry star winding neutral not grounded since 2007. also in my side like that same capacity more transformer not grounded.

Reply Off Topic (Score 5)
Active Contributor

Join Date: May 2011
Posts: 16
#3
In reply to #1

Re: distribution transformer transformer voltage unbalance

07/11/2012 9:10 AM

1000kva 13.8kv/0.4 kv 3phase Delta/star distribution transformer

Dear respected friends in my network transformer as i mention above, their is problum between neutral & earthing appearing 220vac actually it must be ov, in this case neutral not bonded since 2007. also like that i have lots of transformer in my site at diffrent location, their is no problum only one transformer i faced as above mention.

between phase to phase 400vac, is normal

phase to neutral 220vac , is normal

Earth to neutral 220vac, that is completly abnormal

and Earth to L1, Phase=180 Earth to L2, Phase=250 Earth to L3, Phase=248

also if we will check by 220vac screw driver tester,as in neutral full lamp light appearing, and Phase L1, light Not Appearing, But another L2 & L3 Light Appearing.

please if someone have answer so help me, because my suspect of transformer secondry star winding neutral left inside, so must be replaced transformer or what please reply.

Reply Off Topic (Score 5)