distribution transformer transformer proublum neutral voltage unbalance

07/10/2012 2:22 PM

1000kva 13.8kv/0.4 kv 3phase Delta/star distribution transformer

Note:- transformer secondary star winding Neutral not grounded, since 2007 also like this with out neutral grounded, i have more transformer in my site.

Dear respected friends this transformer as i mention above, their is problum in transformer sec. winding neutral, in my case between neutral & earthing appearing 200vac actually it must be 0v,

today as i trace as follow:-

between phase to phase 400vac, is normal

phase to neutral 220vac , is normal

Earth to neutral 200vac, that is completly abnormal

and Earth to L1, Phase=180, Earth to L2, Phase=250, Earth to L3, Phase=248

also if we will check by 500vac screw driver tester, as connect neutral appearing full indicator, and connect Phase L1, so indicator not Appearing, But another L2 & L3 Light Appearing.

please if someone have answer so help me, because my suspect of transformer secondry star winding neutral left inside, so must be replaced transformer or what please reply.

Register to Reply
Pathfinder Tags: electrical
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#1

Re: distribution transformer transformer proublum neutral voltage unbalance

07/10/2012 3:07 PM

You have answered your own question. The voltage between neutral and earth exists because the neutral is NOT bonded to earth. Why did someone disconnect it? You're in the best position to find that out.

The only way to assure that the voltage between neutral and ground will be 0V is for you to restore that connection (bonding strap?) between the neutral point of your transformer and the earth point.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Active Contributor

Join Date: May 2011
Posts: 16
#3
In reply to #1

Re: distribution transformer transformer proublum neutral voltage unbalance

07/11/2012 8:53 AM

respected peter in my site like that more transformer which is not bonded,since 2007 to yet, teier is no change in load side but problum started only some days ago, so my responsible need solution with out bonded.

also thanks for your answer, i hope we will be continue in future.

Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: distribution transformer transformer proublum neutral voltage unbalance

07/11/2012 3:21 AM

Wasn't this thread sufficient?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856